MPC5744 Register Protection
14,363 次查看
Jamber_H
Some modules, such as MC_ME, can set the Register Protection, as shown in the fig.1, but some other modules, such as CMU_0, can't use this function, and it's soft lock bit not exist, as shown in the fig.2.
Another question, in the Protected Registers list, why different modules have same Base Address? as shown in the fig.3, CMU0 and CMU1 has a same Base Address 0xFBFB0200, is it correct?
14,291 次查看
petervlna
The note is correct.
The base address for all CMUs is 0xFBFB_0000.
f the Base Address is 0xFBFB0000, the SoftLock bit should be 0xFBFB0000+0x3800=0xFBFB3800, but this address is still not accseeable as is shown in fig below. So could you tell me how to calculate the CMUs' Mirror Address, SoftLock Address and HardLock Address?
You calculation is not correct.
You have to take base address of the register: which for 0xFBFB_0200 which is only valid for CMU modules, for other peripherals your base is base address of module.
So for soft locking of CMU0_ CSR register you will do write to 0xFBFB_2200.
And lock register you will see at address 0xFBFB_3880 for CMU0_CSR.
Peter
11 回复数
8,187 次查看
mayank22
Hi Peter ,
These are the Modules on which I am implementing Locking mechanism under Register Protection for MPC5746C.  -
    0xFFFB0140, /* CMU------------*/
    0xFFFB0040, /* FXOSC----------*/
    0xFFFB0180, /* MC_CGM --------*/
    0xFFFB8000, /* MC_ME ---------*/
    0xFFFA8000, /* MC_RGM --------*/
    0xFFF50000, /* MEMU_0 -------*/
    0xFFFB0080, /* PLLDIG --------*/
    0xFFFA0400, /* PMCDIG --------*/
    0xFFFC0000, /* SIUL2 ---------*/
    0xFFFB0100, /* SXOSC ---------*/
    0xFFF9C000 /* LPU_CTL -------*/
what I am facing that some module GCR and SLB bit are throwing bus error if tried to access. similarly for those module it is soft/hard lock is working , I can still face the same problem for few registers set. I am attaching two samples of screen shots where first one is working and you can see all register/mirror/SLB and GCR addresses enabled while in second case SLB &GCR throws error if try to use them.
what could be the reason for this different behavior ? if u want I can attach my manual calculations for register/mirror/SLB and GCR addresses.
14,283 次查看
petervlna
To make it easy, here are macros which can be used for configuring register protection.
/*PowerPC*/
#define REGPROTPPMIRROR 0x2000
#define REGPROTPPSLBR 0x3800
#define REGPROTPPGCR 0x3FFC
#define WRITE_WITH_LOCK_PP_8BIT(registeraddress, value)
#define WRITE_WITH_LOCK_PP_16BIT(registeraddress, value)
#define WRITE_WITH_LOCK_PP_32BIT(registeraddress, value)
#define GET_SOFTLOCK_PP(modulebaseaddress, registeraddress, value)
#define CLR_SOFTLOCK_PP_32BIT(modulebaseaddress, registeraddress)
#define CLR_SOFTLOCK_PP_16BIT(modulebaseaddress, registeraddress)
#define CLR_SOFTLOCK_PP_8BIT(modulebaseaddress, registeraddress)
#define SET_SOFTLOCK_PP_32BIT(modulebaseaddress, registeraddress)
#define SET_SOFTLOCK_PP_16BIT(modulebaseaddress, registeraddress)
#define SET_SOFTLOCK_PP_8BIT(modulebaseaddress, registeraddress)
#define SET_HARDLOCK_PP(modulebaseaddress)
#define USER_ACCESS_FORBIDDEN_PP(modulebaseaddress)
#define USER_ACCESS_ALLOWED_PP(modulebaseaddress)
 And usecase example:
 //16k - 32 bit,CAN1
CAN_6.MCR.B.MDIS = 0x0;
WRITE_WITH_LOCK_16K_32BIT((&CAN_6.MCR.R), 0xD890000F);
GET_SOFTLOCK_16K(&CAN_6, &CAN_6.MCR.R,&testik);
CLR_SOFTLOCK_16K_32BIT(&CAN_6, &CAN_6.MCR.R);
SET_SOFTLOCK_16K_32BIT(&CAN_6, &CAN_6.MCR.R);
//SET_HARDLOCK_16k(&CAN_6);
CAN_6.MCR.B.MDIS = 0x1;
USER_ACCESS_FORBIDDEN_16k(&CAN_6);
GET_GCR_16K(&CAN_6,&GCRvalue);
USER_ACCESS_ALLOWED_16k(&CAN_6);
14,279 次查看
Jamber_H
Hi Peter,
Thank you for your reply. Now I know what the NOTE means, which is a keypoint, and I have had a test, it works well.
Jamber
14,325 次查看
petervlna
Only registers listed in appendix A can be locked by register protection:
So not all registers in module support this feature. Usually its only safety relevant.
Well, that is copy paste typo in manual, please have a look at manual Addendum instead:
Here are the addresses:
#define CMU_0 (*(volatile struct CMU_tag *) 0xFBFB0200UL)
#define CMU_1 (*(volatile struct CMU_tag *) 0xFBFB0240UL)
#define CMU_2 (*(volatile struct CMU_tag *) 0xFBFB0280UL)
#define CMU_3 (*(volatile struct CMU_tag *) 0xFBFB02C0UL)
#define CMU_4 (*(volatile struct CMU_tag *) 0xFBFB0300UL)
Peter
14,319 次查看
Jamber_H
Hi Peter,
I think I find the answer, but I don't understand. Thanks for your screenshot I saw the NOTE and it said " All CMUs modules are in the same protected region with the base address aligned to the 16k - 0xFBFB_0000", what's the meaning of this?
If the Base Address is 0xFBFB0000, the SoftLock bit should be 0xFBFB0000+0x3800=0xFBFB3800, but this address is still not accseeable as is shown in fig below. So could you tell me how to calculate the CMUs' Mirror Address, SoftLock Address and HardLock Address?
It's so funny different with other modules.
Jamber
14,292 次查看
petervlna
Peter
14,278 次查看
Jamber_H
Hi Peter,
I think it's better understand if modified the value of "Offset" of CMU in Table2-77 to 0x200, 0x208, 0x20C, et.al. but now I get it anyway, thank you.
Best Regards
Jamber
14,322 次查看
Jamber_H
Hi Peter,
"Only registers listed in appendix A can be locked by register protection:", what confused me is the CMU0 module is right in the Appendix A, but I can't access its SoftLock bit, and I post the screenshot in my question.
Jamber
14,314 次查看
petervlna
Hmm strange,
I was not aware of this. Trying to think about how to calculate the address.
Let me test it here and I will come back to you ASAP.
best regards,
Peter
14,341 次查看
Jamber_H
Could someone help me please?
14,348 次查看
Jamber_H
I Test MC_ME, CMU, ADC, CTU, PWM, only CMU is failed to set softlock, other modules can set softlock succussfully. Why?
%3CLINGO-SUB%20id%3D%22lingo-sub-1261074%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3EMPC5744%20%E5%AF%84%E5%AD%98%E5%99%A8%E4%BF%9D%E6%8A%A4%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1261074%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%E4%BD%A0%E5%A5%BD%E3%80%81%20%3C%2FP%3E%3CP%3E%E6%9C%89%E4%BA%9B%E6%A8%A1%E5%9D%97%EF%BC%88%E5%A6%82%20MC_ME%EF%BC%89%E5%8F%AF%E4%BB%A5%E8%AE%BE%E7%BD%AE%E5%AF%84%E5%AD%98%E5%99%A8%E4%BF%9D%E6%8A%A4%EF%BC%8C%E5%A6%82%E5%9B%BE%201%20%E6%89%80%E7%A4%BA%EF%BC%8C%E4%BD%86%E6%9C%89%E4%BA%9B%E6%A8%A1%E5%9D%97%EF%BC%88%E5%A6%82%20CMU_0%EF%BC%89%E5%88%99%E6%97%A0%E6%B3%95%E4%BD%BF%E7%94%A8%E8%AF%A5%E5%8A%9F%E8%83%BD%EF%BC%8C%E4%B9%9F%E4%B8%8D%E5%AD%98%E5%9C%A8%E8%BD%AF%E9%94%81%E5%AE%9A%E4%BD%8D%EF%BC%8C%E5%A6%82%E5%9B%BE%202%20%E6%89%80%E7%A4%BA%E3%80%82%3C%2FP%3E%3CP%3E%E5%8F%A6%E4%B8%80%E4%B8%AA%E9%97%AE%E9%A2%98%E6%98%AF%EF%BC%8C%E5%9C%A8%E5%8F%97%E4%BF%9D%E6%8A%A4%E5%AF%84%E5%AD%98%E5%99%A8%E5%88%97%E8%A1%A8%E4%B8%AD%EF%BC%8C%E4%B8%BA%E4%BB%80%E4%B9%88%E4%B8%8D%E5%90%8C%E6%A8%A1%E5%9D%97%E7%9A%84%E5%9F%BA%E5%9C%B0%E5%9D%80%E7%9B%B8%E5%90%8C%EF%BC%9FCMU0%20%E5%92%8C%20CMU1%20%E5%85%B7%E6%9C%89%E7%9B%B8%E5%90%8C%E7%9A%84%E5%9F%BA%E5%9C%B0%E5%9D%80%200xFBFB0200%EF%BC%8C%E5%AF%B9%E5%90%97%EF%BC%9F%3C%2FP%3E%3CBR%20%2F%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%222021-04-13_151624.png%22%20style%3D%22width%3A%20400px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%222021-04-13_151624.png%22%20style%3D%22width%3A%20400px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F142103i750DC5EEDAB03D7C%2Fimage-size%2Fmedium%3Fv%3Dv2%26amp%3Bpx%3D400%22%20role%3D%22button%22%20title%3D%222021-04-13_151624.png%22%20alt%3D%222021-04-13_151624.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%E2%80%83%3C%2FP%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%222021-04-13_151502.png%22%20style%3D%22width%3A%20400px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%222021-04-13_151502.png%22%20style%3D%22width%3A%20400px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F142104i7268E737D5078B55%2Fimage-size%2Fmedium%3Fv%3Dv2%26amp%3Bpx%3D400%22%20role%3D%22button%22%20title%3D%222021-04-13_151502.png%22%20alt%3D%222021-04-13_151502.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%E2%80%83%3C%2FP%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%222021-04-13_152957.png%22%20style%3D%22width%3A%20400px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%222021-04-13_152957.png%22%20style%3D%22width%3A%20400px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F142105i2BD0A71F38211B49%2Fimage-size%2Fmedium%3Fv%3Dv2%26amp%3Bpx%3D400%22%20role%3D%22button%22%20title%3D%222021-04-13_152957.png%22%20alt%3D%222021-04-13_152957.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%E2%80%83%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-2134847%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%20translate%3D%22no%22%3ERe%3A%20MPC5744%20Register%20Protection%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-2134847%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%E5%97%A8%EF%BC%8C%E5%BD%BC%E5%BE%97%20%E3%80%81%3C%2FP%3E%3CP%3E%E8%BF%99%E4%BA%9B%E6%98%AF%E6%88%91%E4%B8%BA%20MPC5746C%20%E5%AE%9E%E7%8E%B0%E5%AF%84%E5%AD%98%E5%99%A8%E4%BF%9D%E6%8A%A4%E4%B8%8B%E9%94%81%E5%AE%9A%E6%9C%BA%E5%88%B6%E7%9A%84%E6%A8%A1%E5%9D%97%E3%80%82%20%3CSPAN%3E%20-%20%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%20%20%20%200xFFFB0140%2C%20%2F*%20CMU------------*%2F%3C%2FP%3E%3CP%3E%20%20%20%200xFFFB0040%2C%20%2F*%20FXOSC----------*%2F%3C%2FP%3E%3CP%3E%20%20%20%200xFFFB0180%2C%20%2F*%20MC_CGM%20--------*%2F%3C%2FP%3E%3CP%3E%20%20%20%200xFFFB8000%2C%20%2F*%20MC_ME%20---------*%2F%3C%2FP%3E%3CP%3E%20%20%20%200xFFFA8000%2C%20%2F*%20MC_RGM%20--------*%2F%3C%2FP%3E%3CP%3E%20%20%20%200xFFF50000%2C%20%2F*%20MEMU_0%20-------*%2F%3C%2FP%3E%3CP%3E%20%20%20%200xFFFB0080%2C%20%2F*%20PLLDIG%20--------*%2F%3C%2FP%3E%3CP%3E%20%20%20%200xFFFA0400%2C%20%2F*%20PMCDIG%20--------*%2F%3C%2FP%3E%3CP%3E%20%20%20%200xFFFC0000%2C%20%2F*%20SIUL2%20---------*%2F%3C%2FP%3E%3CP%3E%20%20%20%200xFFFB0100%2C%20%2F*%20SXOSC%20---------*%2F%3C%2FP%3E%3CP%3E%20%20%20%200xFFF9C000%20%2F*%20LPU_CTL%20-------*%2F%3C%2FP%3E%3CP%3E%E6%88%91%E9%9D%A2%E4%B8%B4%E7%9A%84%E9%97%AE%E9%A2%98%E6%98%AF%EF%BC%8C%E5%A6%82%E6%9E%9C%E5%B0%9D%E8%AF%95%E8%AE%BF%E9%97%AE%E6%9F%90%E4%BA%9B%E6%A8%A1%E5%9D%97%20GCR%20%E5%92%8C%20SLB%20%E4%BD%8D%E4%BC%9A%E5%BC%95%E5%8F%91%E6%80%BB%E7%BA%BF%E9%94%99%E8%AF%AF%E3%80%82%E5%90%8C%E6%A0%B7%EF%BC%8C%E5%AF%B9%E4%BA%8E%E9%82%A3%E4%BA%9B%E8%BD%AF%2F%E7%A1%AC%E9%94%81%E6%AD%A3%E5%B8%B8%E5%B7%A5%E4%BD%9C%E7%9A%84%E6%A8%A1%E5%9D%97%EF%BC%8C%E6%88%91%E5%9C%A8%E8%AE%BE%E7%BD%AE%E5%87%A0%E4%B8%AA%E5%AF%84%E5%AD%98%E5%99%A8%E6%97%B6%E4%BB%8D%E7%84%B6%E4%BC%9A%E9%81%87%E5%88%B0%E5%90%8C%E6%A0%B7%E7%9A%84%E9%97%AE%E9%A2%98%E3%80%82%E6%88%91%E5%9C%A8%E9%99%84%E4%BB%B6%E4%B8%AD%E6%8F%90%E4%BE%9B%E4%BA%86%E4%B8%A4%E4%B8%AA%E5%B1%8F%E5%B9%95%E6%88%AA%E5%9B%BE%E6%A0%B7%E6%9C%AC%EF%BC%8C%E7%AC%AC%E4%B8%80%E4%B8%AA%E6%A0%B7%E6%9C%AC%E6%AD%A3%E5%B8%B8%E5%B7%A5%E4%BD%9C%EF%BC%8C%E5%8F%AF%E4%BB%A5%E7%9C%8B%E5%88%B0%E6%89%80%E6%9C%89%E5%AF%84%E5%AD%98%E5%99%A8%2F%E9%95%9C%E5%83%8F%2FSLB%20%E5%92%8C%20GCR%20%E5%9C%B0%E5%9D%80%E9%83%BD%E5%B7%B2%E5%90%AF%E7%94%A8%EF%BC%8C%E8%80%8C%E5%9C%A8%E7%AC%AC%E4%BA%8C%E4%B8%AA%E6%A0%B7%E6%9C%AC%E4%B8%AD%EF%BC%8C%E5%A6%82%E6%9E%9C%E5%B0%9D%E8%AF%95%E4%BD%BF%E7%94%A8%20SLB%26amp%3BGCR%EF%BC%8C%E5%88%99%E4%BC%9A%E5%87%BA%E7%8E%B0%E9%94%99%E8%AF%AF%E3%80%82%20%3C%2FP%3E%3CP%3E%E5%87%BA%E7%8E%B0%E8%BF%99%E7%A7%8D%E4%B8%8D%E5%90%8C%E8%A1%8C%E4%B8%BA%E7%9A%84%E5%8E%9F%E5%9B%A0%E6%98%AF%E4%BB%80%E4%B9%88%EF%BC%9F%E5%A6%82%E6%9E%9C%E6%82%A8%E9%9C%80%E8%A6%81%EF%BC%8C%E6%88%91%E5%8F%AF%E4%BB%A5%E9%99%84%E4%B8%8A%E5%AF%84%E5%AD%98%E5%99%A8%2F%E9%95%9C%E5%83%8F%2FSLB%20%E5%92%8C%20GCR%20%E5%9C%B0%E5%9D%80%E7%9A%84%E6%89%8B%E5%B7%A5%E8%AE%A1%E7%AE%97%E7%BB%93%E6%9E%9C%E3%80%82%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1263496%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%20translate%3D%22no%22%3ERe%3A%20MPC5744%20Register%20Protection%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1263496%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%E5%97%A8%EF%BC%8C%E5%BD%BC%E5%BE%97%E3%80%81%3C%2FP%3E%3CP%3E%E5%A6%82%E6%9E%9C%E5%B0%86%E8%A1%A8%202-77%20%E4%B8%AD%20CMU%22Offset%22%20%E7%9A%84%E5%80%BC%E4%BF%AE%E6%94%B9%E4%B8%BA%200x200%E3%80%810x208%E3%80%810x20C%20%E7%AD%89%EF%BC%8C%E6%88%91%E8%AE%A4%E4%B8%BA%E4%BC%9A%E6%9B%B4%E5%A5%BD%E7%90%86%E8%A7%A3%E3%80%82%E4%BD%86%E7%8E%B0%E5%9C%A8%E6%88%91%E6%98%8E%E7%99%BD%E4%BA%86%EF%BC%8C%E8%B0%A2%E8%B0%A2%E4%BD%A0%E3%80%82%3C%2FP%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%222021-04-16_184156.png%22%20style%3D%22width%3A%20400px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%222021-04-16_184156.png%22%20style%3D%22width%3A%20400px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F142512i791DB299DAAF1E20%2Fimage-size%2Fmedium%3Fv%3Dv2%26amp%3Bpx%3D400%22%20role%3D%22button%22%20title%3D%222021-04-16_184156.png%22%20alt%3D%222021-04-16_184156.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%E2%80%83%3C%2FP%3E%3CP%3E%E9%A1%BA%E7%A5%9D%E5%95%86%E7%A5%BA%EF%BC%81%3C%2FP%3E%3CP%3EJamber%3C%2FP%3E%3CBR%20%2F%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1263490%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%20translate%3D%22no%22%3ERe%3A%20MPC5744%20Register%20Protection%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1263490%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%E5%97%A8%EF%BC%8C%E5%BD%BC%E5%BE%97%E3%80%81%3C%2FP%3E%3CP%3E%E8%B0%A2%E8%B0%A2%E6%82%A8%E7%9A%84%E7%AD%94%E5%A4%8D%E3%80%82%E7%8E%B0%E5%9C%A8%E6%88%91%E7%9F%A5%E9%81%93%20%22%E6%B3%A8%E9%87%8A%20%22%E6%98%AF%E4%BB%80%E4%B9%88%E6%84%8F%E6%80%9D%E4%BA%86%EF%BC%8C%E8%BF%99%E6%98%AF%E4%B8%80%E4%B8%AA%E5%85%B3%E9%94%AE%E7%82%B9%EF%BC%8C%E8%80%8C%E4%B8%94%E6%88%91%E8%BF%98%E8%BF%9B%E8%A1%8C%E4%BA%86%E6%B5%8B%E8%AF%95%EF%BC%8C%E6%95%88%E6%9E%9C%E5%BE%88%E5%A5%BD%E3%80%82%3C%2FP%3E%3CP%3E%E9%A1%BA%E7%A5%9D%E5%95%86%E7%A5%BA%EF%BC%81%3C%2FP%3E%3CP%3EJamber%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1263438%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%20translate%3D%22no%22%3ERe%3A%20MPC5744%20Register%20Protection%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1263438%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%E4%BD%A0%E5%A5%BD%3C%2FP%3E%0A%3CP%3E%E4%B8%BA%E6%96%B9%E4%BE%BF%E8%B5%B7%E8%A7%81%EF%BC%8C%E4%BB%A5%E4%B8%8B%E6%98%AF%E5%8F%AF%E7%94%A8%E4%BA%8E%E9%85%8D%E7%BD%AE%E5%AF%84%E5%AD%98%E5%99%A8%E4%BF%9D%E6%8A%A4%E7%9A%84%E5%AE%8F%E3%80%82%3C%2FP%3E%0A%3CPRE%20translate%3D%22no%22%3E%2F*PowerPC*%2F%3CBR%20%2F%3E%3CBR%20%2F%3E%2F*-----------------------------------------------------------------------------------------------------------*%2F%3CBR%20%2F%3E%23define%20REGPROTPPMIRROR%200x2000%3CBR%20%2F%3E%23define%20REGPROTPPSLBR%200x3800%3CBR%20%2F%3E%23define%20REGPROTPPGCR%200x3FFC%3CBR%20%2F%3E%3CBR%20%2F%3E%23define%20WRITE_WITH_LOCK_PP_8BIT(registeraddress%2C%20value)%26nbsp%3B%26nbsp%3B%26nbsp%3B%3CBR%20%2F%3E%23define%20WRITE_WITH_LOCK_PP_16BIT(registeraddress%2C%20value)%26nbsp%3B%26nbsp%3B%26nbsp%3B%3CBR%20%2F%3E%23define%20WRITE_WITH_LOCK_PP_32BIT(registeraddress%2C%20value)%26nbsp%3B%26nbsp%3B%26nbsp%3B%3CBR%20%2F%3E%3CBR%20%2F%3E%23define%20GET_SOFTLOCK_PP(modulebaseaddress%2C%20registeraddress%2C%20value)%3CBR%20%2F%3E%23define%20CLR_SOFTLOCK_PP_32BIT(modulebaseaddress%2C%20registeraddress)%3CBR%20%2F%3E%23define%20CLR_SOFTLOCK_PP_16BIT(modulebaseaddress%2C%20registeraddress)%3CBR%20%2F%3E%23define%20CLR_SOFTLOCK_PP_8BIT(modulebaseaddress%2C%20registeraddress)%3CBR%20%2F%3E%3CBR%20%2F%3E%23define%20SET_SOFTLOCK_PP_32BIT(modulebaseaddress%2C%20registeraddress)%3CBR%20%2F%3E%23define%20SET_SOFTLOCK_PP_16BIT(modulebaseaddress%2C%20registeraddress)%3CBR%20%2F%3E%23define%20SET_SOFTLOCK_PP_8BIT(modulebaseaddress%2C%20registeraddress)%3CBR%20%2F%3E%3CBR%20%2F%3E%23define%20SET_HARDLOCK_PP(modulebaseaddress)%3CBR%20%2F%3E%23define%20USER_ACCESS_FORBIDDEN_PP(modulebaseaddress)%3CBR%20%2F%3E%23define%20USER_ACCESS_ALLOWED_PP(modulebaseaddress)%3C%2FPRE%3E%0A%3CP%3E%E4%BD%BF%E7%94%A8%E5%AE%9E%E4%BE%8B%3C%2FP%3E%0A%3CDIV%20style%3D%22box-sizing%3A%20border-box%3B%20font-family%3A%20'Segoe%20UI'%2C%20system-ui%2C%20'Apple%20Color%20Emoji'%2C%20'Segoe%20UI%20Emoji'%2C%20sans-serif%3B%20font-size%3A%2014px%3B%20font-style%3A%20normal%3B%20font-variant-ligatures%3A%20normal%3B%20font-variant-caps%3A%20normal%3B%20font-weight%3A%20400%3B%20letter-spacing%3A%20normal%3B%20orphans%3A%202%3B%20text-align%3A%20start%3B%20text-indent%3A%200px%3B%20text-transform%3A%20none%3B%20white-space%3A%20normal%3B%20widows%3A%202%3B%20word-spacing%3A%200px%3B%22%3E%0A%3CPRE%20translate%3D%22no%22%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%20%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%3CSPAN%20style%3D%22color%3A%20%236888c9%3B%22%3E%2F%2F16k%20-%2032%20bit%2CCAN1%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20CAN_6.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMCR%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EB%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMDIS%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20%3D%200x0%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20WRITE_WITH_LOCK_16K_32BIT((%26amp%3BCAN_6.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMCR%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3ER%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E)%2C%200xD890000F)%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20GET_SOFTLOCK_16K(%26amp%3BCAN_6%2C%20%26amp%3BCAN_6.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMCR%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3ER%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%2C%26amp%3Btestik)%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20CAN_6.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMCR%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EB%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMDIS%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20%3D%200x0%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20CLR_SOFTLOCK_16K_32BIT(%26amp%3BCAN_6%2C%20%26amp%3BCAN_6.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMCR%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3ER%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E)%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20GET_SOFTLOCK_16K(%26amp%3BCAN_6%2C%20%26amp%3BCAN_6.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMCR%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3ER%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%2C%26amp%3Btestik)%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20CAN_6.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMCR%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EB%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMDIS%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20%3D%200x0%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20SET_SOFTLOCK_16K_32BIT(%26amp%3BCAN_6%2C%20%26amp%3BCAN_6.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMCR%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3ER%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E)%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20GET_SOFTLOCK_16K(%26amp%3BCAN_6%2C%20%26amp%3BCAN_6.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMCR%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3ER%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%2C%26amp%3Btestik)%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%20%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%3CSPAN%20style%3D%22color%3A%20%236888c9%3B%22%3E%2F%2FSET_HARDLOCK_16k(%26amp%3BCAN_6)%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20CLR_SOFTLOCK_16K_32BIT(%26amp%3BCAN_6%2C%20%26amp%3BCAN_6.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMCR%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3ER%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E)%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20GET_SOFTLOCK_16K(%26amp%3BCAN_6%2C%20%26amp%3BCAN_6.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMCR%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3ER%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%2C%26amp%3Btestik)%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20CAN_6.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMCR%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EB%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMDIS%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20%3D%200x1%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20USER_ACCESS_FORBIDDEN_16k(%26amp%3BCAN_6)%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20GET_GCR_16K(%26amp%3BCAN_6%2C%26amp%3BGCRvalue)%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20CAN_6.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMCR%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EB%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMDIS%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20%3D%200x0%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20USER_ACCESS_ALLOWED_16k(%26amp%3BCAN_6)%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20GET_GCR_16K(%26amp%3BCAN_6%2C%26amp%3BGCRvalue)%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20CAN_6.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMCR%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EB%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E.%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3EMDIS%3C%2FSPAN%3E%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20%3D%200x0%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20SET_HARDLOCK_16k(%26amp%3BCAN_6)%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3CBR%20%2F%3E%3CSPAN%20style%3D%22font-size%3A%2011pt%3B%22%3E%3CSPAN%3E%3CSPAN%20style%3D%22font-family%3A%20Calibri%2Csans-serif%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%2010.0pt%3B%22%3E%3CSPAN%20style%3D%22font-family%3A%20Consolas%3B%22%3E%20GET_GCR_16K(%26amp%3BCAN_6%2C%26amp%3BGCRvalue)%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FPRE%3E%0A%3C%2FDIV%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1263427%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%20translate%3D%22no%22%3ERe%3A%20MPC5744%20Register%20Protection%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1263427%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%E4%BD%A0%E5%A5%BD%3C%2FP%3E%0A%3CP%3E%E6%B3%A8%E9%87%8A%E6%98%AF%E6%AD%A3%E7%A1%AE%E7%9A%84%E3%80%82%3C%2FP%3E%0A%3CP%3E%E6%89%80%E6%9C%89%20CMU%20%E7%9A%84%E5%9F%BA%E5%9C%B0%E5%9D%80%E5%9D%87%E4%B8%BA%20%3CFONT%20color%3D%22%23FF0000%22%3E%3CSPAN%20class%3D%22fontstyle0%22%3E0xFBFB_0000%3C%2FSPAN%3E%3C%2FFONT%3E.%3C%2FP%3E%0A%3CBLOCKQUOTE%3E%0A%3CP%3E%E5%A6%82%E6%9E%9C%E5%9F%BA%E5%9C%B0%E5%9D%80%E4%B8%BA%200xFBFB0000%EF%BC%8C%E5%88%99%E8%BD%AF%E9%94%81%E5%AE%9A%E4%BD%8D%E5%BA%94%E8%AF%A5%E4%B8%BA%200xFBFB0000%2B0x3800%3D0xFBFB3800%EF%BC%8C%E4%BD%86%E5%A6%82%E4%B8%8B%E5%9B%BE%E6%89%80%E7%A4%BA%EF%BC%8C%E8%AF%A5%E5%9C%B0%E5%9D%80%E4%BB%8D%E7%84%B6%E4%B8%8D%E5%8F%AF%E6%B5%8B%E3%80%82%E6%82%A8%E8%83%BD%E5%91%8A%E8%AF%89%E6%88%91%E5%A6%82%E4%BD%95%E8%AE%A1%E7%AE%97%20CMU%20%E7%9A%84%E9%95%9C%E5%83%8F%E5%9C%B0%E5%9D%80%E3%80%81%E8%BD%AF%E9%94%81%E5%9C%B0%E5%9D%80%E5%92%8C%E7%A1%AC%E9%94%81%E5%9C%B0%E5%9D%80%E5%90%97%EF%BC%9F%3C%2FP%3E%0A%3C%2FBLOCKQUOTE%3E%0A%3CP%3E%E4%BD%A0%E7%9A%84%E8%AE%A1%E7%AE%97%E4%B8%8D%E6%AD%A3%E7%A1%AE%E3%80%82%3C%2FP%3E%0A%3CP%3E%E6%82%A8%E5%BF%85%E9%A1%BB%E4%BD%BF%E7%94%A8%E5%AF%84%E5%AD%98%E5%99%A8%E7%9A%84%E5%9F%BA%E5%9C%B0%E5%9D%80%EF%BC%9A0xFBFB_0200%20%E4%BB%85%E9%80%82%E7%94%A8%E4%BA%8E%20CMU%20%E6%A8%A1%E5%9D%97%EF%BC%8C%E5%AF%B9%E4%BA%8E%E5%85%B6%E4%BB%96%E5%A4%96%E8%AE%BE%EF%BC%8C%E6%82%A8%E7%9A%84%E5%9F%BA%E5%9C%B0%E5%9D%80%E6%98%AF%E6%A8%A1%E5%9D%97%E7%9A%84%E5%9F%BA%E5%9C%B0%E5%9D%80%E3%80%82%3C%2FP%3E%0A%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22petervlna_1-1618563997092.png%22%20style%3D%22width%3A%20532px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22petervlna_1-1618563997092.png%22%20style%3D%22width%3A%20532px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F142492i488A18CFB3D0B5CE%2Fimage-dimensions%2F532x28%3Fv%3Dv2%22%20width%3D%22532%22%20height%3D%2228%22%20role%3D%22button%22%20title%3D%22petervlna_1-1618563997092.png%22%20alt%3D%22petervlna_1-1618563997092.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FP%3E%0A%3CBR%20%2F%3E%0A%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22petervlna_0-1618563954927.png%22%20style%3D%22width%3A%20400px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22petervlna_0-1618563954927.png%22%20style%3D%22width%3A%20400px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F142491i8D71FFF8F2B0CCA9%2Fimage-size%2Fmedium%3Fv%3Dv2%26amp%3Bpx%3D400%22%20role%3D%22button%22%20title%3D%22petervlna_0-1618563954927.png%22%20alt%3D%22petervlna_0-1618563954927.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FP%3E%0A%3CP%3E%E5%9B%A0%E6%AD%A4%EF%BC%8C%E8%A6%81%E8%BD%AF%E9%94%81%E5%AE%9A%20CMU0_%20CSR%20%E5%AF%84%E5%AD%98%E5%99%A8%EF%BC%8C%E9%9C%80%E8%A6%81%E5%86%99%E5%85%A5%200xFBFB_2200%E3%80%82%3C%2FP%3E%0A%3CP%3E%E9%94%81%E5%AE%9A%E5%AF%84%E5%AD%98%E5%99%A8%E7%9A%84%E5%9C%B0%E5%9D%80%E4%B8%BA%200xFBFB_3880%EF%BC%8C%E5%8D%B3%20CMU0_CSR%E3%80%82%3C%2FP%3E%0A%3CP%3E%E9%A1%BA%E7%A5%9D%E5%95%86%E7%A5%BA%EF%BC%81%3C%2FP%3E%0A%3CP%3EPeter%3C%2FP%3E%0A%3CBR%20%2F%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1262757%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%20translate%3D%22no%22%3ERe%3A%20MPC5744%20Register%20Protection%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1262757%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%E5%97%AF%EF%BC%8C%E5%A5%87%E6%80%AA%E3%80%81%3C%2FP%3E%0A%3CP%3E%E6%88%91%E5%B9%B6%E4%B8%8D%E7%9F%A5%E9%81%93%E8%BF%99%E4%B8%80%E7%82%B9%E3%80%82%E6%AD%A3%E5%9C%A8%E8%80%83%E8%99%91%E5%A6%82%E4%BD%95%E8%AE%A1%E7%AE%97%E5%9C%B0%E5%9D%80%E3%80%82%3C%2FP%3E%0A%3CP%3E%E8%AE%A9%E6%88%91%E5%9C%A8%E8%BF%99%E9%87%8C%E6%B5%8B%E8%AF%95%E4%B8%80%E4%B8%8B%EF%BC%8C%E6%88%91%E4%BC%9A%E5%B0%BD%E5%BF%AB%E7%BB%99%E4%BD%A0%E7%AD%94%E5%A4%8D%E3%80%82%3C%2FP%3E%0A%3CP%3E%E9%A1%BA%E7%A5%9D%E5%95%86%E7%A5%BA%EF%BC%81%3C%2FP%3E%0A%3CP%3EPeter%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1262681%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%20translate%3D%22no%22%3ERe%3A%20MPC5744%20Register%20Protection%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1262681%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%E5%97%A8%EF%BC%8C%E5%BD%BC%E5%BE%97%E3%80%81%3C%2FP%3E%3CP%3E%E6%88%91%E6%83%B3%E6%88%91%E6%89%BE%E5%88%B0%E7%AD%94%E6%A1%88%E4%BA%86%EF%BC%8C%E4%BD%86%E6%88%91%E4%B8%8D%E6%98%8E%E7%99%BD%E3%80%82%E6%84%9F%E8%B0%A2%E6%82%A8%E7%9A%84%E6%88%AA%E5%9B%BE%EF%BC%8C%E6%88%91%E7%9C%8B%E5%88%B0%E4%BA%86%E6%B3%A8%E9%87%8A%EF%BC%8C%E4%B8%8A%E9%9D%A2%E5%86%99%E7%9D%80%22%20%3CFONT%20color%3D%22%23FF0000%22%3E%3CSPAN%20class%3D%22fontstyle0%22%3E%E6%89%80%E6%9C%89%20CMU%20%E6%A8%A1%E5%9D%97%E9%83%BD%E5%9C%A8%E5%90%8C%E4%B8%80%E4%BF%9D%E6%8A%A4%E5%8C%BA%E5%9F%9F%EF%BC%8C%E5%9F%BA%E5%9C%B0%E5%9D%80%E5%AF%B9%E9%BD%90%E5%88%B0%2016k%20-%200xFBFB_0000%3C%2FSPAN%3E%3C%2FFONT%3E%22%E8%BF%99%E6%98%AF%E4%BB%80%E4%B9%88%E6%84%8F%E6%80%9D%EF%BC%9F%3C%2FP%3E%3CP%3E%E5%A6%82%E6%9E%9C%E5%9F%BA%E5%9C%B0%E5%9D%80%E6%98%AF%200xFBFB0000%EF%BC%8C%E8%BD%AF%E9%94%81%E5%AE%9A%E4%BD%8D%E5%BA%94%E8%AF%A5%E6%98%AF%200xFBFB0000%2B0x3800%3D0xFBFB3800%EF%BC%8C%E4%BD%86%E5%A6%82%E4%B8%8B%E5%9B%BE%E6%89%80%E7%A4%BA%EF%BC%8C%E8%AF%A5%E5%9C%B0%E5%9D%80%E4%BB%8D%E7%84%B6%E4%B8%8D%E5%8F%AF%E6%B5%8B%E3%80%82%E6%82%A8%E8%83%BD%E5%91%8A%E8%AF%89%E6%88%91%E5%A6%82%E4%BD%95%E8%AE%A1%E7%AE%97%20CMU%20%E7%9A%84%E9%95%9C%E5%83%8F%E5%9C%B0%E5%9D%80%E3%80%81%E8%BD%AF%E9%94%81%E5%9C%B0%E5%9D%80%E5%92%8C%E7%A1%AC%E9%94%81%E5%9C%B0%E5%9D%80%E5%90%97%EF%BC%9F%3C%2FP%3E%3CP%3E%E4%B8%8E%E5%85%B6%E4%BB%96%E6%A8%A1%E5%9D%97%E4%B8%8D%E5%90%8C%EF%BC%8C%E5%AE%83%E6%98%AF%E5%A6%82%E6%AD%A4%E6%9C%89%E8%B6%A3%E3%80%82%3C%2FP%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%222021-04-15_164430.png%22%20style%3D%22width%3A%20400px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%222021-04-15_164430.png%22%20style%3D%22width%3A%20400px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F142350iCB5F08904AF719C7%2Fimage-size%2Fmedium%3Fv%3Dv2%26amp%3Bpx%3D400%22%20role%3D%22button%22%20title%3D%222021-04-15_164430.png%22%20alt%3D%222021-04-15_164430.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%222021-04-15_164141.png%22%20style%3D%22width%3A%20400px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%222021-04-15_164141.png%22%20style%3D%22width%3A%20391px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F142351iC911E02E1280A248%2Fimage-size%2Fmedium%3Fv%3Dv2%26amp%3Bpx%3D400%22%20role%3D%22button%22%20title%3D%222021-04-15_164141.png%22%20alt%3D%222021-04-15_164141.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%E9%A1%BA%E7%A5%9D%E5%95%86%E7%A5%BA%EF%BC%81%3C%2FP%3E%3CP%3EJamber%3C%2FP%3E%3CP%3E%E2%80%83%3C%2FP%3E%3CP%3E%E2%80%83%3C%2FP%3E%3CBR%20%2F%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1262639%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%20translate%3D%22no%22%3ERe%3A%20MPC5744%20Register%20Protection%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1262639%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%E5%97%A8%EF%BC%8C%E5%BD%BC%E5%BE%97%E3%80%81%20%3C%2FP%3E%3CP%3E%3CSPAN%3E%E6%84%9F%E8%B0%A2%E6%82%A8%E7%9A%84%E5%9B%9E%E5%A4%8D%E3%80%82%20%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%3CSPAN%3E%22%3C%2FSPAN%3E%3CFONT%20color%3D%22%230000FF%22%3E%3CEM%3E%E5%8F%AA%E6%9C%89%E9%99%84%E5%BD%95%20A%20%E4%B8%AD%E5%88%97%E5%87%BA%E7%9A%84%E5%AF%84%E5%AD%98%E5%99%A8%E5%8F%AF%E4%BB%A5%E8%A2%AB%E5%AF%84%E5%AD%98%E5%99%A8%E4%BF%9D%E6%8A%A4%E9%94%81%E5%AE%9A%EF%BC%9A%3C%2FEM%3E%3C%2FFONT%3E%3CSPAN%3E%22%E4%BB%A4%E6%88%91%E5%9B%B0%E6%83%91%E7%9A%84%E6%98%AF%EF%BC%8CCMU0%20%E6%A8%A1%E5%9D%97%E5%B0%B1%E5%9C%A8%E9%99%84%E5%BD%95%20A%20%E4%B8%AD%EF%BC%8C%E4%BD%86%E6%88%91%E6%97%A0%E6%B3%95%E8%AE%BF%E9%97%AE%E5%85%B6%20SoftLock%20%E4%BD%8D%EF%BC%8C%E6%88%91%E5%9C%A8%E9%97%AE%E9%A2%98%E4%B8%AD%E8%B4%B4%E5%87%BA%E4%BA%86%E6%88%AA%E5%9B%BE%E3%80%82%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%3CSPAN%3E%E9%A1%BA%E7%A5%9D%E5%95%86%E7%A5%BA%EF%BC%81%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%3CSPAN%3EJamber%3C%2FSPAN%3E%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1262586%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%20translate%3D%22no%22%3ERe%3A%20MPC5744%20Register%20Protection%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1262586%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%E4%BD%A0%E5%A5%BD%3C%2FP%3E%0A%3CP%3E%E5%8F%AA%E6%9C%89%E9%99%84%E5%BD%95%20A%20%E4%B8%AD%E5%88%97%E5%87%BA%E7%9A%84%E5%AF%84%E5%AD%98%E5%99%A8%E5%8F%AF%E4%BB%A5%E8%A2%AB%E5%AF%84%E5%AD%98%E5%99%A8%E4%BF%9D%E6%8A%A4%E9%94%81%E5%AE%9A%EF%BC%9A%3C%2FP%3E%0A%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22petervlna_0-1618472142468.png%22%20style%3D%22width%3A%20400px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22petervlna_0-1618472142468.png%22%20style%3D%22width%3A%20400px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F142330i186C0B3B86FA91C2%2Fimage-size%2Fmedium%3Fv%3Dv2%26amp%3Bpx%3D400%22%20role%3D%22button%22%20title%3D%22petervlna_0-1618472142468.png%22%20alt%3D%22petervlna_0-1618472142468.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FP%3E%0A%3CP%3E%E5%9B%A0%E6%AD%A4%EF%BC%8C%E5%B9%B6%E9%9D%9E%E6%89%80%E6%9C%89%E6%A8%A1%E5%9D%97%E4%B8%AD%E7%9A%84%E5%AF%84%E5%AD%98%E5%99%A8%E9%83%BD%E6%94%AF%E6%8C%81%E8%BF%99%E4%B8%80%E5%8A%9F%E8%83%BD%E3%80%82%E9%80%9A%E5%B8%B8%E5%AE%83%E5%8F%AA%E4%B8%8E%E5%8A%9F%E8%83%BD%E5%AE%89%E5%85%A8%E6%9C%89%E5%85%B3%E3%80%82%3C%2FP%3E%0A%3CBLOCKQUOTE%3E%0A%3CP%3E%E5%8F%A6%E4%B8%80%E4%B8%AA%E9%97%AE%E9%A2%98%E6%98%AF%EF%BC%8C%E5%9C%A8%E5%8F%97%E4%BF%9D%E6%8A%A4%E5%AF%84%E5%AD%98%E5%99%A8%E5%88%97%E8%A1%A8%E4%B8%AD%EF%BC%8C%E4%B8%BA%E4%BB%80%E4%B9%88%E4%B8%8D%E5%90%8C%E6%A8%A1%E5%9D%97%E7%9A%84%E5%9F%BA%E5%9C%B0%E5%9D%80%E7%9B%B8%E5%90%8C%EF%BC%9FCMU0%20%E5%92%8C%20CMU1%20%E5%85%B7%E6%9C%89%E7%9B%B8%E5%90%8C%E7%9A%84%E5%9F%BA%E5%9C%B0%E5%9D%80%200xFBFB0200%EF%BC%8C%E5%AF%B9%E5%90%97%EF%BC%9F%3C%2FP%3E%0A%3C%2FBLOCKQUOTE%3E%0A%3CP%3E%E8%BF%99%E6%98%AF%E6%89%8B%E5%86%8C%E4%B8%AD%E7%9A%84%E5%A4%8D%E5%88%B6%E7%B2%98%E8%B4%B4%E9%94%99%E5%AD%97%EF%BC%8C%E8%AF%B7%E6%9F%A5%E9%98%85%E6%89%8B%E5%86%8C%E9%99%84%E5%BD%95%EF%BC%9A%3C%2FP%3E%0A%3CP%3E%E5%9C%B0%E5%9D%80%E5%A6%82%E4%B8%8B%3C%2FP%3E%0A%3CP%3E%23define%20CMU_0%20(*(volatile%20struct%20CMU_tag%20*)%200xFBFB0200UL)%3CBR%20%2F%3E%23define%20CMU_1%20(*(volatile%20struct%20CMU_tag%20*)%200xFBFB0240UL)%3CBR%20%2F%3E%23define%20CMU_2%20(*(volatile%20struct%20CMU_tag%20*)%200xFBFB0280UL)%20%23define%20CMU_3%20(*(volatile%20struct%20CMU_tag%20*)%200xFBFB02C0UL)%3CBR%20%2F%3E%23define%20CMU_3%20(*(volatile%20struct%20CMU_tag%20*)%200xFBFB02C0UL)%3CBR%20%2F%3E%23define%20CMU_4%20(*(volatile%20struct%20CMU_tag%20*)%200xFBFB0300UL)%3C%2FP%3E%0A%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22petervlna_1-1618472584102.png%22%20style%3D%22width%3A%20400px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22petervlna_1-1618472584102.png%22%20style%3D%22width%3A%20400px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F142334i8F23C73A19733F3A%2Fimage-size%2Fmedium%3Fv%3Dv2%26amp%3Bpx%3D400%22%20role%3D%22button%22%20title%3D%22petervlna_1-1618472584102.png%22%20alt%3D%22petervlna_1-1618472584102.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FP%3E%0A%3CP%3E%E9%A1%BA%E7%A5%9D%E5%95%86%E7%A5%BA%EF%BC%81%3C%2FP%3E%0A%3CP%3EPeter%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1262009%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%20translate%3D%22no%22%3ERe%3A%20MPC5744%20Register%20Protection%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1262009%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%E8%B0%81%E8%83%BD%E5%B8%AE%E5%B8%AE%E6%88%91%EF%BC%9F%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1261623%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%20translate%3D%22no%22%3ERe%3A%20MPC5744%20Register%20Protection%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1261623%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3EI%20%E6%B5%8B%E8%AF%95%20MC_ME%E3%80%81CMU%E3%80%81ADC%E3%80%81CTU%E3%80%81PWM%EF%BC%8C%E5%8F%AA%E6%9C%89%20CMU%20%E8%AE%BE%E7%BD%AE%E8%BD%AF%E9%94%81%E5%AE%9A%E5%A4%B1%E8%B4%A5%EF%BC%8C%E5%85%B6%E4%BB%96%E6%A8%A1%E5%9D%97%E5%8F%AF%E6%88%90%E5%8A%9F%E8%AE%BE%E7%BD%AE%E8%BD%AF%E9%94%81%E5%AE%9A%E3%80%82%E4%B8%BA%E4%BB%80%E4%B9%88%EF%BC%9F%3C%2FP%3E%3C%2FLINGO-BODY%3E