Module 5: V/F Scalar Control

cancel
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Module 5: V/F Scalar Control

201,867 Views
Daniel_Popa
NXP Employee
NXP Employee
pastedImage_1.png

 

 

INTRODUCTION

 

In this module of the 3-Phase PMSM Control Workshop with NXP's Model-Based Design Toolbox , we are going to spin the PMSM for the first time with S32K and MotorGD Development Kits, learn more about Model-Based Design approach by building a PMSM mathematical model in Simulink to facilitate the development and validation of control algorithm and ultimately deploy that algorithm on the real hardware and check the experimental results against the one obtained in simulation environment. 

 

First, lets see what do we want to achieve in this module ?

  • Check the PWM signals generation based on Space Vector Modulation (SVM) technique discussed in the previous module Module 4: Space Vector Modulation . More than that, we want to check the PWM signals under normal conditions and there is no better way to do that rather than having the motor spinning. By implementing a simple way to accelerate or decelerate the motor and maintain various speed levels based on the user commands received via serial communication from a host PC we can easily verify the SVM under both dynamic and steady-state regimes.
  • Having the motor spinning in a steady-state regime will give us the possibility to implement, test and validate the phase currents measurement which is a critical mandatory step for Field Oriented Control (FOC). Because the phase currents are measured with shunt resistors mounted in series with the lower inverter switches we will need to synchronize the A/C conversions with PWM signals to obtain the meaningful values (...but more about that in the next module)

 

Based on these considerations, the simplest control method I can think off that allows us to achieve all these goals is: V/F Scalar Control. Another name for this method is Volts per Hertz (V/Hz) but the main principle behind it is the same: the ratio between voltage and frequency is kept constant throughout the motor speed range.

 

In Fig. 1, which represent the global application mapping diagram as discussed in Module 3: System Partitioning , are shown the main hardware blocks that are going to be configured and the control path we are going to follow (with red line). To achieve V/F scalar control we are going to configure the S32K FlexTimer peripheral to generate six PWM signals that are used to control the MotorGD Development Kit DC to AC power inverter via a dedicated MOSFET pre-driver chip: MC34GD3000. To enable the MC34GD3000 chip operation we will need to control two additional signals : Enable and Reset via dedicated GPIO. 

 

The interactions between host PC and hardware will be done via OpenSDA serial communication that will be used to download the code generated from MATLAB and to visualize various control signals with FreeMASTER. 

 

pastedImage_7.png
Fig. 1: Application Mapping -  HW & SW modules used for V/F Scalar Control are highlighted in green

 

After the control algorithm verification & validation but prior to connecting the PMSM Linix motor, we are going to check the PWM signals with an oscilloscope. This will ensure we are following all hardware recommendations and since we do not have yet active protections, it will spare us from unpleasant surprises.

 

 

 

V/F SCALAR CONTROL

 

If you recall the picture from Fig. 3, the 3-Phase PMSM Control Workshop with NXP's Model-Based Design Toolbox article, then you know that V/F Scalar Control is the term used to describe a very basic form of motor control that is using a non-vector approach scheme. A PMSM can be led to steady state regime by one of the following control techniques:

  • simple voltage fed controller - like the one we are going to implement now.
  • current type controller (DTC);
  • speed controlled scheme (FOC);

 

To explain how this technique works lets recall first the Module 2: PMSM and FOC Theory . It that module we have discussed various reference frames used to describe the PMSM theory of operation and we have obtained the main equations of the motor in the  shown here as (eq. 1 and eq. 2)

pastedImage_4.png

 

(eq. 1)

pastedImage_8.png

 

(eq. 2)

where:

pastedImage_17.png voltages and current in d-axis and q-axis respectively
pastedImage_19.png d and q-axis inductances and stator winding resistance 
pastedImage_22.png d and q-axis flux linkage and permanent magnet flux linkage
pastedImage_23.png electrical rotor speed

 

Rewriting (eq.1) in scalar from and time domain we will obtain:

pastedImage_24.png

pastedImage_25.png

 

 

(eq. 3)

 

In steady state regime, the flux linkage variation is zero, and for further simplification we are going to assume the stator winding resistance is neglectable. Taking into consideration these simplifications and the flux linkage equation (eq. 2) then the equations (eq. 3) becomes:

pastedImage_27.png

pastedImage_28.png

 

(eq. 4)

 

At this point we can transform the electric speed in frequency and rewrite the (eq.4) as a ratio of V/F:

pastedImage_1.png

pastedImage_2.png

 

 

(eq. 5)

 

In V/F scalar control method the frequency of the stator magnetic flux is set according with the desired synchronous rotor speed while the magnitude of the stator voltage is adjusted to keep the ratio between them constant. No control over voltage or current vectors angles is utilized, hence the name scalar control. 

 

The V/F ratio is calculated from the nominal values of the PMSM voltage and frequency parameters. By maintaining a constant V/F ratio between the amplitude and frequency of 3-phase voltage waveforms, then the stator flux of the PMSM can be maintained relatively constant in steady state. However, in practice a typical V/F profile is not constant over the entire range of motor speed.

 

As can be seen in Fig. 2, the V/F profile may be divided in three main regions:

  1. Compensation – a higher than normal voltage is required to compensate the voltage drop across the stator resistance that was neglected for simplified mathematical model
  2. Linear - follows the constant V/f relationship as derived from (eq. 5)
  3. Field weakening - constant V/f ratio cannot be satisfied due to the stator voltages limitation at the rated value in order to avoid insulation breakdown

 

pastedImage_2.png
Fig. 2: V/F profile practical aspects

 

The V/F scalar control is the most common control strategy used for induction motor drives. In case of PMSM, the V/F scalar control is a good alternative in applications where good dynamic performance is not required (e.g.: HVAC, fans, pumps or blowers). In such cases the V/F scalar control is performed without the need of a position/speed sensor.

 

By using V/F scalar control there is no need for high capability CPU as in the case of FOC, but keep in mind that this kind of simplicity also comes with some disadvantages:

  • instability of the system after exceeding a certain applied frequency
  • systems low dynamic performance, which limits the use of this control method
  • poor fault protection against stall detection and over-currents

 

In case of PMSM, both open and closed-loop control of the speed can be implemented based on the V/F scalar control. Open-loop control is used in applications where system dynamic response is not a concern. For such use cases, the frequency is determined based on the desired speed and the assumption that the rotor will ultimately follow the synchronous speed. 

 

Throughout this module we are going to implement an open-loop control system topology for a 3-phase PMSM using V/F scalar control as the one shown in Fig. 3. Such control structure will allow us to control the PMSM speed without any feedback of motor parameters or rotor position. The motor is driven by the conventional 3 phase voltage-source inverter via MotorGD DevKit. The NXP's S32K MCU is being used to generate the six PWM signals using a modified SVM PWM technique with 3-rd harmonic injection.

 

pastedImage_1.png
Fig. 3: V/F scalar control block diagram

In order to maintain a similar topology with two control loops and similar data structures for the examples that we are going to use in this workshop, we are going to implement the V/F scalar control application based on: 

  • FAST control loop is executed at each 0.1ms and computes the PWM duty cycles based on Space Vector Modulation. The reference voltages for (dq)-axes and the motor electrical speed represent the inputs. The electrical angle needed for Inverse Park Transformation is computed based on electrical speed reference.
  • SLOW control loop is executed at each 1ms and provides the voltage references for Inverse Park transformation and the electrical speed profile. Inside this loop, the user commands are handled and based on a parameterisable Ramp Profile the appropriate control parameters are generated. The V/F profile is implemented via a tunable Look-Up-Table (LUT)  

 

 

 

MATLAB MODELLING OF CONTROL ALGORITHM

 

MATLAB/Simulink environment and NXP toolbox for S32K1xx allow us to approach the motor control algorithm development very straightforward. Using Model-Based Design strategy we can develop, implement, simulate and test the control method entirely in simulation environment and once we are satisfied with the results we can proceed further by deploying the generated code on the real target and perform final validation and testing.

 

Fig. 4 shows the Simulink model we are going to use for V/F scalar control implementation, testing and validation. The model can be find attached at the end of this article.

pastedImage_2.png
Fig. 4: Simulink model for the entire plant: MCU-DC2AC INVERTER-PMSM

 

The model shown in Fig. 4 consists in three major subsystems that mimics the actual hardware arrangement, each one of them implementing a specific functionality: 

  • S32K14x EVB - implements the S32K MCU logic that allows the control algorithm to compute the PWM commands for the power inverter;
  • Motor GD DevKit - implements a simplified model of power inverter that converts the PWM commands into high voltage continuous signals;
  • PMSM Model - implements a simplified PMSM motor model that replicates the behavior for the real LINIX motor.

 

S32K14x EVB Subsystem

This is a discrete model that implements the V/F scalar control block diagram shown in Fig. 3. There are 2 subsystems that are triggered based on specific timing intervals. These 2 subsystem mimics the existance of the separated digital control loops: SLOW & FAST 

pastedImage_5.png
Fig. 5: FAST and SLOW control loop model

The SLOW Loop Subsystem Fig. 6, updates the commands for the FAST Loop Subsystem shown in Fig. 7. Based on the SPEED_CMD set by the user as motor target speed, a trapezoidal speed profile is generated using a dedicated Simulink block exposed by the AMMCLIB Add-on. Based on this SPEED_REF the electrical angle used for Inverse Park transformation is going to be derived.

pastedImage_8.png
Fig. 6: SLOW control loop model

The quadrature voltages alpha-beta are computed based on the electrical angle and the (dq) reference voltages obtained in SLOW Loop. In case of UD_REF the value is set to 0 just to emulate the theory behind FOC and in case of UQ_REF the value is obtained from a Look-Up-Table (LUT) that implement the concept of V/F scalar control.

pastedImage_11.png
Fig. 7: FAST control loop model

At each 0.1ms the PWM commands are computed and updated based on AMMCLIB specialized Simulink block that implements and optimized Space Vector Modulation with 3rd harmonic injection. These PWM commands are then passed to the next subsystem that emulates the operations for power inverter.

 

 

MotorGD DevKit Subsystem

This subsystem implements a basic model to emulate the DC2AC power inverter. The PWM commands are converted into high voltage signals (depending on the Vdc value selected) that are then applied to the motor windings.

pastedImage_4.png
Fig. 8: Simplified Power Inverter model

 

PMSM Model Subsystem

The Simulink model consists in standard 3-phase PMSM motor equations shown in Module 2: PMSM and FOC Theory. Within the model you can easily identify:

  • stator windings electrical model
  • electro-mechanical model
  • sinusoidal back-EMF model
pastedImage_8.png
Fig. 9: 3-phase PMSM model

Note 1: we are not going into details about PMSM modelling since this is not the purpose of this module. Feel free to follow the link indicated in the model to get more details. As usual, if you have any questions about it, feel free to ask.

 

Note 2: I've choose to implement this simplified model to avoid the usage of other MATLAB toolboxes. If you have access to Simscape Power System you could use one of the motors from there.

        

 

 

 

MATLAB SIMULATION OF THE PLANT

 

The entire V/F scalar control algorithm (...and not only) can be validated using this simulation environment provided in MATLAB/Simulink. This way we can validate the Space Vector Modulation, V/f scalar control and PMSM motor dynamic responses even without having the actual hardware setup. For those of you planning to use NXP hardware in the future, this approach might be useful in getting familiar with motor control.

 

Fig. 10, 11 and 12 show the main control signals and outputs for each subsystems discussed earlier. At this point we can investigate various quantities that might not be easily accessible on the real plant.  

pastedImage_1.png

Fig. 10: V/F scalar control commands in case of start-up ramp:

(1) Speed Profile, (2) Electric Angle, (3) quadrature voltage references and (4) 3-phase stator voltages references

 

pastedImage_4.png
Fig. 11: Space Vector Modulation verification: Inputs & Outputs

 

pastedImage_7.png

Fig. 12: PMSM Model Responses in case of start-up sequence:

(1) Command vs. Actual Motor Speed, (2) Rotor angle vs. Rotor position, (3) Stator Currents and (4) Back EMF voltages

 

As can be seen there is a good match between the results obtained in simulation and the PMSM motor theory. Now that we have built confidence in the results it's time to move on to next stage.

 

 

 

EMBEDDED TARGET VERIFICATION OF CONTROL ALGORITHM

 

Since the modelling and simulation phases are completed with satisfactory results, it is time to convert the Simulink model and adapt it for Code Generation. The Fig. 13, shows the actual model that we are going to use the Code Generation.

 

pastedImage_4.png
Fig. 13: Simulink model for S32K embedded target code generation

 

The model depicted in Fig. 13 is derived from the one shown in Fig. 4 and almost 90% of it share the same similarities. To have the model suitable for code generation there are a few modifications that needs to be done:

  1. Enable the MOSFET pre-driver;
  2. Enable the PWM signal generation from the appropriate FTM module;
  3. Add FreeMASTER communication driver into the application in order to have the capabilities to read/write data to/from S32K MCU;
  4. Remove the continuous blocks used in the previous simulation phase;

 

Video training: Open Loop V/F Scalar Control Model for PMSM
 
(view in My Videos)
 
 

 

 

MC34GD3000 Pre-Driver Enablement

The MC34GD3000 is a field effect transistor (FET) pre-driver designed for 3-phase motor control and similar applications. The IC contains three high-side and three low-side FET pre-drivers. Three external bootstrap capacitors provide gate charge to the high side FETs. The IC interfaces to a S32K MCU via six direct input control signals, an SPI port for device setup and asynchronous reset, enable and interrupt signals. As it is shown in Fig. 14, the MC34GD3000 MOSFET pre-driver needs to be enabled before PWM signals generation. 

The pre-driver can be configured over SPI communication to enable various features. Please check the MC34GD3000 for details. In this module we are not going to use this feature.

    

After IC initialization phase is complete, the device goes into the enable mode and operates normally. Normal operation continues in this mode as long as both enable pins EN1/EN2 and RSTB are high.

 

pastedImage_18.png
Fig. 14: MC34GD Pre-driver pins

 

Add S32K dedicated peripheral blocks for GPIO to enable the MC34GD3000 pre-driver normal operation and remove the existing simplified simulation model blocks.

pastedImage_9.png pastedImage_10.png
Fig. 15: MotorGD subsystem: on the left - simplified inverter Simulink block diagram, on the right - S32K GPIO peripherals that set EN1/EN2 and RST pins to high

 

pastedImage_12.png pastedImage_13.png
Fig. 16: GPIO Configuration for Enable and RST signals

 

 

S32K FlexTimer(FTM) Enablement

The most important aspect of the whole application is to be able to generate the PWM signals based on the Space Vector Modulation technique and pass these signals to MC34GD3000 pre-driver. NXP's Model-Based Design Toolbox for S32K1xx address this issue in a very simple and convenient way by providing a S32K dedicated peripheral block for FTM as shown in Fig. 1

pastedImage_12.png pastedImage_13.png
Fig. 17: PWM generation in Simulink modelling vs. PWM generation used for code generation on S32K

 

The FTM Simulink block is configured to initialize the FTM3 module since the output signals from that specific module are routed on the PCB to control the actual power inverter MOSFETs. The schematic for the MotorGD DevKit Fig. 18, shows the actual signal routing. 

The MotorGD DevKit was designed to be compatible with Arduino shields, therefore only some specific signals are available on the pin-headers. In case you design your own power inverter you might need to reconfigure the actual pins that controls the MOSFETs. 

    

 

 

pastedImage_20.png

Fig. 18: MC34GD3000 and MotorGD DevKit Power Inverter signal routing

 

Based on the pins assignment on both MotorGD DevKit Fig. 19 and S32K14x EVB  Fig. 20, we can configure the actual FTM peripheral as shown in Fig. 21.

pastedImage_1.png
Fig. 19: MotorGD DevKit Pin Assignment
pastedImage_7.png
Fig. 20: S32K144 Evaluation Board Pin Assignment

 

pastedImage_8.png pastedImage_10.png
Fig. 21: FTM Peripheral Block Configuration for controlling the power inverter from MotorGD DevKit

 

FreeMASTER Support for Data Visualization

Before generating the C-code for the application and deployment on the hardware, we need to enable and configure the FreeMASTER embedded driver to allow us the visualize the data in real time. Since most critical part of the V/F control algorithm is done in the FAST loop that is executed at each 0.1ms, we will need to configure the FreeMASTER to capture the data in that specific routine.

 

NXP's Model-Based Design Toolbox lets you configure and call the FreeMASTER anywhere in your model. For this application, since the goal is to check the real hardware data against the ones obtained from Simulink simulation we are going to configure the FreeMASTER as shown in Fig. 22.

 

pastedImage_2.png pastedImage_4.png
Fig. 22: FreeMASTER configuration

 

Please note that we have configured the FreeMASTER to work in Short Interrupt mode, with a relative high priority - less than the ones needed for actual motor control loops and we have enabled the Recorder option for a timebase of 0.1ms. All these settings and the actual function call for the FreeMASTER Recorder (Fig. 23) are needed to make sure you capture the data in the FAST loop - otherwise we might read wrong data.

pastedImage_7.png
Fig. 23: Place the FreeMASTER Recorder Call Simulink Block in the FAST Loop Sybsystem

 

 

 

EMBEDDED TARGET VERIFICATION AGAINST SIMULINK SIMULATION 

 

At this point we can run the application on the embedded side and verify the results against the ones obtained in simulation. Since we want to verify the algorithm behavior prior to running the actual motor, then for these kind of tests, we do not have to power on the MotorGD DevKit. This verification step can be done using PIL co-simulation as well but for getting closer to the final application setup, I've choose to run the application completely independent of MATLAB environment. In this case the real time data from S32K are obtained and visualized via FreeMASTER in RECORDER mode. The FreeMASTER project used in conjunction with Simulink model shown in Fig. 13 is attached at the end of the article.

 

First, we will check the correct generation of the commands for SVM and the PWM duty cycles waveforms associated with these commands. In the next figures, on the left hand side we can see the waveforms generated with MATLAB/Simulink environment in SIMULATION mode while on the right hand side the same data are RECORDED with FreeMASTER on real hardware S32K MCU for the same scenario. As you can see there is a remarkable similarities between these sets of data, giving us confidence that once the PMSM will be connected the motor will behave as predicted in SIMULATION environment.

pastedImage_4.png pastedImage_5.png

Fig. 24: SIMULATION vs. REAL Start-up Sequence

(1) Speed Reference Profile, (2)Electric Angle Transformation, (3) Fixed Frame Quadrature Voltages,

(4) 3-phase PWM duty-cycles for each PMSM phase 

 

pastedImage_7.png pastedImage_8.png

Fig. 25: SIMULATION vs. REAL Space Vector Modulation in Steady State Regime

Inputs: (1) DQ Frame Voltages, (2) Fixed Frame Quadrature voltages, (3) Electric Angle for 500[rpm] equivalent

Output: (4) SVM Sector Identification 

 

pastedImage_10.png pastedImage_11.png

Fig. 26: SIMULATION vs. REAL PMSM Steady State Zoom

(1) Electric angle variation for 500[rpm] motor speed and equivalent (2) SVM 3-phase voltage references 

 

 

 

VALIDATION ON REAL PLANT 

 

Once the verification phase is completed successfully, we can start to validation on the real plant: MCU-DRIVER-PMSM

We start with PWM signal generation. The scope of this verification is to check the correct waveform generation (polarity and frequency) and signal integrity (rising/falling slopes, signal levels, dead-time). For this test we are going to use an oscilloscope to scope the digital signals directly on MotorGD DevKit PCB.

 

pastedImage_4.png
Fig. 27: PWM High (yellow) and Low (cyan) Commands

Note PWM HIGH and LOW are configured to be complementary but due to HW restrictions the low side PWM signals are active LOW.

    

As can be seen in Fig. 27, the PWM signal generation is done correctly with 10KHz frequency and correct polarities based on the settings from Fig. 21.

 

At this point we can connect the PMSM and let is spin. If you power on the boards, the motor should start sniping, acceleration from 0 to 1000[rpm] in 1[sec]. From FreeMASTER watch variable window you can change the Speed_Command variable to increase and decrease the motor speed.

 

With the motor running, we can do some additional verification with the oscilloscope directly on the motor windings.

pastedImage_10.png
Fig. 28: Phase A &B terminal voltages and Line A-B resulting voltage. Check Module 4: Space Vector Modulation for details

 

 

 

CONCLUSIONS 

 

In V/F scalar control the stator currents are not controlled directly. A V/F controlled PMSM can become unstable easily especially when the load torque increases. Considering its disadvantages the V/F scalar control is not suitable for low speed control in high dynamic applications but might be a good choice for PMSM used for HVAC applications, where high performance is not required.

 

In general, open loop V/f control is not stable in the whole frequency range, it may become unstable, even at no-load, from a certain excitation frequencies lower than the rated speed. To address such use-cases, it is necessary to have a stabilizing loop in the system. This stabilizing loop can be implemented by means of an speed measurement system, increasing cost, and complexity. 

 

At point we have reached our main goal and we now have a control simple method to spin the PMSM in open loop. We've validated the PWM generation techniques and we are now ready for the next step: implementing a proper Field Oriented Control technique for PMSM.

 

We hope you find this information useful. Feel free to LIKE this article and comment below.

 

Update January 28th 2019 - This Simulink model is now available on MATLAB 2018b and MBDT for S32K14x 2018.R1 release

Before using the new models make sure you apply all the hot-patches from here: HotFix: MBD Toolbox 2018.R1 for S32K 

 

Update revisions:

March 18, 2019

May 06, 2020

90 Replies

15,214 Views
lethuer
Contributor V

For the Embedded target model we also have to replace the Hardware specific blocks.

1. Driver

The 3-ph Driver FNB41560 has no enable or reset signals.

But here we should at least observe the Fault1 (Motor over current, pfc over current and dc bus under voltage - active low) & Fault2 (overvoltage - active high) signals.

Additionally I would recommend to monitor the IPM_Temp Signal to protect overheating.

If one of them occurs the PWM has to be stopped !

Any further recommendations for that ?

Unbenannt.PNG

2. PWM Signal Generation

For the PWM Output I've implement the "eFlexPWM_Three_Phase_Output"

Where is the difference to "FTM_Three_Phase_Output" ?

Unbenannt.PNG

Resolution is set to 0.1% and Deadtime 1500 nanoseconds (see datasheet extract).

Unbenannt.PNG

Unbenannt.PNGUnbenannt.PNG

3. FreeMASTER

There is the FreeMASTER Config block, which I can't find in the KV4x library.

Unbenannt.PNG

So I think we have to configure it in the MCD_MKV4xF_Config ?

Unbenannt.PNG

But here I don't have these Options:

Unbenannt.PNG

So how I could configure freemaster in short Interrupt mode ?

In the Fast Loop there is a "FreeMaster_Recorder_Call" Block. Also this one I didn't found in the KV4x library.

What I have to choose here ?

Unbenannt.PNG

Also I have found this test Points in the fast Loop control:

Unbenannt.PNG

Could you please explain the meaning of it ?

Best regards

Leon

15,482 Views
Daniel_Popa
NXP Employee
NXP Employee

Hi Leon, 

Regarding your questions:

The 3-ph Driver FNB41560 has no enable or reset signals.

But here we should at least observe the Fault1 (Motor over current, pfc over current and dc bus under voltage - active low) & Fault2 (overvoltage - active high) signals.

Additionally I would recommend to monitor the IPM_Temp Signal to protect overheating.

If one of them occurs the PWM has to be stopped !

Any further recommendations for that ?

Seems about right!

For the PWM Output I've implement the "eFlexPWM_Three_Phase_Output"

Where is the difference to "FTM_Three_Phase_Output" ?

Kinetis is different than S32K (even if they have similar ARM M4 Cores) in terms of peripherals on the SoC

The Simulink blocks keeps a similar look-and-feel, but there might be different options due to IP differences.

There is the FreeMASTER Config block, which I can't find in the KV4x library.

The Freemaster block implemented in S32K is brand new and contains enhancements what are only available on S32K products (and for all future releases)

In the old versions we will not find all these option. 

Nonetheless, you can modify the behavior by hand. If you go to ..\mctbx_Kinetis\mctbx_kv\src\FreeMaster_files you will find a file freemaster_cfg.h that is copied into the generated folder. You can change this file to configure the FreeMASTER to use RECORDER and INTERRUPTS.

Also I have found this test Points in the fast Loop control:

Could you please explain the meaning of it ?

Is is explained here: https://community.nxp.com/thread/449904?commentID=977772#comment-977772 

Hope this helps!

Daniel

0 Kudos
Reply

16,173 Views
lethuer
Contributor V

Hi Daniel, 

 

Regarding your questions:

The 3-ph Driver FNB41560 has no enable or reset signals.

But here we should at least observe the Fault1 (Motor over current, pfc over current and dc bus under voltage - active low) & Fault2 (overvoltage - active high) signals.

Additionally I would recommend to monitor the IPM_Temp Signal to protect overheating.

If one of them occurs the PWM has to be stopped !

Any further recommendations for that ?

 

Seems about right!

Okay ! So I have one more question about this...

In the FNB41560 Subsystem I read the Fault1 and Fault2 signals.

Unbenannt.PNG

Unbenannt5.PNG

I want to use them in the PWM Commands Subsystem for deactivating the pwm if one fault Signal occurs. 

Unbenannt4.PNG

With GoTo / From Blocks this isn't possible, but I don't want to have additional Input / Output ports.

Goto/From connections cannot cross nonvirtual subsystem boundaries. The only exception is when a goto is connected to a state output port
Component:Simulink | Category:Model error
Invalid connection starts with 'V_f_Scalar_Control_KV4x/FNB41560/Goto'
Component:Simulink | Category:Model error
Invalid connection ends with 'V_f_Scalar_Control_KV4x/HVP-MC3PH/Fast Loop Control/PWM Commands/From'

How could I realize it to use the fault signals in the HVP-MC3PH/Fast Loop Control/PWM Commands Subsystem without having additional Input / Output ports ?

Also I'm not sure if this is the correct way to implement this safety function ?

Maybe there should be triggered a Interrupt if one fault Signal occurs ?

Best regards

Leon

16,142 Views
Daniel_Popa
NXP Employee
NXP Employee

You could use the Data Store blocks to write and read the values.

pastedImage_1.png

In general the protection routine is called on ADC interrupt immediately after current measurements and prior to the next PWM duty cycle update in order to stop the inverter ASAP.

Best regards,

Daniel

0 Kudos
Reply

16,140 Views
lethuer
Contributor V

Hello dumitru-daniel.popa‌, wangxuan‌

Could you have a look over it ?

now my model for the embedded target looks like this:

The data store Memory blocks have to be on the same Level like the both Subsystems "HVP-MC3PH" and "FNB41560", so that it is possible to write data in the FNB41560 Subsystem and read them in the HVP-MC3PH/Fast Loop Control/PWM Commands Subsystem, correct ?

Unbenannt1.PNG

the content of "FNB41560" Subsystem:

is it correct to place the ADC_Config, ADC_Start and ADC_Samples here or should they be on the same Level like MCD_MKV4xF_Config ?

Unbenannt3.PNG

In the adc samples Subsystem only the sample of ipm temp is configured:

Unbenannt2.PNG

The HVP-MC3PH / Fast Loop Control / PWM Commands Subsystem:

Unbenannt5.PNG

If Fault1, Fault2 or IPM_Temp is Logical 1 the Switch passes Input 1 which I configured "0".

For the IPM_Temp signal I have one question.

The block diagram of the driver and layout of mc3ph main board:

Unbenannt8.PNG

Unbenannt9.PNG

In the mc3ph user guide documentation I found this R-T curve of the ntc Thermistor for temperature sensing:

Unbenannt6.PNG

For example I want to stop the PWM if temperature is higher than 100°C.

By the way: What is your temperature recommendation for shutting down ?

At 100°C the Thermistor should have R = 3000 Ohm

So the voltage Level at the "IPM_Temp" should be calculated like this:

Unbenannt7.PNG

Because of the 12-bit adc the Maximum value is 2^12=4096

So as threshold I configured (2,357/3,3)*4096 = 2925.

From this value the output of the "compare to constant" block is logical 1.

Is that correct so far or have I made any mistakes?

Again I attached the model.

For simulating the PWM_3PH signals in SVM scope I have to comment through the not Operator in FNB41560 Subsystem.

At the Moment of downloading the code to the target this must be undone.

Any further recommendations ?

Thank you

Leon

0 Kudos
Reply

16,145 Views
wangxuan
Contributor III

Hi,Leon

  I want to build your model into C code and download it to the control board. We have the same hardware HVP-KV46 and HVP-MC3PH. I have done this. The power I chose was powered by the control board KV46 to the HVP-MC3PH, so the 5V and 15V parts were not available. What I want to ask you is whether you have successfully communicated the model with FREEmaster. I can't connect them to a successful communication. How did you solve it? I hope you can tell me, thank you very much.

pastedImage_1.png

  pastedImage_2.png

pastedImage_3.png

Best regards,

wangxuan

0 Kudos
Reply

16,145 Views
lethuer
Contributor V

Hi wangxuan‌

I think the UART configuration is wrong. This option depends on the Jumper Setting you have Chosen on the main board.

In the User Guide in 3.2.1 you can find the Jumper Settings.

In default you have this configuration:

Unbenannt.PNG

hvp-mc3pg schematic

Unbenannt.PNG

kv46 schematic:

Unbenannt.PNG

My FreeMASTER configuration:

Unbenannt.PNG

Best regards

Leon

0 Kudos
Reply

16,197 Views
wangxuan
Contributor III

Hi Leon Thürnau

Thank you for your help.

  1. I made changes in the model according to your settings (model in Annex 1). It is frustrating that he still had the same mistake. I made the same FREEmaster configuration in Attachment 2, but it can communicate normally. I don't know why.
  2. In addition, I want to use the real oscilloscope to go to the J10 test point PWM signal, I want to see if they are normal, but I measured the waveform shown in Figure 4, it does not look like a pulse, and Annex 2 The measured PWM signal is perfect in Figure 5. Did you measure the PWM signal of our model? thank you very much!

pastedImage_3.png

pastedImage_2.png

pastedImage_4.png

pastedImage_1.png

pastedImage_5.pngpastedImage_6.png

Best regards

 

wangxuan

0 Kudos
Reply

16,232 Views
wangxuan
Contributor III

I forgot to add an attachment, add it here

0 Kudos
Reply

16,234 Views
lethuer
Contributor V

Hi,

yes I did several times. My PWM signals looks fine. Here is a picture of all three Low Side IGBT A B and C

PWM AL, BL, CL.PNG

dumitru-daniel.popa‌ maybe you could help ?

Seems that there are some bugs with FreeMASTER and PWM ?

Best regards

Leon

0 Kudos
Reply

16,234 Views
wangxuan
Contributor III

Hi Leon Thürnau

  I also want to ask you:
Are you using the same model generated code? What is the power supply mode of the motherboard? Is it with a real motor? Can you get the PWM waveform from your diagram if you only use the control board to supply power? Thank you.

 

Best regards

 

wangxuan

0 Kudos
Reply

16,234 Views
lethuer
Contributor V

Also I want to let you know that I'm using R2017b, so I can't open your model.

Best regards

0 Kudos
Reply

16,234 Views
wangxuan
Contributor III

Hi   Leon Thürnau

   Thank you for your model and help, this time my FreeMaster communication with the motherboard is normal, but I do not understand how to set up additional switches in the PTE21, and just like you suggested when I comment out the fault1 in PWM_COMMANDS subsystem signal, PWM generated The duty cycle is still 50%. Can you give me some suggestions and tips, thank you.

pastedImage_1.png

Best regards

wangxuan

0 Kudos
Reply

16,234 Views
lethuer
Contributor V

Hello wangxuan‌

I had connected the Switch between J2 pins 1 and 4.

In Standard Jumper configuration "RxD_EXT" is equal to "RxD1".

RxD1 is connected to "PTE21" on the Controller Card.

You should check the Input signals of the "OR" with freemaster.

If any of this signals is Logical true then the Switch block passes Input 1.

Best regards

Leon

0 Kudos
Reply

16,234 Views
lethuer
Contributor V

Hi wangxuan‌

I'm not sure if this was exatly the same model. I've attached my actual one, maybe you could try this.

The download to the target is succesful and the model starts.

Please connect the additional Switch to "pte21" so that the PWM dowsn't start immediatly after download the code.

Because I'm using a real Motor the power supply of the main board is 325V DC.

I also can measure the PWM signals at J1 if the main board is powered from the Controller Card. But then of course you have to comment out the fault1 in PWM_COMMANDS subsystem signal, because it is undervoltage fault.

Best regards

Leon

16,234 Views
lethuer
Contributor V

Hi dumitru-daniel.popa‌

did you have time to have a look over this ?

If the Simulation result is good enough after I found a proper LUT for my Motor I want to download the code to the target and check the results there, just like the way you did in "EMBEDDED TARGET VERIFICATION AGAINST SIMULINK SIMULATION". But for this it would be helpful the questions asked are cleared.

Thank you so much for all the support !

Leon

0 Kudos
Reply

16,292 Views
wangxuan
Contributor III

Hi Leon Thürnau,dumitru-daniel.popa

    I have reviewed your comment, which is of great help to me and in many places I did not think of it. I use HVP-MC3PH and HVP-KV46 just like you, but I have not purchased PMSM motor. I think my first step is to do simulation in MATLAB environment. The motor is also virtual, so it is only the verification control algorithm. I feel like we are teammates, our ultimate goal is to make our motor run safely and smoothly.
Seeing your modified model and problem bothering me as well, I also know that FreeMaster_Data_Recorder was found in the library with the following path:

pastedImage_2.png

pastedImage_3.png

pastedImage_4.png

If possible, I hope to have more help with KV4.

Best regards

wangxuan

0 Kudos
Reply

16,291 Views
lethuer
Contributor V

Hi !

Seems we have the same goal !

But I want to see the motor running, so both Models are required for me.

the „freemaster_data_recorder“ Block in the kv4x Library i also have seen.

But in S32K it is called „freemaster_recorder_call“... Maybe there are some differences ?

in a previous Model the Communication with freemaster was Fine only with activate this Option in the Processor Config Block.

I didn’t implement a additional freemaster Block.

Only have chose the correct uart interface, which depends on the Jumpers.

best regards

0 Kudos
Reply

16,292 Views
lethuer
Contributor V

Hi wangxuan‌ dumitru-daniel.popa‌

Because I want to implement the workshop also based on HVP-MC3PH i've replaced the S32K blocks with the KV4x blocks and I've attached my model.

Unbenannt.PNG

But unfortunately the KV4x library doesn't have single type precison (only 16 Bit). Because of that there are some data type conversation required. In the fast Loop control Subsystem this leads to some trouble with Cos, Sin and ParkInv Block:

Unbenannt.PNG

Unbenannt.PNG

In the KV4x library I didn't found a SinCos Block, so I've used one Sin Block and one Cos Block. The entry of them is the blue signal from picture above.

Unbenannt.PNG

Unbenannt.PNG

The Output from the Sin Block is always 0, the Output from Cos is always 3,25*10^4.

Unbenannt.PNG

Unbenannt.PNG

The conversation of UQ_Ref leads to 0 instead of values between 0.4...0.5

So all entrys of the ParkInv Block are wrong and it can't work correctly.

Alpha and Beta are always 0.

Best regards

16,292 Views
Daniel_Popa
NXP Employee
NXP Employee

Hi Leon, 

I this case you need to design the entire algoritm to work on 16bit values. 

I would suggest to start with the input values and compute them as fixed-point 16-bit fractional and avoid the Simulink Data Type Conversion. 

If you need to do that conversion - then you have to do it by multiplication and shifting rather than casting. Simulink Data Type Conversion will not help you in this case.

Hope this helps!

Daniel

0 Kudos
Reply

16,291 Views
wangxuan
Contributor III

Hi,dumitru-daniel.popa

     Through the reply you gave me I understand the principle of GFLIB_Ramp_FLT, I found a similar module GFLIB_Ramp_F16 in the KV4 library, I think their role is the same, but require different types of data. We got an error in Simulink Data Type Conversion, and we should count them as fixed-point 16-bit fractional starting from the input value. Could you give us an example of how to convert, for example, starting from speed command value 1000 . Because after I find the relevant information still need help, thank you!

pastedImage_1.png

pastedImage_4.png

pastedImage_2.png

Best regards

wangxuan

0 Kudos
Reply