Hello Yogesh,
My question is:
Is it allowed and technically supported to reconfigure the watchdog timeout multiple times within the same power cycle on FS6500 or FS4500 devices?
If yes, are there any restrictions, specific sequences, or register access limitations that should be considered when changing the watchdog timeout after initial configuration?
[A] Yes, it is allowed to reconfigure the watchdog timeout within the same power cycle. It is also possible to se the Watchdog Window to infinitely open (allowed only in INIT_FS phase), meaning that if no watchdog refresh is sent, no error is generated.
You can reconfigure the watchdog timeout in the INIT_FS phase or in Normal mode.

With Best Regards,
Jozef