S32k322 ADC Configuration Issue
1,216 次查看
praveen_ext
I am using three ADC channel is configured for current sensing using BCTU interrupt(CTU mode is configured to trigger mode) and remaining ADC channels are configured in Normal chain method for voltage and temperature sensing.
During this configuration voltage and temperature sensing is working as expected but current sensor is sensing raw values with noise so we are getting abnormal spike in current control. Also we have changed the Ctu mode from trigger to control mode ,in current sensor channel raw value noise is reduced. But other channel configured in normal channel were not working.
Our expectation is to work with single ADC peripheral(ADC0) in current sensing using BCTU trigger as well as voltage and temperature sensing in normal chain method without any spike.
Note: Our hardware is designed with configuration (i.e Current sensor channels is configuration is as follows, P7-ADC0,P2 and P3 -ADC1 for reading in BCTU method. Followed by remaining ADC channels configured to normal chain method(ADC0 - X0,X1,S19 and ADC1-P0,P2,P3,P1,S10)
标签 (2)
标记 (1)
6 回复数
1,149 次查看
praveen_ext
Hi @Senlent ,
I have also same issue which you mentioned above.
Our external oscillator clock is 25 MHz. According to the S32K322 datasheet, the ADC supports up to 80 MHz, so I have configured a prescaler of 2. I also configured the sampling time to 1.2 microseconds and set the BCTU mode to trigger mode. However, we are still getting noisy data when executing the BCTU method and the normal chain method simultaneously on the same ADC0 peripheral. Is there a workaround or an alternative method to safely run both on the same ADC0 peripheral?
1,172 次查看
Senlent
Hi@praveen_ext
I believe this is the exact same issue you're facing.
https://community.nxp.com/t5/S32K/Difference-in-ADC-noise-between-BCTU-Control-Mode-and-Trigger/td-p...
From the screenshot you provided, it seems you haven't made any changes to my previous reply.
I've already informed you that there's a problem with your ADC clock divider configuration,
Also, are you sure your external clock is 25MHz?
If you've checked these two points and the problem persists after testing, you can try modifying the ADC channel's sampling time.
This option allows you to modify the sampling time; you can try increasing the sampling time and testing again.
963 次查看
praveen_ext
Hi @Senlent ,
In the meantime, I reduced the Instance 1 clock frequency to 40 MHz and configured the sampling time to 1.2 microseconds. Following these changes, the measured values from the BCTU are no longer showing noise.
Adc_Raw_Val_Ph3 connceted with sensor remainig two values in floating.
RwaeVal - configured normal chain
praveen_ext_0-1782473167287.pngpraveen_ext_1-1782473350906.pngpraveen_ext_2-1782473423830.png
标记 (1)
960 次查看
Senlent
Hi@praveen_ext
Aren't you the same company? You're asking the exact same questions.
https://community.nxp.com/t5/S32K/Difference-in-ADC-noise-between-BCTU-Control-Mode-and-Trigger/m-p/...
It seems you haven't been reading my answer carefully.
This is the third time I've told you that your clock divider settings are incorrect.
For 160MHz, you need to set them to 2 and 4.
888 次查看
praveen_ext
Hi @Senlent ,
We tested the previous suggestions, but the issue is still not resolved. After further configuration and verification, I have attached the updated test data and configuration images below.
kindly assist us where we missed.
ADC0
ADC1
标记 (1)
883 次查看
Senlent
Hi@praveen_ext
Share your project and i will test it on myside,
%3CLINGO-SUB%20id%3D%22lingo-sub-2386456%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3ES32k322%20ADC%E9%85%8D%E7%BD%AE%E9%97%AE%E9%A2%98%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-2386456%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%E6%88%91%E4%BD%BF%E7%94%A8%E4%BA%86%E4%B8%89%E4%B8%AA%20ADC%20%E9%80%9A%E9%81%93%EF%BC%8C%E9%85%8D%E7%BD%AE%E4%B8%BA%E4%BD%BF%E7%94%A8%20BCTU%20%E4%B8%AD%E6%96%AD%E8%BF%9B%E8%A1%8C%E7%94%B5%E6%B5%81%E6%A3%80%E6%B5%8B%EF%BC%88CTU%20%E6%A8%A1%E5%BC%8F%E9%85%8D%E7%BD%AE%E4%B8%BA%E8%A7%A6%E5%8F%91%E6%A8%A1%E5%BC%8F%EF%BC%89%EF%BC%8C%E5%85%B6%E4%BD%99%20ADC%20%E9%80%9A%E9%81%93%E9%85%8D%E7%BD%AE%E4%B8%BA%E6%AD%A3%E5%B8%B8%E9%93%BE%E5%BC%8F%E6%96%B9%E6%B3%95%E8%BF%9B%E8%A1%8C%E7%94%B5%E5%8E%8B%E5%92%8C%E6%B8%A9%E5%BA%A6%E6%A3%80%E6%B5%8B%E3%80%82%3C%2FP%3E%3CP%3E%E5%9C%A8%E6%AD%A4%E9%85%8D%E7%BD%AE%E4%B8%8B%EF%BC%8C%E7%94%B5%E5%8E%8B%E5%92%8C%E6%B8%A9%E5%BA%A6%E4%BC%A0%E6%84%9F%E5%B7%A5%E4%BD%9C%E6%AD%A3%E5%B8%B8%EF%BC%8C%E4%BD%86%E7%94%B5%E6%B5%81%E4%BC%A0%E6%84%9F%E5%99%A8%E6%A3%80%E6%B5%8B%E5%88%B0%E7%9A%84%E6%98%AF%E5%B8%A6%E6%9C%89%E5%99%AA%E5%A3%B0%E7%9A%84%E5%8E%9F%E5%A7%8B%E5%80%BC%EF%BC%8C%E5%9B%A0%E6%AD%A4%E7%94%B5%E6%B5%81%E6%8E%A7%E5%88%B6%E4%B8%AD%E4%BC%9A%E5%87%BA%E7%8E%B0%E5%BC%82%E5%B8%B8%E5%B0%96%E5%B3%B0%E3%80%82%E6%AD%A4%E5%A4%96%EF%BC%8C%E6%88%91%E4%BB%AC%E5%B0%86%20Ctu%20%E6%A8%A1%E5%BC%8F%E4%BB%8E%E8%A7%A6%E5%8F%91%E6%A8%A1%E5%BC%8F%E6%94%B9%E4%B8%BA%E6%8E%A7%E5%88%B6%E6%A8%A1%E5%BC%8F%EF%BC%8C%E7%9B%AE%E5%89%8D%E4%BC%A0%E6%84%9F%E5%99%A8%E9%80%9A%E9%81%93%E7%9A%84%E5%8E%9F%E5%A7%8B%E5%80%BC%E5%99%AA%E5%A3%B0%E6%9C%89%E6%89%80%E9%99%8D%E4%BD%8E%E3%80%82%E4%BD%86%E6%98%AF%EF%BC%8C%E6%AD%A3%E5%B8%B8%E9%A2%91%E9%81%93%E4%B8%AD%E9%85%8D%E7%BD%AE%E7%9A%84%E5%85%B6%E4%BB%96%E9%A2%91%E9%81%93%E5%8D%B4%E6%97%A0%E6%B3%95%E5%B7%A5%E4%BD%9C%E3%80%82%3C%2FP%3E%3CP%3E%E6%88%91%E4%BB%AC%E6%9C%9F%E6%9C%9B%E4%BD%BF%E7%94%A8%E5%8D%95%E4%B8%AA%20ADC%20%E5%A4%96%E8%AE%BE%20(ADC0)%20%E8%BF%9B%E8%A1%8C%E7%94%B5%E6%B5%81%E6%A3%80%E6%B5%8B%EF%BC%8C%E9%87%87%E7%94%A8%20BCTU%20%E8%A7%A6%E5%8F%91%EF%BC%8C%E5%B9%B6%E9%87%87%E7%94%A8%E5%B8%B8%E8%A7%84%E9%93%BE%E5%BC%8F%E6%96%B9%E6%B3%95%E8%BF%9B%E8%A1%8C%E7%94%B5%E5%8E%8B%E5%92%8C%E6%B8%A9%E5%BA%A6%E6%A3%80%E6%B5%8B%EF%BC%8C%E8%80%8C%E4%B8%8D%E4%BC%9A%E5%87%BA%E7%8E%B0%E4%BB%BB%E4%BD%95%E5%B0%96%E5%B3%B0%E3%80%82%3C%2FP%3E%3CP%3E%3CSTRONG%3E%E6%B3%A8%E6%84%8F%3C%2FSTRONG%3E%EF%BC%9A%E6%88%91%E4%BB%AC%E7%9A%84%E7%A1%AC%E4%BB%B6%E8%AE%BE%E8%AE%A1%E6%9C%89%E9%85%8D%E7%BD%AE%EF%BC%88%E5%8D%B3%E5%BD%93%E5%89%8D%E4%BC%A0%E6%84%9F%E5%99%A8%E9%80%9A%E9%81%93%E9%85%8D%E7%BD%AE%E5%A6%82%E4%B8%8B%EF%BC%8CP7-ADC0%E3%80%81P2%20%E5%92%8C%20P3-ADC1%20%E7%94%A8%E4%BA%8E%20BCTU%20%E6%96%B9%E6%B3%95%E8%AF%BB%E5%8F%96%EF%BC%89%E3%80%82%E6%8E%A5%E4%B8%8B%E6%9D%A5%EF%BC%8C%E5%85%B6%E4%BD%99ADC%E9%80%9A%E9%81%93%E9%85%8D%E7%BD%AE%E4%B8%BA%E6%AD%A3%E5%B8%B8%E9%93%BE%E5%BC%8F%E6%96%B9%E6%B3%95%EF%BC%88ADC0%20-%20X0%E3%80%81X1%E3%80%81S19%20%E5%92%8C%20ADC1%20-%20P0%E3%80%81P2%E3%80%81P3%E3%80%81P1%E3%80%81S10%EF%BC%89%3C%2FP%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22ADC_Data1.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22ADC_Data1.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22ADC_Data1.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22ADC_Data1.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22ADC_Data1.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22ADC_Data1.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22ADC_Data1.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F390173i2190E72E8A90C7CE%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22ADC_Data1.png%22%20alt%3D%22ADC_Data1.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22ADC_Data2.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22ADC_Data2.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22ADC_Data2.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22ADC_Data2.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22ADC_Data2.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22ADC_Data2.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22ADC_Data2.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F390174i677783B99DE1F652%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22ADC_Data2.png%22%20alt%3D%22ADC_Data2.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22Screenshot%202026-06-25%20191818.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Screenshot%202026-06-25%20191818.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Screenshot%202026-06-25%20191818.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Screenshot%202026-06-25%20191818.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Screenshot%202026-06-25%20191818.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Screenshot%202026-06-25%20191818.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Screenshot%202026-06-25%20191818.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F390175i30E0CC3BACDD1A8C%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22Screenshot%202026-06-25%20191818.png%22%20alt%3D%22Screenshot%202026-06-25%20191818.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-LABS%20id%3D%22lingo-labs-2386456%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CLINGO-LABEL%3ES32K1%E7%B3%BB%E5%88%97%E7%9A%84S32SDK%3C%2FLINGO-LABEL%3E%3CLINGO-LABEL%3ES32V%20%E7%9A%84%20S32%20SDK%3C%2FLINGO-LABEL%3E%3C%2FLINGO-LABS%3E%3CLINGO-SUB%20id%3D%22lingo-sub-2386631%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%20translate%3D%22no%22%3ERe%3A%20S32k322%20ADC%20Configuration%20Issue%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-2386631%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%E4%BD%A0%E5%A5%BD%40%20%3CSPAN%3Epraveen_ext%3C%2FSPAN%3E%3C%2FP%3E%0A%3CP%3E%E6%88%91%E7%9B%B8%E4%BF%A1%E4%BD%A0%E9%81%87%E5%88%B0%E7%9A%84%E9%97%AE%E9%A2%98%E5%92%8C%E8%BF%99%E4%B8%AA%E4%B8%80%E6%A8%A1%E4%B8%80%E6%A0%B7%E3%80%82%3C%2FP%3E%0A%3CP%3E%3CA%20href%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2FS32K%2FDifference-in-ADC-noise-between-BCTU-Control-Mode-and-Trigger%2Ftd-p%2F2384122%22%20target%3D%22_blank%22%3Ehttps%3A%2F%2Fcommunity.nxp.com%2Ft5%2FS32K%2FDifference-in-ADC-noise-between-BCTU-Control-Mode-and-Trigger%2Ftd-p%2F2384122%3C%2FA%3E%3C%2FP%3E%0A%3CP%3E%E4%BB%8E%E4%BD%A0%E6%8F%90%E4%BE%9B%E7%9A%84%E6%88%AA%E5%9B%BE%E6%9D%A5%E7%9C%8B%EF%BC%8C%E4%BD%A0%E4%BC%BC%E4%B9%8E%E6%B2%A1%E6%9C%89%E5%AF%B9%E6%88%91%E4%B9%8B%E5%89%8D%E7%9A%84%E5%9B%9E%E5%A4%8D%E5%81%9A%E4%BB%BB%E4%BD%95%E4%BF%AE%E6%94%B9%E3%80%82%3C%2FP%3E%0A%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22Senlent_0-1782438264318.png%22%20style%3D%22width%3A%20449px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Senlent_0-1782438264318.png%22%20style%3D%22width%3A%20449px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Senlent_0-1782438264318.png%22%20style%3D%22width%3A%20449px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Senlent_0-1782438264318.png%22%20style%3D%22width%3A%20449px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Senlent_0-1782438264318.png%22%20style%3D%22width%3A%20449px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Senlent_0-1782438264318.png%22%20style%3D%22width%3A%20449px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Senlent_0-1782438264318.png%22%20style%3D%22width%3A%20449px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F390222iD7FB9C2AC274B747%2Fimage-dimensions%2F449x262%3Fv%3Dv2%22%20width%3D%22449%22%20height%3D%22262%22%20role%3D%22button%22%20title%3D%22Senlent_0-1782438264318.png%22%20alt%3D%22Senlent_0-1782438264318.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%0A%3CP%3E%E6%88%91%E5%B7%B2%E7%BB%8F%E5%91%8A%E7%9F%A5%E8%BF%87%E4%BD%A0%EF%BC%8C%E4%BD%A0%E7%9A%84ADC%E6%97%B6%E9%92%9F%E5%88%86%E9%A2%91%E5%99%A8%E9%85%8D%E7%BD%AE%E5%AD%98%E5%9C%A8%E9%97%AE%E9%A2%98%E3%80%82%3C%2FP%3E%0A%3CP%3E%E5%8F%A6%E5%A4%96%EF%BC%8C%E4%BD%A0%E7%A1%AE%E5%AE%9A%E4%BD%A0%E7%9A%84%E5%A4%96%E9%83%A8%E6%97%B6%E9%92%9F%E9%A2%91%E7%8E%87%E6%98%AF%2025MHz%20%E5%90%97%EF%BC%9F%3C%2FP%3E%0A%3CBR%20%2F%3E%0A%3CP%3E%E5%A6%82%E6%9E%9C%E6%82%A8%E5%B7%B2%E7%BB%8F%E6%A3%80%E6%9F%A5%E4%BA%86%E8%BF%99%E4%B8%A4%E7%82%B9%EF%BC%8C%E5%B9%B6%E4%B8%94%E5%9C%A8%E6%B5%8B%E8%AF%95%E5%90%8E%E9%97%AE%E9%A2%98%E4%BB%8D%E7%84%B6%E5%AD%98%E5%9C%A8%EF%BC%8C%E6%82%A8%E5%8F%AF%E4%BB%A5%E5%B0%9D%E8%AF%95%E4%BF%AE%E6%94%B9%20ADC%20%E9%80%9A%E9%81%93%E7%9A%84%E9%87%87%E6%A0%B7%E6%97%B6%E9%97%B4%E3%80%82%3C%2FP%3E%0A%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22Senlent_1-1782438511587.png%22%20style%3D%22width%3A%20486px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Senlent_1-1782438511587.png%22%20style%3D%22width%3A%20486px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Senlent_1-1782438511587.png%22%20style%3D%22width%3A%20486px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Senlent_1-1782438511587.png%22%20style%3D%22width%3A%20486px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Senlent_1-1782438511587.png%22%20style%3D%22width%3A%20486px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Senlent_1-1782438511587.png%22%20style%3D%22width%3A%20486px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Senlent_1-1782438511587.png%22%20style%3D%22width%3A%20486px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F390223iEF62F91EB9DBC358%2Fimage-dimensions%2F486x79%3Fv%3Dv2%22%20width%3D%22486%22%20height%3D%2279%22%20role%3D%22button%22%20title%3D%22Senlent_1-1782438511587.png%22%20alt%3D%22Senlent_1-1782438511587.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%0A%3CP%3E%E6%AD%A4%E9%80%89%E9%A1%B9%E5%85%81%E8%AE%B8%E6%82%A8%E4%BF%AE%E6%94%B9%E9%87%87%E6%A0%B7%E6%97%B6%E9%97%B4%EF%BC%9B%E6%82%A8%E5%8F%AF%E4%BB%A5%E5%B0%9D%E8%AF%95%E5%A2%9E%E5%8A%A0%E9%87%87%E6%A0%B7%E6%97%B6%E9%97%B4%E5%B9%B6%E5%86%8D%E6%AC%A1%E8%BF%9B%E8%A1%8C%E6%B5%8B%E8%AF%95%E3%80%82%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-2387030%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%20translate%3D%22no%22%3ERe%3A%20S32k322%20ADC%20Configuration%20Issue%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-2387030%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%E5%97%A8%3CA%20href%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fuser%2Fviewprofilepage%2Fuser-id%2F188029%22%20target%3D%22_blank%22%3E%40Senlent%3C%2FA%3E%20%EF%BC%8C%3CBR%20%2F%3E%3CBR%20%2F%3E%E6%88%91%E4%B9%9F%E6%9C%89%E5%92%8C%E4%BD%A0%E4%B8%8A%E9%9D%A2%E6%8F%90%E5%88%B0%E7%9A%84%E5%90%8C%E6%A0%B7%E7%9A%84%E9%97%AE%E9%A2%98%E3%80%82%3CBR%20%2F%3E%3CBR%20%2F%3E%E6%88%91%E4%BB%AC%E7%9A%84%E5%A4%96%E9%83%A8%E6%8C%AF%E8%8D%A1%E5%99%A8%E6%97%B6%E9%92%9F%E9%A2%91%E7%8E%87%E4%B8%BA%2025%20MHz%E3%80%82%E6%A0%B9%E6%8D%AE%20S32K322%20%E6%95%B0%E6%8D%AE%E6%89%8B%E5%86%8C%EF%BC%8CADC%20%E6%94%AF%E6%8C%81%E9%AB%98%E8%BE%BE%2080%20MHz%20%E7%9A%84%E9%A2%91%E7%8E%87%EF%BC%8C%E6%89%80%E4%BB%A5%E6%88%91%E5%B0%86%E9%A2%84%E5%88%86%E9%A2%91%E5%99%A8%E9%85%8D%E7%BD%AE%E4%B8%BA%202%E3%80%82%E6%88%91%E8%BF%98%E5%B0%86%E9%87%87%E6%A0%B7%E6%97%B6%E9%97%B4%E9%85%8D%E7%BD%AE%E4%B8%BA%201.2%20%E5%BE%AE%E7%A7%92%EF%BC%8C%E5%B9%B6%E5%B0%86%20BCTU%20%E6%A8%A1%E5%BC%8F%E8%AE%BE%E7%BD%AE%E4%B8%BA%E8%A7%A6%E5%8F%91%E4%BF%A1%E5%8F%B7%E6%A8%A1%E5%BC%8F%E3%80%82%E4%BD%86%E6%98%AF%EF%BC%8C%E5%BD%93%E5%9C%A8%E5%90%8C%E4%B8%80%E4%B8%AA%20ADC0%20%E5%A4%96%E8%AE%BE%E4%B8%8A%E5%90%8C%E6%97%B6%E6%89%A7%E8%A1%8C%20BCTU%20%E6%96%B9%E6%B3%95%E5%92%8C%E6%99%AE%E9%80%9A%E9%93%BE%E6%96%B9%E6%B3%95%E6%97%B6%EF%BC%8C%E6%88%91%E4%BB%AC%E4%BB%8D%E7%84%B6%E4%BC%9A%E5%BE%97%E5%88%B0%E5%99%AA%E5%A3%B0%E6%95%B0%E6%8D%AE%E3%80%82%E6%98%AF%E5%90%A6%E6%9C%89%E5%8F%98%E9%80%9A%E6%96%B9%E6%B3%95%E6%88%96%E6%9B%BF%E4%BB%A3%E6%96%B9%E6%B3%95%E5%8F%AF%E4%BB%A5%E5%AE%89%E5%85%A8%E5%9C%B0%E5%9C%A8%E5%90%8C%E4%B8%80%E4%B8%AA%20ADC0%20%E5%A4%96%E8%AE%BE%E4%B8%8A%E8%BF%90%E8%A1%8C%E8%BF%99%E4%B8%A4%E4%B8%AA%E7%A8%8B%E5%BA%8F%EF%BC%9F%3CBR%20%2F%3E%3CBR%20%2F%3E%3C%2FP%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22praveen_ext_0-1782473167287.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_0-1782473167287.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_0-1782473167287.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_0-1782473167287.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_0-1782473167287.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_0-1782473167287.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F390351iBC4A8A915270DE7C%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22praveen_ext_0-1782473167287.png%22%20alt%3D%22praveen_ext_0-1782473167287.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22praveen_ext_1-1782473350906.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_1-1782473350906.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_1-1782473350906.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_1-1782473350906.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_1-1782473350906.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_1-1782473350906.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F390352i2B2D151CC1349AAD%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22praveen_ext_1-1782473350906.png%22%20alt%3D%22praveen_ext_1-1782473350906.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22praveen_ext_2-1782473423830.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_2-1782473423830.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_2-1782473423830.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_2-1782473423830.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_2-1782473423830.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_2-1782473423830.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F390353iF5A48DEA700B87D2%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22praveen_ext_2-1782473423830.png%22%20alt%3D%22praveen_ext_2-1782473423830.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%3CBR%20%2F%3E%3CBR%20%2F%3E%3CBR%20%2F%3E%3CBR%20%2F%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-2388942%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%20translate%3D%22no%22%3ERe%3A%20S32k322%20ADC%20Configuration%20Issue%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-2388942%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%E4%BD%A0%E5%A5%BD%40%20%3CSPAN%3Epraveen_ext%3C%2FSPAN%3E%3C%2FP%3E%0A%3CP%3E%3CSPAN%3E%E4%BD%A0%E4%BB%AC%E4%B8%8D%E5%B0%B1%E6%98%AF%E5%90%8C%E4%B8%80%E5%AE%B6%E5%85%AC%E5%8F%B8%E5%90%97%EF%BC%9F%E4%BD%A0%E9%97%AE%E7%9A%84%E4%B9%9F%E6%98%AF%E5%90%8C%E6%A0%B7%E7%9A%84%E9%97%AE%E9%A2%98%E3%80%82%3C%2FSPAN%3E%3C%2FP%3E%0A%3CP%3E%3CSPAN%3E%3CA%20href%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2FS32K%2FDifference-in-ADC-noise-between-BCTU-Control-Mode-and-Trigger%2Fm-p%2F2384122%23M59412%22%20target%3D%22_blank%22%3Ehttps%3A%2F%2Fcommunity.nxp.com%2Ft5%2FS32K%2FDifference-in-ADC-noise-between-BCTU-Control-Mode-and-Trigger%2Fmp%2F2384122%23M59412%3C%2FA%3E%3C%2FSPAN%3E%3C%2FP%3E%0A%3CBR%20%2F%3E%0A%3CP%3E%3CSPAN%3E%E7%9C%8B%E6%9D%A5%E4%BD%A0%E6%B2%A1%E6%9C%89%E4%BB%94%E7%BB%86%E9%98%85%E8%AF%BB%E6%88%91%E7%9A%84%E5%9B%9E%E7%AD%94%E3%80%82%20%3C%2FSPAN%3E%3C%2FP%3E%0A%3CP%3E%3CSPAN%3E%E8%BF%99%E6%98%AF%E6%88%91%E7%AC%AC%E4%B8%89%E6%AC%A1%E5%91%8A%E8%AF%89%E4%BD%A0%EF%BC%8C%E4%BD%A0%E7%9A%84%E6%97%B6%E9%92%9F%E5%88%86%E9%A2%91%E5%99%A8%E8%AE%BE%E7%BD%AE%E4%B8%8D%E6%AD%A3%E7%A1%AE%E3%80%82%20%3C%2FSPAN%3E%3C%2FP%3E%0A%3CP%3E%3CSPAN%3E%E5%AF%B9%E4%BA%8E%20160MHz%EF%BC%8C%E4%BD%A0%E9%9C%80%E8%A6%81%E5%B0%86%E5%AE%83%E4%BB%AC%E8%AE%BE%E7%BD%AE%E4%B8%BA%202%20%E5%92%8C%204%E3%80%82%3C%2FSPAN%3E%3C%2FP%3E%0A%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22Senlent_0-1782897219790.png%22%20style%3D%22width%3A%20580px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Senlent_0-1782897219790.png%22%20style%3D%22width%3A%20580px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Senlent_0-1782897219790.png%22%20style%3D%22width%3A%20580px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Senlent_0-1782897219790.png%22%20style%3D%22width%3A%20580px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22Senlent_0-1782897219790.png%22%20style%3D%22width%3A%20580px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F390924i77CDC4C355CE4977%2Fimage-dimensions%2F580x71%3Fv%3Dv2%22%20width%3D%22580%22%20height%3D%2271%22%20role%3D%22button%22%20title%3D%22Senlent_0-1782897219790.png%22%20alt%3D%22Senlent_0-1782897219790.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%0A%3CBR%20%2F%3E%0A%3CBR%20%2F%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-2388936%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%20translate%3D%22no%22%3ERe%3A%20S32k322%20ADC%20Configuration%20Issue%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-2388936%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%3CSPAN%3E%E5%97%A8%3C%2FSPAN%3E%3CA%20href%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fuser%2Fviewprofilepage%2Fuser-id%2F188029%22%20target%3D%22_blank%22%3E%40Senlent%3C%2FA%3E%20%3CSPAN%3E%EF%BC%8C%3C%2FSPAN%3E%3CBR%20%2F%3E%3CBR%20%2F%3E%3CSPAN%3E%E6%88%91%E4%B9%9F%E6%9C%89%E5%92%8C%E4%BD%A0%E4%B8%8A%E9%9D%A2%E6%8F%90%E5%88%B0%E7%9A%84%E5%90%8C%E6%A0%B7%E7%9A%84%E9%97%AE%E9%A2%98%E3%80%82%3C%2FSPAN%3E%3CBR%20%2F%3E%3CBR%20%2F%3E%3CSPAN%3E%E6%88%91%E4%BB%AC%E7%9A%84%E5%A4%96%E9%83%A8%E6%8C%AF%E8%8D%A1%E5%99%A8%E6%97%B6%E9%92%9F%E9%A2%91%E7%8E%87%E4%B8%BA%2025%20MHz%E3%80%82%E6%A0%B9%E6%8D%AE%20S32K322%20%E6%95%B0%E6%8D%AE%E6%89%8B%E5%86%8C%EF%BC%8CADC%20%E6%94%AF%E6%8C%81%E6%9C%80%E9%AB%98%2080%20MHz%20%E7%9A%84%E9%A2%91%E7%8E%87%EF%BC%8C%E6%89%80%E4%BB%A5%E6%88%91%E5%B0%86%E9%A2%84%E5%88%86%E9%A2%91%E5%99%A8%E8%AE%BE%E7%BD%AE%E4%B8%BA%202%E3%80%82%E6%88%91%E8%BF%98%E5%B0%86%E9%87%87%E6%A0%B7%E6%97%B6%E9%97%B4%E8%AE%BE%E7%BD%AE%E4%B8%BA%201.2%20%E5%BE%AE%E7%A7%92%EF%BC%8C%E5%B9%B6%E5%B0%86%20BCTU%20%E6%A8%A1%E5%BC%8F%E8%AE%BE%E7%BD%AE%E4%B8%BA%E8%A7%A6%E5%8F%91%E6%A8%A1%E5%BC%8F%E3%80%82%E4%BD%86%E6%98%AF%EF%BC%8C%E5%BD%93%E5%9C%A8%E5%90%8C%E4%B8%80%E4%B8%AA%20ADC0%20%E5%A4%96%E8%AE%BE%E4%B8%8A%E5%90%8C%E6%97%B6%E6%89%A7%E8%A1%8C%20BCTU%20%E6%96%B9%E6%B3%95%E5%92%8C%E5%B8%B8%E8%A7%84%E9%93%BE%E5%BC%8F%E6%96%B9%E6%B3%95%E6%97%B6%EF%BC%8C%E4%BB%8D%E7%84%B6%E4%BC%9A%E5%BE%97%E5%88%B0%E5%99%AA%E5%A3%B0%E6%95%B0%E6%8D%AE%E3%80%82%E6%98%AF%E5%90%A6%E6%9C%89%E8%A7%A3%E5%86%B3%E6%96%B9%E6%B3%95%E6%88%96%E6%9B%BF%E4%BB%A3%E6%96%B9%E6%B3%95%E5%8F%AF%E4%BB%A5%E5%AE%89%E5%85%A8%E5%9C%B0%E5%9C%A8%E5%90%8C%E4%B8%80%E4%B8%AA%20ADC0%20%E5%A4%96%E8%AE%BE%E4%B8%8A%E8%BF%90%E8%A1%8C%E8%BF%99%E4%B8%A4%E7%A7%8D%E6%96%B9%E6%B3%95%EF%BC%9F%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%E4%B8%8E%E6%AD%A4%E5%90%8C%E6%97%B6%EF%BC%8C%E6%88%91%E5%B0%86%E5%AE%9E%E4%BE%8B%201%20%E7%9A%84%E6%97%B6%E9%92%9F%E9%A2%91%E7%8E%87%E9%99%8D%E4%BD%8E%E5%88%B0%2040%20MHz%EF%BC%8C%E5%B9%B6%E5%B0%86%E9%87%87%E6%A0%B7%E6%97%B6%E9%97%B4%E9%85%8D%E7%BD%AE%E4%B8%BA%201.2%20%E5%BE%AE%E7%A7%92%E3%80%82%E7%BB%8F%E8%BF%87%E8%BF%99%E4%BA%9B%E6%94%B9%E5%8F%98%E5%90%8E%EF%BC%8CBCTU%20%E7%9A%84%E6%B5%8B%E9%87%8F%E5%80%BC%E4%B8%8D%E5%86%8D%E6%98%BE%E7%A4%BA%E5%99%AA%E5%A3%B0%E3%80%82%3C%2FP%3E%3CDIV%3E%3CDIV%3E%3CSPAN%3EAdc_Raw_Val_Ph3%20%E4%B8%8E%E4%BC%A0%E6%84%9F%E5%99%A8%E8%BF%9E%E6%8E%A5%EF%BC%8C%E4%B8%A4%E4%B8%AA%E5%80%BC%E4%BB%8D%E7%84%B6%E5%A4%84%E4%BA%8E%E6%B5%AE%E7%A9%BA%E3%80%82%3C%2FSPAN%3E%3C%2FDIV%3E%3CDIV%3E%3CDIV%3E%3CDIV%3E%3CSPAN%3ERwaeVal%20-%20%E9%85%8D%E7%BD%AE%E6%AD%A3%E5%B8%B8%E9%93%BE%3C%2FSPAN%3E%3C%2FDIV%3E%3C%2FDIV%3E%3C%2FDIV%3E%3C%2FDIV%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22praveen_ext_0-1782473167287.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_0-1782473167287.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_0-1782473167287.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_0-1782473167287.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F390912iF0D4A14CEF781F1D%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22praveen_ext_0-1782473167287.png%22%20alt%3D%22praveen_ext_0-1782473167287.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22praveen_ext_1-1782473350906.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_1-1782473350906.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_1-1782473350906.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_1-1782473350906.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F390913i657FECB285EAF9A1%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22praveen_ext_1-1782473350906.png%22%20alt%3D%22praveen_ext_1-1782473350906.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22praveen_ext_2-1782473423830.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_2-1782473423830.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_2-1782473423830.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_2-1782473423830.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F390914iEF02BB62A6C6C5E1%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22praveen_ext_2-1782473423830.png%22%20alt%3D%22praveen_ext_2-1782473423830.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22praveen_ext_2-1782896838602.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_2-1782896838602.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_2-1782896838602.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_2-1782896838602.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F390916iF3C268C9A8B17C56%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22praveen_ext_2-1782896838602.png%22%20alt%3D%22praveen_ext_2-1782896838602.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22praveen_ext_5-1782896882736.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_5-1782896882736.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_5-1782896882736.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_5-1782896882736.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F390921iCEA0EA37451B487E%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22praveen_ext_5-1782896882736.png%22%20alt%3D%22praveen_ext_5-1782896882736.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22praveen_ext_6-1782896898785.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_6-1782896898785.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_6-1782896898785.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_6-1782896898785.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F390923i84F360666D5772F6%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22praveen_ext_6-1782896898785.png%22%20alt%3D%22praveen_ext_6-1782896898785.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%3CBR%20%2F%3E%3CBR%20%2F%3E%3CBR%20%2F%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-2389474%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%20translate%3D%22no%22%3ERe%3A%20S32k322%20ADC%20Configuration%20Issue%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-2389474%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%E5%97%A8%3CA%20href%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fuser%2Fviewprofilepage%2Fuser-id%2F188029%22%20target%3D%22_blank%22%3E%40Senlent%3C%2FA%3E%20%EF%BC%8C%3CBR%20%2F%3E%3CBR%20%2F%3E%E6%88%91%E4%BB%AC%E6%B5%8B%E8%AF%95%E4%BA%86%E4%B9%8B%E5%89%8D%E7%9A%84%E5%BB%BA%E8%AE%AE%EF%BC%8C%E4%BD%86%E9%97%AE%E9%A2%98%E4%BB%8D%E7%84%B6%E6%B2%A1%E6%9C%89%E8%A7%A3%E5%86%B3%E3%80%82%E7%BB%8F%E8%BF%87%E8%BF%9B%E4%B8%80%E6%AD%A5%E9%85%8D%E7%BD%AE%E5%92%8C%E9%AA%8C%E8%AF%81%EF%BC%8C%E6%88%91%E5%B7%B2%E5%B0%86%E6%9B%B4%E6%96%B0%E5%90%8E%E7%9A%84%E6%B5%8B%E8%AF%95%E6%95%B0%E6%8D%AE%E5%92%8C%E9%85%8D%E7%BD%AE%E5%9B%BE%E7%89%87%E9%99%84%E5%9C%A8%E4%B8%8B%E9%9D%A2%E3%80%82%3C%2FP%3E%3CP%3E%E8%AF%B7%E6%82%A8%E5%B8%AE%E5%BF%99%E6%8C%87%E5%87%BA%E6%88%91%E4%BB%AC%E9%81%97%E6%BC%8F%E7%9A%84%E5%9C%B0%E6%96%B9%E3%80%82%3C%2FP%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22praveen_ext_0-1782975094933.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_0-1782975094933.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_0-1782975094933.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F391048iA396B79E2C13A466%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22praveen_ext_0-1782975094933.png%22%20alt%3D%22praveen_ext_0-1782975094933.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%3CSTRONG%3EADC0%3C%2FSTRONG%3E%3C%2FP%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22praveen_ext_1-1782975139376.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_1-1782975139376.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_1-1782975139376.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F391049iE60A60EE55C7EDBF%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22praveen_ext_1-1782975139376.png%22%20alt%3D%22praveen_ext_1-1782975139376.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22praveen_ext_2-1782975176694.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_2-1782975176694.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_2-1782975176694.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F391050iA9D2037496A8CA0C%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22praveen_ext_2-1782975176694.png%22%20alt%3D%22praveen_ext_2-1782975176694.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%3CSTRONG%3EADC1%3C%2FSTRONG%3E%3C%2FP%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22praveen_ext_3-1782975241134.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_3-1782975241134.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_3-1782975241134.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F391051i7955C46CB5317BFE%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22praveen_ext_3-1782975241134.png%22%20alt%3D%22praveen_ext_3-1782975241134.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22praveen_ext_4-1782975291742.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_4-1782975291742.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22praveen_ext_4-1782975291742.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F391052i4F7A1329F096037D%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22praveen_ext_4-1782975291742.png%22%20alt%3D%22praveen_ext_4-1782975291742.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%3CBR%20%2F%3E%3CBR%20%2F%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-2389479%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%20translate%3D%22no%22%3ERe%3A%20S32k322%20ADC%20Configuration%20Issue%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-2389479%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%E4%BD%A0%E5%A5%BD%40%20%3CSPAN%3Epraveen_ext%3C%2FSPAN%3E%3C%2FP%3E%0A%3CP%3E%E8%AF%B7%E5%88%86%E4%BA%AB%E6%82%A8%E7%9A%84%E9%A1%B9%E7%9B%AE%EF%BC%8C%E6%88%91%E5%B0%86%E5%9C%A8%E6%88%91%E7%9A%84%E7%8E%AF%E5%A2%83%E4%B8%AD%E8%BF%9B%E8%A1%8C%E6%B5%8B%E8%AF%95%E3%80%82%3C%2FP%3E%3C%2FLINGO-BODY%3E