Example MPC5744P TSENS temperature calculation GHS614
* Detailed Description:
* Example shows MCU's temperature measurement with the help of TSENS.
* Calibartion constants for TSENS0 and TSENS1 are read from Test Flash and
* ADC0/ADC1 is set to measure Vbg and TSENS outputs.
* Calculated internal temperature can be desplayed on the Terminal.
* EVB connection:
*   Route LINFlexD_0 TXD/RXD (PB2/PB3) signals to the main board RS-232 transceiver
*   Daughtercard:
*   J17.11–12 ON  .. Connect LINFlexD_0 TXD (PB2) to main board.
*   J17.8–9 ON .. Connect LINFlexD_0 RXD (PB3) to main board.
*   Motherboard
*   J14 - SCI_RX ON
*   J13 - SCI_TX ON
*   J25 - SCI_PWR ON
* See results on PC terminal (19200, 8N1, None). You should get following text
* (with different values for sure)
* TSENS0/TSENS1 temperature measurement
* press any key to continue...
* Calibration constants read from Test Flash
* TSENS0                           TSENS1
* K1 = 429                         K1 = -220
* K2 = -5785                       K2 = -5767
* K3 = -12800                      K3 = -12736
* K4 = 45                          K4 = 45
*      K1 * Vbg_code * 2^-1 + K2 * TSENS_code * 2^3
* T = ------------------------------------------------------------------------- / 4 - 273.15 [degC]
*     [K3 * Vbg_code * 2^2 + K4 * TSENS_code] * 2^-10
* Vbg0_code      = 1502               Vbg1_code      = 1502
* TSENS0_code = 2002               TSENS1_code = 1988
* TSENS0 temp = 34.57 degC         TSENS1 temp = 36.78 degC
* Test HW:  MPC57xx
* Maskset:  1N65H
* Target :  RAM, internal_FLASH
* Fsys:     200 MHz PLL with 40 MHz crystal reference
* Terminal: 19200, 8N1, None
附件
评论
Hi petr,
we download your demo program and run it in our DEMO board. The program seems some problem puzzles me.
When we download the HEX of the example program to 5744pq9  chip, and make it go,  we can see the result of MCU temperature calculate is not stable.
below is the screenshot of Lauterbach debugger.
we can see that the MCU temperature oscillates in -10 and 50 degree. it is obviously not correct.
So , can you help me to find the reason of this phenomenon.
Thank you very much.
Any body help me?
I checked it on the MPC5744P EVB and got this result
so hard to say.
What is the full part number you are using?
BR, Petr
Hi Petr,
Thank for your response.
We found that the Vbg0_code and Vbg1_code that acquired by ADC is also not very stable. Can you help me to check your Vbg0_code and Vbg1_code ?
The DEMO program we used is your attachment without changing.
hi Petr,
we have some new discovery.
When we used the CTU to trigger ADC to acquire Vbg0_code or Vbg1_code, the ADC value is not stable.
But when we used register to trigger ADC to acquire Vbg0_code or Vbg1_code, the ADC value seems stabled.
Why?
our CTU trigger ADC period is 100 us, is it too fast?
hi Petr,
i am waiting for your response.
Pat
Hi Liu,
I guess, I had the same problem as you. Here is the answer of the support :"...it is necessary to increase the sampling time for band gap due to slow internal capacitance....".
Since, a note is added in the RM, ADC_CTR0 field descriptions, Bit 24-31 INPSAMP :
   NOTE: The Bandgap voltage sampling time is controlled by CTR0[INPSAMP]. CTR0[INPSAMP] is also
   used for the external channel sample time. When the user software needs to sample the
   Bandgap voltage, it must change the CTR0[INPSAMP] value to allow for a longer time while the
   Bandgap is being sampled, then change its value back to the normal value for sampling external
   channels.
Pat
hi pat,
thanks for your response.
now i understand why i should change the CTR0[INPSAMP] value to allow for a longer time while the  Bandgap is being sampled.
can you give me a suggest value of CTR0[INPSAMP] for sampling the Bandgap?    Because  i hope the value is not very big. the big value of CTR0[INPSAMP] will effect more of my basic software scheduler.
Pat
Hi liu,
A value of 0x50 has been suggested by the design team, which is strongly custom hardware/PCB dependent like noise on voltage reference, etc...  So, be careful.
Pat
Maybe you need modify the code:
// TSEN1 temperature calculation
    ADC_1.MCR.B.NSTART = 1;                       /* Trigger normal conversions for ADC1 */
    while(ADC_1.CDR[15].B.VALID != 1) {};         /* Wait for last scan to complete */
    Vbg1_Code = ADC_1.CDR[10].B.CDATA;
    TSENS1_Code = ADC_1.CDR[15].B.CDATA;
    temp1 = K1_1 * Vbg1_Code / 2 + K2_1 * TSENS1_Code * 8;
    temp2 = (K3_1 * Vbg1_Code * 4 + K4_1 * TSENS1_Code) * 0.0009765625;
    TSENS1_T = temp1 / temp2 / 4 - 273.15;
%3CLINGO-SUB%20id%3D%22lingo-sub-1122429%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%E7%A4%BA%E4%BE%8B%20MPC5744P%20TSENS%20%E6%B8%A9%E5%BA%A6%E8%AE%A1%E7%AE%97%20GHS614%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1122429%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%26lt%3Bmeta%20http-equiv%3D%22Content-Type%22%20content%3D%22text%2Fhtml%3B%20charset%3Dutf-8%22%20%2F%26gt%3B%0A%3CP%3E********************************************************************************%3C%2FP%3E%3CP%3E*%20%E8%AF%A6%E7%BB%86%E8%AF%B4%E6%98%8E%EF%BC%9A%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20%E7%A4%BA%E4%BE%8B%E5%B1%95%E7%A4%BA%E4%BA%86%E5%80%9F%E5%8A%A9%20TSENS%20%E8%BF%9B%E8%A1%8C%20MCU%20%E7%9A%84%E6%B8%A9%E5%BA%A6%E6%B5%8B%E9%87%8F%E3%80%82%3C%2FP%3E%3CP%3E*%20TSENS0%20%E5%92%8C%20TSENS1%20%E7%9A%84%E6%A0%A1%E5%87%86%E5%B8%B8%E6%95%B0%E4%BB%8E%E6%B5%8B%E8%AF%95%E9%97%AA%E5%AD%98%E4%B8%AD%E8%AF%BB%E5%8F%96%EF%BC%8C%3C%2FP%3E%3CP%3E*%20ADC0%2FADC1%20%E8%AE%BE%E7%BD%AE%E4%B8%BA%E6%B5%8B%E9%87%8F%20Vbg%20%E5%92%8C%20TSENS%20%E8%BE%93%E5%87%BA%E3%80%82%3C%2FP%3E%3CP%3E*%20%E8%AE%A1%E7%AE%97%E5%87%BA%E7%9A%84%E5%86%85%E9%83%A8%E6%B8%A9%E5%BA%A6%E5%8F%AF%E4%BB%A5%E6%98%BE%E7%A4%BA%E5%9C%A8%E7%BB%88%E7%AB%AF%E4%B8%8A%E3%80%82%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20EVB%E8%BF%9E%E6%8E%A5%EF%BC%9A%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20%E5%B0%86%20LINFlexD_0%20TXD%2FRXD%EF%BC%88PB2%2FPB3%EF%BC%89%E4%BF%A1%E5%8F%B7%E8%B7%AF%E7%94%B1%E8%87%B3%E4%B8%BB%E6%9D%BF%20RS-232%20%E6%94%B6%E5%8F%91%E5%99%A8%3C%2FP%3E%3CP%3E*%20%E5%AD%90%E5%8D%A1%EF%BC%9A%3C%2FP%3E%3CP%3E*%20J17.11%E2%80%9312ON%20..%20%E5%B0%86%20LINFlexD_0%20TXD%20(PB2)%20%E8%BF%9E%E6%8E%A5%E5%88%B0%E4%B8%BB%E6%9D%BF%E3%80%82%3C%2FP%3E%3CP%3E*%20J17.8%E2%80%939%E5%BC%80%E5%90%AF..%E5%B0%86%20LINFlexD_0%20RXD%20(PB3)%20%E8%BF%9E%E6%8E%A5%E5%88%B0%E4%B8%BB%E6%9D%BF%E3%80%82%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20%20%E6%AF%8D%E6%9D%BF%3C%2FP%3E%3CP%3E*%20J14%E2%80%94%E2%80%94SCI_RX%E5%BC%80%E5%90%AF%3C%2FP%3E%3CP%3E*%20J13-SCI_TX%E5%BC%80%E5%90%AF%3C%2FP%3E%3CP%3E*%20J25%E2%80%94%E2%80%94SCI_PWR%E5%BC%80%E5%90%AF%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20%E6%9F%A5%E7%9C%8B%20PC%20%E7%BB%88%E7%AB%AF%E4%B8%8A%E7%9A%84%E7%BB%93%E6%9E%9C%EF%BC%8819200%E3%80%818N1%E3%80%81%E6%97%A0%EF%BC%89%E3%80%82%E6%82%A8%E5%BA%94%E8%AF%A5%E7%9C%8B%E5%88%B0%E4%BB%A5%E4%B8%8B%E6%96%87%E6%9C%AC%3C%2FP%3E%3CP%3E*%EF%BC%88%E8%82%AF%E5%AE%9A%E6%9C%89%E4%B8%8D%E5%90%8C%E7%9A%84%E5%80%BC%EF%BC%89%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20TSENS0%2FTSENS1%20%E6%B8%A9%E5%BA%A6%E6%B5%8B%E9%87%8F%3C%2FP%3E%3CP%3E*%20%E6%8C%89%E4%BB%BB%E6%84%8F%E9%94%AE%E7%BB%A7%E7%BB%AD...%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20%E4%BB%8E%E6%B5%8B%E8%AF%95%E9%97%AA%E5%AD%98%E8%AF%BB%E5%8F%96%E7%9A%84%E6%A0%A1%E5%87%86%E5%B8%B8%E6%95%B0%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20TSENS0%20TSENS1%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20K1%20%3D%20429%20K1%20%3D%20-220%3C%2FP%3E%3CP%3E*%20K2%20%3D%20-5785%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%20K2%20%3D%20-5767%3C%2FP%3E%3CP%3E*%20K3%20%3D%20-12800%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%20K3%20%3D%20-12736%3C%2FP%3E%3CP%3E*%20K4%20%3D%2045%20K4%20%3D%2045%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20K1%20*%20Vbg_code%20*%202%5E-1%20%2B%20K2%20*%20TSENS_code%20*%202%5E3%3C%2FP%3E%3CP%3E*%20T%20%3D%20-------------------------------------------------------------------------%20%2F%204%20-%20273.15%20%5B%E6%91%84%E6%B0%8F%E5%BA%A6%5D%3C%2FP%3E%3CP%3E*%20%5BK3%20*%20Vbg_code%20*%202%5E2%20%2B%20K4%20*%20TSENS_code%5D%20*%202%5E-10%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20Vbg0_code%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%20%3D%201502%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%20Vbg1_code%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%20%3D%201502%3C%2FP%3E%3CP%3E*%20TSENS0_%E4%BB%A3%E7%A0%81%20%3D%202002%20TSENS1_%E4%BB%A3%E7%A0%81%20%3D%201988%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20TSENS0%20%E6%B8%A9%E5%BA%A6%20%3D%2034.57%20%E6%91%84%E6%B0%8F%E5%BA%A6%20TSENS1%20%E6%B8%A9%E5%BA%A6%20%3D%2036.78%20%E6%91%84%E6%B0%8F%E5%BA%A6%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20------------------------------------------------------------------------------%3C%2FP%3E%3CP%3E*%20%E6%B5%8B%E8%AF%95%E7%A1%AC%E4%BB%B6%EF%BC%9AMPC57xx%3C%2FP%3E%3CP%3E*%20Maskset%3A%26nbsp%3B%201N65H%3C%2FP%3E%3CP%3E*%20%E7%9B%AE%E6%A0%87%EF%BC%9ARAM%E3%80%81%E5%86%85%E9%83%A8%E9%97%AA%E5%AD%98%3C%2FP%3E%3CP%3E*%20Fsys%3A%20200%20MHz%20PLL%EF%BC%8C%E5%B8%A6%2040%20MHz%20%E6%99%B6%E6%8C%AF%E5%8F%82%E8%80%83%3C%2FP%3E%3CP%3E*%20%E7%BB%88%E7%AB%AF%EF%BC%9A19200%E3%80%818N1%E3%80%81%E6%97%A0%3C%2FP%3E%3CP%3E********************************************************************************%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-TEASER%20id%3D%22lingo-teaser-1122429%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%26lt%3Bmeta%20http-equiv%3D%22Content-Type%22%20content%3D%22text%2Fhtml%3B%20charset%3Dutf-8%22%20%2F%26gt%3B%0A%3CP%3E********************************************************************************%3C%2FP%3E%3CP%3E*%20%E8%AF%A6%E7%BB%86%E8%AF%B4%E6%98%8E%EF%BC%9A%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20%E7%A4%BA%E4%BE%8B%E5%B1%95%E7%A4%BA%E4%BA%86%E5%80%9F%E5%8A%A9%20TSENS%20%E8%BF%9B%E8%A1%8C%20MCU%20%E7%9A%84%E6%B8%A9%E5%BA%A6%E6%B5%8B%E9%87%8F%E3%80%82%3C%2FP%3E%3CP%3E*%20TSENS0%20%E5%92%8C%20TSENS1%20%E7%9A%84%E6%A0%A1%E5%87%86%E5%B8%B8%E6%95%B0%E4%BB%8E%E6%B5%8B%E8%AF%95%E9%97%AA%E5%AD%98%E4%B8%AD%E8%AF%BB%E5%8F%96%EF%BC%8C%3C%2FP%3E%3CP%3E*%20ADC0%2FADC1%20%E8%AE%BE%E7%BD%AE%E4%B8%BA%E6%B5%8B%E9%87%8F%20Vbg%20%E5%92%8C%20TSENS%20%E8%BE%93%E5%87%BA%E3%80%82%3C%2FP%3E%3CP%3E*%20%E8%AE%A1%E7%AE%97%E5%87%BA%E7%9A%84%E5%86%85%E9%83%A8%E6%B8%A9%E5%BA%A6%E5%8F%AF%E4%BB%A5%E6%98%BE%E7%A4%BA%E5%9C%A8%E7%BB%88%E7%AB%AF%E4%B8%8A%E3%80%82%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20EVB%E8%BF%9E%E6%8E%A5%EF%BC%9A%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20%E5%B0%86%20LINFlexD_0%20TXD%2FRXD%EF%BC%88PB2%2FPB3%EF%BC%89%E4%BF%A1%E5%8F%B7%E8%B7%AF%E7%94%B1%E8%87%B3%E4%B8%BB%E6%9D%BF%20RS-232%20%E6%94%B6%E5%8F%91%E5%99%A8%3C%2FP%3E%3CP%3E*%20%E5%AD%90%E5%8D%A1%EF%BC%9A%3C%2FP%3E%3CP%3E*%20J17.11%E2%80%9312ON%20..%20%E5%B0%86%20LINFlexD_0%20TXD%20(PB2)%20%E8%BF%9E%E6%8E%A5%E5%88%B0%E4%B8%BB%E6%9D%BF%E3%80%82%3C%2FP%3E%3CP%3E*%20J17.8%E2%80%939%E5%BC%80%E5%90%AF..%E5%B0%86%20LINFlexD_0%20RXD%20(PB3)%20%E8%BF%9E%E6%8E%A5%E5%88%B0%E4%B8%BB%E6%9D%BF%E3%80%82%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20%20%E6%AF%8D%E6%9D%BF%3C%2FP%3E%3CP%3E*%20J14%E2%80%94%E2%80%94SCI_RX%E5%BC%80%E5%90%AF%3C%2FP%3E%3CP%3E*%20J13-SCI_TX%E5%BC%80%E5%90%AF%3C%2FP%3E%3CP%3E*%20J25%E2%80%94%E2%80%94SCI_PWR%E5%BC%80%E5%90%AF%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20%E6%9F%A5%E7%9C%8B%20PC%20%E7%BB%88%E7%AB%AF%E4%B8%8A%E7%9A%84%E7%BB%93%E6%9E%9C%EF%BC%8819200%E3%80%818N1%E3%80%81%E6%97%A0%EF%BC%89%E3%80%82%E6%82%A8%E5%BA%94%E8%AF%A5%E7%9C%8B%E5%88%B0%E4%BB%A5%E4%B8%8B%E6%96%87%E6%9C%AC%3C%2FP%3E%3CP%3E*%EF%BC%88%E8%82%AF%E5%AE%9A%E6%9C%89%E4%B8%8D%E5%90%8C%E7%9A%84%E5%80%BC%EF%BC%89%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20TSENS0%2FTSENS1%20%E6%B8%A9%E5%BA%A6%E6%B5%8B%E9%87%8F%3C%2FP%3E%3CP%3E*%20%E6%8C%89%E4%BB%BB%E6%84%8F%E9%94%AE%E7%BB%A7%E7%BB%AD...%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20%E4%BB%8E%E6%B5%8B%E8%AF%95%E9%97%AA%E5%AD%98%E8%AF%BB%E5%8F%96%E7%9A%84%E6%A0%A1%E5%87%86%E5%B8%B8%E6%95%B0%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20TSENS0%20TSENS1%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20K1%20%3D%20429%20K1%20%3D%20-220%3C%2FP%3E%3CP%3E*%20K2%20%3D%20-5785%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%20K2%20%3D%20-5767%3C%2FP%3E%3CP%3E*%20K3%20%3D%20-12800%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%20K3%20%3D%20-12736%3C%2FP%3E%3CP%3E*%20K4%20%3D%2045%20K4%20%3D%2045%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20K1%20*%20Vbg_code%20*%202%5E-1%20%2B%20K2%20*%20TSENS_code%20*%202%5E3%3C%2FP%3E%3CP%3E*%20T%20%3D%20-------------------------------------------------------------------------%20%2F%204%20-%20273.15%20%5B%E6%91%84%E6%B0%8F%E5%BA%A6%5D%3C%2FP%3E%3CP%3E*%20%5BK3%20*%20Vbg_code%20*%202%5E2%20%2B%20K4%20*%20TSENS_code%5D%20*%202%5E-10%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20Vbg0_code%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%20%3D%201502%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%20Vbg1_code%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%26nbsp%3B%20%3D%201502%3C%2FP%3E%3CP%3E*%20TSENS0_%E4%BB%A3%E7%A0%81%20%3D%202002%20TSENS1_%E4%BB%A3%E7%A0%81%20%3D%201988%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20TSENS0%20%E6%B8%A9%E5%BA%A6%20%3D%2034.57%20%E6%91%84%E6%B0%8F%E5%BA%A6%20TSENS1%20%E6%B8%A9%E5%BA%A6%20%3D%2036.78%20%E6%91%84%E6%B0%8F%E5%BA%A6%3C%2FP%3E%3CP%3E*%3C%2FP%3E%3CP%3E*%20------------------------------------------------------------------------------%3C%2FP%3E%3CP%3E*%20%E6%B5%8B%E8%AF%95%E7%A1%AC%E4%BB%B6%EF%BC%9AMPC57xx%3C%2FP%3E%3CP%3E*%20Maskset%3A%26nbsp%3B%201N65H%3C%2FP%3E%3CP%3E*%20%E7%9B%AE%E6%A0%87%EF%BC%9ARAM%E3%80%81%E5%86%85%E9%83%A8%E9%97%AA%E5%AD%98%3C%2FP%3E%3CP%3E*%20Fsys%3A%20200%20MHz%20PLL%EF%BC%8C%E5%B8%A6%2040%20MHz%20%E6%99%B6%E6%8C%AF%E5%8F%82%E8%80%83%3C%2FP%3E%3CP%3E*%20%E7%BB%88%E7%AB%AF%EF%BC%9A19200%E3%80%818N1%E3%80%81%E6%97%A0%3C%2FP%3E%3CP%3E********************************************************************************%3C%2FP%3E%3C%2FLINGO-TEASER%3E%3CLINGO-LABS%20id%3D%22lingo-labs-1122429%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CLINGO-LABEL%3E%E6%A6%82%E8%BF%B0%3C%2FLINGO-LABEL%3E%3C%2FLINGO-LABS%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1122439%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%E5%9B%9E%E5%A4%8D%EF%BC%9AMPC5744P%20TSENS%20%E6%B8%A9%E5%BA%A6%E8%AE%A1%E7%AE%97%E7%A4%BA%E4%BE%8B%20GHS614%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1122439%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%26lt%3Bmeta%20http-equiv%3D%22Content-Type%22%20content%3D%22text%2Fhtml%3B%20charset%3Dutf-8%22%20%2F%26gt%3B%0A%3CP%3EHi%2C%3C%2FP%3E%3CP%3E%3C%2FP%3E%3CP%3E%E4%B9%9F%E8%AE%B8%E4%BD%A0%E9%9C%80%E8%A6%81%E4%BF%AE%E6%94%B9%E4%BB%A3%E7%A0%81%EF%BC%9A%3C%2FP%3E%3CP%20style%3D%22margin%3A%200cm%200cm%200pt%3B%22%3E%3CSPAN%20style%3D%22color%3A%20%23000000%3B%20font-size%3A%20medium%3B%20font-family%3A%20Calibri%3B%22%3E%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3C%2FSPAN%3E%3C%2FP%3E%3CP%20style%3D%22margin%3A%200cm%200cm%200pt%3B%22%3E%3CSPAN%20style%3D%22color%3A%20%23000000%3B%20font-size%3A%20medium%3B%20font-family%3A%20Calibri%3B%22%3E%2F%2F%20TSEN1%E6%B8%A9%E5%BA%A6%E8%AE%A1%E7%AE%97%3C%2FSPAN%3E%3C%2FP%3E%3CP%20style%3D%22margin%3A%200cm%200cm%200pt%3B%22%3E%3CSPAN%20style%3D%22color%3A%20%23000000%3B%20font-size%3A%20medium%3B%20font-family%3A%20Calibri%3B%22%3EADC_1.MCR.B.NSTART%20%3D%201%3B%20%2F*%20%E8%A7%A6%E5%8F%91%20ADC1%20%E7%9A%84%E6%AD%A3%E5%B8%B8%E8%BD%AC%E6%8D%A2%20*%2F%3C%2FSPAN%3E%3C%2FP%3E%3CP%20style%3D%22margin%3A%200cm%200cm%200pt%3B%22%3E%3CSPAN%20style%3D%22color%3A%20%23000000%3B%20font-size%3A%20medium%3B%20font-family%3A%20Calibri%3B%22%3Ewhile(ADC_1.CDR%5B15%5D.B.VALID%20!%3D%201)%20%7B%7D%3B%20%2F*%E7%AD%89%E5%BE%85%E6%9C%80%E5%90%8E%E4%B8%80%E6%AC%A1%E6%89%AB%E6%8F%8F%E5%AE%8C%E6%88%90*%2F%3C%2FSPAN%3E%3C%2FP%3E%3CP%20style%3D%22margin%3A%200cm%200cm%200pt%3B%22%3E%3CSPAN%20style%3D%22color%3A%20%23000000%3B%20font-size%3A%20medium%3B%20font-family%3A%20Calibri%3B%22%3E%26nbsp%3B%26nbsp%3B%26nbsp%3B%20Vbg1_Code%20%3D%20ADC_1.CDR%5B10%5D.B.CDATA%3B%3C%2FSPAN%3E%3C%2FP%3E%3CP%20style%3D%22margin%3A%200cm%200cm%200pt%3B%22%3E%3CSPAN%20style%3D%22color%3A%20%23000000%3B%20font-size%3A%20medium%3B%20font-family%3A%20Calibri%3B%22%3E%26nbsp%3B%26nbsp%3B%26nbsp%3B%20TSENS1_Code%20%3D%20ADC_1.CDR%5B15%5D.B.CDATA%3B%3C%2FSPAN%3E%3C%2FP%3E%3CP%20style%3D%22margin%3A%200cm%200cm%200pt%3B%22%3E%3CSPAN%20style%3D%22color%3A%20%23000000%3B%20font-size%3A%20medium%3B%20font-family%3A%20Calibri%3B%22%3E%26nbsp%3B%3C%2FSPAN%3E%3C%2FP%3E%3CP%20style%3D%22margin%3A%200cm%200cm%200pt%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%20medium%3B%20font-family%3A%20Calibri%3B%22%3E%3CSPAN%20style%3D%22color%3A%20%23000000%3B%22%3E%26nbsp%3B%26nbsp%3B%26nbsp%3B%20temp1%20%3D%20K1_1%20*%20Vbg1_Code%20%2F%202%20%2B%20K2_1%20*%20TSENS%3C%2FSPAN%3E%3CSTRONG%20style%3D%22color%3A%20red%3B%22%3E1%3C%2FSTRONG%3E%3CSPAN%20style%3D%22color%3A%20%23000000%3B%22%3E_Code%20*%208%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%20style%3D%22margin%3A%200cm%200cm%200pt%3B%22%3E%3CSPAN%20style%3D%22font-size%3A%20medium%3B%20font-family%3A%20Calibri%3B%22%3E%3CSPAN%20style%3D%22color%3A%20%23000000%3B%22%3Etemp2%20%3D%20(K3_1%20*%20Vbg1_Code%20*%204%20%2B%20K4_1%20*%20TSENS%3C%2FSPAN%3E%20%3CSTRONG%20style%3D%22color%3A%20red%3B%22%3E1%3C%2FSTRONG%3E%20%3CSPAN%20style%3D%22color%3A%20%23000000%3B%22%3E_Code)%20*%200.0009765625%3B%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%20style%3D%22margin%3A%200cm%200cm%200pt%3B%22%3E%3CSPAN%20style%3D%22color%3A%20%23000000%3B%20font-size%3A%20medium%3B%20font-family%3A%20Calibri%3B%22%3E%26nbsp%3B%3C%2FSPAN%3E%3C%2FP%3E%3CP%20style%3D%22margin%3A%200cm%200cm%200pt%3B%22%3E%3CSPAN%20style%3D%22color%3A%20%23000000%3B%20font-size%3A%20medium%3B%20font-family%3A%20Calibri%3B%22%3E%26nbsp%3B%26nbsp%3B%26nbsp%3B%20TSENS1_T%20%3D%20temp1%20%2F%20temp2%20%2F%204%20-%20273.15%3B%3C%2FSPAN%3E%3C%2FP%3E%3CP%20style%3D%22margin%3A%200cm%200cm%200pt%3B%22%3E%3CSPAN%20style%3D%22color%3A%20%23000000%3B%20font-size%3A%20medium%3B%20font-family%3A%20Calibri%3B%22%3E%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3D%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%3C%2FP%3E%3CP%3E%3C%2FP%3E%3CP%3E%E9%A1%BA%E7%A5%9D%E5%95%86%E7%A5%BA%EF%BC%81%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1122438%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%E5%9B%9E%E5%A4%8D%EF%BC%9AMPC5744P%20TSENS%20%E6%B8%A9%E5%BA%A6%E8%AE%A1%E7%AE%97%E7%A4%BA%E4%BE%8B%20GHS614%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1122438%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%26lt%3Bmeta%20http-equiv%3D%22Content-Type%22%20content%3D%22text%2Fhtml%3B%20charset%3Dutf-8%22%20%2F%26gt%3B%0A%3CP%3EHi%20liu%2C%3C%2FP%3E%3CP%3E%3C%2FP%3E%3CP%3E%E8%AE%BE%E8%AE%A1%E5%9B%A2%E9%98%9F%E5%BB%BA%E8%AE%AE%E4%BD%BF%E7%94%A8%200x50%20%E8%BF%99%E4%B8%AA%E5%80%BC%EF%BC%8C%E5%AE%83%E4%B8%8E%E5%AE%9A%E5%88%B6%E7%A1%AC%E4%BB%B6%2FPCB%20%E5%AF%86%E5%88%87%E7%9B%B8%E5%85%B3%EF%BC%8C%E4%BE%8B%E5%A6%82%E7%94%B5%E5%8E%8B%E5%8F%82%E8%80%83%E4%B8%8A%E7%9A%84%E5%99%AA%E5%A3%B0%E7%AD%89...%E6%89%80%E4%BB%A5%EF%BC%8C%E8%A6%81%E5%B0%8F%E5%BF%83%E3%80%82%3C%2FP%3E%3CP%3E%3C%2FP%3E%3CP%3E%E9%A1%BA%E7%A5%9D%E5%95%86%E7%A5%BA%EF%BC%81%3C%2FP%3E%3CP%3E%E6%8B%8D%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1122437%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%E5%9B%9E%E5%A4%8D%EF%BC%9AMPC5744P%20TSENS%20%E6%B8%A9%E5%BA%A6%E8%AE%A1%E7%AE%97%E7%A4%BA%E4%BE%8B%20GHS614%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1122437%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%26lt%3Bmeta%20http-equiv%3D%22Content-Type%22%20content%3D%22text%2Fhtml%3B%20charset%3Dutf-8%22%20%2F%26gt%3B%0A%3CP%3Ehi%20pat%2C%3C%2FP%3E%3CP%3E%E6%84%9F%E8%B0%A2%E6%82%A8%E7%9A%84%E5%9B%9E%E5%A4%8D%E3%80%82%3C%2FP%3E%3CP%3E%E7%8E%B0%E5%9C%A8%E6%88%91%E6%98%8E%E7%99%BD%E4%BA%86%E4%B8%BA%E4%BB%80%E4%B9%88%E6%88%91%E5%BA%94%E8%AF%A5%E6%94%B9%E5%8F%98%3CSPAN%20style%3D%22font-style%3A%20inherit%3B%20font-family%3A%20inherit%3B%22%3E%20CTR0%5BINPSAMP%5D%20%E5%80%BC%E4%BB%A5%E5%85%81%E8%AE%B8%E5%9C%A8%3C%2FSPAN%3E%3CSPAN%20style%3D%22font-style%3A%20inherit%3B%20font-family%3A%20inherit%3B%22%3E%20%E5%B8%A6%E9%9A%99%E9%87%87%E6%A0%B7%20%E6%97%B6%E6%9C%89%E6%9B%B4%E9%95%BF%E7%9A%84%E6%97%B6%E9%97%B4%20%E3%80%82%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%3CSPAN%20style%3D%22font-style%3A%20inherit%3B%20font-family%3A%20inherit%3B%22%3E%E6%82%A8%E8%83%BD%E7%BB%99%E6%88%91%E4%B8%80%E4%B8%AA%E7%94%A8%E4%BA%8E%E9%87%87%E6%A0%B7%E5%B8%A6%E9%9A%99%E7%9A%84%20CTR0%5BINPSAMP%5D%20%E7%9A%84%E5%BB%BA%E8%AE%AE%E5%80%BC%E5%90%97%EF%BC%9F%E5%9B%A0%E4%B8%BA%E6%88%91%E5%B8%8C%E6%9C%9B%E8%BF%99%E4%B8%AA%E5%80%BC%E4%B8%8D%E6%98%AF%E5%BE%88%E5%A4%A7%E3%80%82CTR0%5BINPSAMP%5D%20%E7%9A%84%E5%A4%A7%E5%80%BC%E5%B0%86%E5%AF%B9%E6%88%91%E7%9A%84%E5%9F%BA%E6%9C%AC%E8%BD%AF%E4%BB%B6%E8%B0%83%E5%BA%A6%E7%A8%8B%E5%BA%8F%E4%BA%A7%E7%94%9F%E6%9B%B4%E5%A4%A7%E7%9A%84%E5%BD%B1%E5%93%8D%E3%80%82%3C%2FSPAN%3E%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1122436%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%E5%9B%9E%E5%A4%8D%EF%BC%9AMPC5744P%20TSENS%20%E6%B8%A9%E5%BA%A6%E8%AE%A1%E7%AE%97%E7%A4%BA%E4%BE%8B%20GHS614%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1122436%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%26lt%3Bmeta%20http-equiv%3D%22Content-Type%22%20content%3D%22text%2Fhtml%3B%20charset%3Dutf-8%22%20%2F%26gt%3B%0A%3CP%3E%E6%82%A8%E5%A5%BD%EF%BC%8C%E5%88%98%EF%BC%8C%3C%2FP%3E%3CP%3E%3C%2FP%3E%3CP%3E%E6%88%91%E6%83%B3%EF%BC%8C%E6%88%91%E9%81%87%E5%88%B0%E4%BA%86%E5%92%8C%E4%BD%A0%E5%90%8C%E6%A0%B7%E7%9A%84%E9%97%AE%E9%A2%98%E3%80%82%E6%94%AF%E6%8C%81%E7%9A%84%E7%AD%94%E6%A1%88%E5%A6%82%E4%B8%8B%EF%BC%9A%E2%80%9C%20%3CEM%3E...%E7%94%B1%E4%BA%8E%E5%86%85%E9%83%A8%E7%94%B5%E5%AE%B9%E8%BE%83%E6%85%A2%EF%BC%8C%E5%9B%A0%E6%AD%A4%E6%9C%89%E5%BF%85%E8%A6%81%E5%A2%9E%E5%8A%A0%E5%B8%A6%E9%9A%99%E7%9A%84%E9%87%87%E6%A0%B7%E6%97%B6%E9%97%B4...%3C%2FEM%3E%20%E2%80%9D%E3%80%82%3C%2FP%3E%3CP%3E%3C%2FP%3E%3CP%3E%E7%94%B1%E4%BA%8E%E5%9C%A8%20RM%E3%80%81ADC_CTR0%20%E5%AD%97%E6%AE%B5%E6%8F%8F%E8%BF%B0%EF%BC%88%E4%BD%8D%2024-31%20INPSAMP%EF%BC%89%E4%B8%AD%E6%B7%BB%E5%8A%A0%E4%BA%86%E6%B3%A8%E9%87%8A%EF%BC%9A%3C%2FP%3E%3CP%3E%3CSTRONG%3E%E6%B3%A8%E6%84%8F%EF%BC%9A%3C%2FSTRONG%3E%E5%B8%A6%E9%9A%99%E7%94%B5%E5%8E%8B%E9%87%87%E6%A0%B7%E6%97%B6%E9%97%B4%E7%94%B1%20CTR0%5BINPSAMP%5D%20%E6%8E%A7%E5%88%B6%E3%80%82CTR0%5BINPSAMP%5D%20%E4%B9%9F%E6%98%AF%3C%2FP%3E%3CP%3E%E7%94%A8%E4%BA%8E%E5%A4%96%E9%83%A8%E9%80%9A%E9%81%93%E9%87%87%E6%A0%B7%E6%97%B6%E9%97%B4%E3%80%82%3CSTRONG%3E%E5%BD%93%E7%94%A8%E6%88%B7%E8%BD%AF%E4%BB%B6%E9%9C%80%E8%A6%81%E9%87%87%E6%A0%B7%3C%2FSTRONG%3E%3C%2FP%3E%3CP%3E%3CSTRONG%3E%E5%B8%A6%E9%9A%99%E7%94%B5%E5%8E%8B%EF%BC%8C%E5%AE%83%E5%BF%85%E9%A1%BB%E6%94%B9%E5%8F%98%20CTR0%5BINPSAMP%5D%20%E5%80%BC%EF%BC%8C%E4%BB%A5%E5%85%81%E8%AE%B8%E6%9B%B4%E9%95%BF%E7%9A%84%E6%97%B6%E9%97%B4%EF%BC%8C%E8%80%8C%3C%2FSTRONG%3E%3C%2FP%3E%3CP%3E%3CSTRONG%3E%E5%B8%A6%E9%9A%99%E6%AD%A3%E5%9C%A8%E8%A2%AB%E9%87%87%E6%A0%B7%3C%2FSTRONG%3E%EF%BC%8C%E7%84%B6%E5%90%8E%E5%B0%86%E5%85%B6%E5%80%BC%E6%94%B9%E5%9B%9E%E6%AD%A3%E5%B8%B8%E5%80%BC%E4%BB%A5%E8%BF%9B%E8%A1%8C%E5%A4%96%E9%83%A8%E9%87%87%E6%A0%B7%3C%2FP%3E%3CP%3E%E9%80%9A%E9%81%93%E3%80%82%3C%2FP%3E%3CP%3E%3C%2FP%3E%3CP%3E%E9%A1%BA%E7%A5%9D%E5%95%86%E7%A5%BA%EF%BC%81%3C%2FP%3E%3CP%3E%E6%8B%8D%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1122435%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%E5%9B%9E%E5%A4%8D%EF%BC%9AMPC5744P%20TSENS%20%E6%B8%A9%E5%BA%A6%E8%AE%A1%E7%AE%97%E7%A4%BA%E4%BE%8B%20GHS614%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1122435%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%26lt%3Bmeta%20http-equiv%3D%22Content-Type%22%20content%3D%22text%2Fhtml%3B%20charset%3Dutf-8%22%20%2F%26gt%3B%0A%3CP%3Ehi%20Petr%2C%3C%2FP%3E%3CP%3E%E6%88%91%E6%AD%A3%E5%9C%A8%E7%AD%89%E5%BE%85%E6%82%A8%E7%9A%84%E5%9B%9E%E5%A4%8D%E3%80%82%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1122434%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%E5%9B%9E%E5%A4%8D%EF%BC%9AMPC5744P%20TSENS%20%E6%B8%A9%E5%BA%A6%E8%AE%A1%E7%AE%97%E7%A4%BA%E4%BE%8B%20GHS614%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1122434%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%26lt%3Bmeta%20http-equiv%3D%22Content-Type%22%20content%3D%22text%2Fhtml%3B%20charset%3Dutf-8%22%20%2F%26gt%3B%0A%3CP%3Ehi%20Petr%2C%3C%2FP%3E%3CP%3E%E6%88%91%E4%BB%AC%E6%9C%89%E4%B8%80%E4%BA%9B%E6%96%B0%E7%9A%84%E5%8F%91%E7%8E%B0%E3%80%82%3C%2FP%3E%3CP%3E%E5%BD%93%E6%88%91%E4%BB%AC%E4%BD%BF%E7%94%A8CTU%E8%A7%A6%E5%8F%91ADC%E9%87%87%E9%9B%86%3CSPAN%20style%3D%22color%3A%20%2351626f%3B%20font-family%3A%20arial%2C%20helvetica%2C%20'helvetica%20neue'%2C%20verdana%2C%20sans-serif%3B%22%3EVbg0_code%E6%88%96%3CSPAN%20style%3D%22color%3A%20%2351626f%3B%20font-family%3A%20arial%2C%20helvetica%2C%20'helvetica%20neue'%2C%20verdana%2C%20sans-serif%3B%22%3EVbg1_code%E6%97%B6%EF%BC%8CADC%E5%80%BC%E5%B9%B6%E4%B8%8D%E7%A8%B3%E5%AE%9A%E3%80%82%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%3CSPAN%20style%3D%22color%3A%20%2351626f%3B%20font-family%3A%20arial%2C%20helvetica%2C%20'helvetica%20neue'%2C%20verdana%2C%20sans-serif%3B%22%3E%E4%BD%86%E6%98%AF%E5%BD%93%E6%88%91%E4%BB%AC%E4%BD%BF%E7%94%A8%E5%AF%84%E5%AD%98%E5%99%A8%E8%A7%A6%E5%8F%91ADC%E8%8E%B7%E5%8F%96%3CSPAN%20style%3D%22color%3A%20%2351626f%3B%20font-family%3A%20arial%2C%20helvetica%2C%20'helvetica%20neue'%2C%20verdana%2C%20sans-serif%3B%22%3EVbg0_code%E6%88%96%3CSPAN%20style%3D%22color%3A%20%2351626f%3B%20font-family%3A%20arial%2C%20helvetica%2C%20'helvetica%20neue'%2C%20verdana%2C%20sans-serif%3B%22%3EVbg1_code%E6%97%B6%EF%BC%8CADC%E5%80%BC%E4%BC%BC%E4%B9%8E%E7%A8%B3%E5%AE%9A%E4%BA%86%E3%80%82%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%3CSPAN%20style%3D%22color%3A%20%2351626f%3B%20font-family%3A%20arial%2C%20helvetica%2C%20'helvetica%20neue'%2C%20verdana%2C%20sans-serif%3B%22%3E%E4%B8%BA%E4%BB%80%E4%B9%88%EF%BC%9F%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%3CSPAN%20style%3D%22color%3A%20%2351626f%3B%20font-family%3A%20arial%2C%20helvetica%2C%20'helvetica%20neue'%2C%20verdana%2C%20sans-serif%3B%22%3E%E6%88%91%E4%BB%AC%E7%9A%84CTU%E8%A7%A6%E5%8F%91ADC%E5%91%A8%E6%9C%9F%E6%98%AF100us%EF%BC%8C%E6%98%AF%E4%B8%8D%E6%98%AF%E5%A4%AA%E5%BF%AB%E4%BA%86%EF%BC%9F%3C%2FSPAN%3E%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1122433%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%E5%9B%9E%E5%A4%8D%EF%BC%9AMPC5744P%20TSENS%20%E6%B8%A9%E5%BA%A6%E8%AE%A1%E7%AE%97%E7%A4%BA%E4%BE%8B%20GHS614%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1122433%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%26lt%3Bmeta%20http-equiv%3D%22Content-Type%22%20content%3D%22text%2Fhtml%3B%20charset%3Dutf-8%22%20%2F%26gt%3B%0A%3CP%3EHi%20Petr%2C%3C%2FP%3E%3CP%3E%E6%84%9F%E8%B0%A2%E6%82%A8%E7%9A%84%E5%9B%9E%E5%A4%8D%E3%80%82%3C%2FP%3E%3CP%3E%E6%88%91%E4%BB%AC%E5%8F%91%E7%8E%B0ADC%E9%87%87%E9%9B%86%E5%88%B0%E7%9A%84Vbg0_code%E5%92%8CVbg1_code%E4%B9%9F%E4%B8%8D%E5%A4%AA%E7%A8%B3%E5%AE%9A%E3%80%82%E4%BD%A0%E8%83%BD%E5%B8%AE%E6%88%91%E6%A3%80%E6%9F%A5%E4%B8%80%E4%B8%8B%E4%BD%A0%E7%9A%84%20Vbg0_code%20%E5%92%8C%20Vbg1_code%20%E5%90%97%EF%BC%9F%3C%2FP%3E%3CP%3E%3C%2FP%3E%3CP%3E%E6%88%91%E4%BB%AC%E4%BD%BF%E7%94%A8%E7%9A%84DEMO%E7%A8%8B%E5%BA%8F%E6%98%AF%E6%82%A8%E7%9A%84%E9%99%84%E4%BB%B6%EF%BC%8C%E6%97%A0%E9%9C%80%E6%9B%B4%E6%94%B9%E3%80%82%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1122432%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%E5%9B%9E%E5%A4%8D%EF%BC%9AMPC5744P%20TSENS%20%E6%B8%A9%E5%BA%A6%E8%AE%A1%E7%AE%97%E7%A4%BA%E4%BE%8B%20GHS614%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1122432%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%26lt%3Bmeta%20http-equiv%3D%22Content-Type%22%20content%3D%22text%2Fhtml%3B%20charset%3Dutf-8%22%20%2F%26gt%3B%0A%3CP%3E%E6%88%91%E5%9C%A8%20MPC5744P%20EVB%20%E4%B8%8A%E6%A3%80%E6%9F%A5%E4%BA%86%E5%AE%83%E5%B9%B6%E5%BE%97%E5%88%B0%E4%BA%86%E8%BF%99%E4%B8%AA%E7%BB%93%E6%9E%9C%3C%2FP%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22pastedImage_0.png%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22pastedImage_0.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F60650i9CB423AA1AAB0924%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22pastedImage_0.png%22%20alt%3D%22pastedImage_0.png%22%20%2F%3E%3Cspan%20class%3D%22lia-inline-image-caption%22%20onclick%3D%22event.preventDefault()%3B%22%3EpastedImage_0.png%3C%2Fspan%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%E5%BE%88%E9%9A%BE%E8%AF%B4%E3%80%82%3C%2FP%3E%3CP%3E%E6%82%A8%E4%BD%BF%E7%94%A8%E7%9A%84%E5%AE%8C%E6%95%B4%E9%9B%B6%E4%BB%B6%E7%BC%96%E5%8F%B7%E6%98%AF%E5%A4%9A%E5%B0%91%EF%BC%9F%3C%2FP%3E%3CP%3E%3C%2FP%3E%3CP%3EBR%2C%20Petr%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1122431%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%E5%9B%9E%E5%A4%8D%EF%BC%9AMPC5744P%20TSENS%20%E6%B8%A9%E5%BA%A6%E8%AE%A1%E7%AE%97%E7%A4%BA%E4%BE%8B%20GHS614%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1122431%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%26lt%3Bmeta%20http-equiv%3D%22Content-Type%22%20content%3D%22text%2Fhtml%3B%20charset%3Dutf-8%22%20%2F%26gt%3B%0A%3CP%3E%E6%9C%89%E8%B0%81%E8%83%BD%E5%B8%AE%E5%B8%AE%E6%88%91%E5%90%97%EF%BC%9F%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-1122430%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%E5%9B%9E%E5%A4%8D%EF%BC%9AMPC5744P%20TSENS%20%E6%B8%A9%E5%BA%A6%E8%AE%A1%E7%AE%97%E7%A4%BA%E4%BE%8B%20GHS614%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-1122430%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%26lt%3Bmeta%20http-equiv%3D%22Content-Type%22%20content%3D%22text%2Fhtml%3B%20charset%3Dutf-8%22%20%2F%26gt%3B%0A%3CP%3EHi%20petr%2C%3C%2FP%3E%3CP%3E%E6%88%91%E4%BB%AC%E4%B8%8B%E8%BD%BD%E6%82%A8%E7%9A%84%E6%BC%94%E7%A4%BA%E7%A8%8B%E5%BA%8F%E5%B9%B6%E5%9C%A8%E6%88%91%E4%BB%AC%E7%9A%84%E6%BC%94%E7%A4%BA%E6%9D%BF%E4%B8%AD%E8%BF%90%E8%A1%8C%E5%AE%83%E3%80%82%E8%AF%A5%E7%A8%8B%E5%BA%8F%E4%BC%BC%E4%B9%8E%E5%AD%98%E5%9C%A8%E4%B8%80%E4%BA%9B%E4%BB%A4%E6%88%91%E5%9B%B0%E6%83%91%E7%9A%84%E9%97%AE%E9%A2%98%E3%80%82%3C%2FP%3E%3CP%3E%E5%BD%93%E6%88%91%E4%BB%AC%E5%B0%86%E7%A4%BA%E4%BE%8B%E7%A8%8B%E5%BA%8F%E7%9A%84HEX%E4%B8%8B%E8%BD%BD%E5%88%B05744pq9%E8%8A%AF%E7%89%87%E4%B8%AD%E5%B9%B6%E8%BF%90%E8%A1%8C%E5%90%8E%EF%BC%8C%E6%88%91%E4%BB%AC%E5%8F%AF%E4%BB%A5%E7%9C%8B%E5%88%B0MCU%E6%B8%A9%E5%BA%A6%E8%AE%A1%E7%AE%97%E7%9A%84%E7%BB%93%E6%9E%9C%E5%B9%B6%E4%B8%8D%E7%A8%B3%E5%AE%9A%E3%80%82%3C%2FP%3E%3CP%3E%E4%B8%8B%E9%9D%A2%E6%98%AF%20Lauterbach%20%E8%B0%83%E8%AF%95%E5%99%A8%E7%9A%84%E5%B1%8F%E5%B9%95%E6%88%AA%E5%9B%BE%E3%80%82%3C%2FP%3E%3CP%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22aaa.png%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22aaa.png%22%20style%3D%22width%3A%20780px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F60614iC8C62000AFA3AE53%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22aaa.png%22%20alt%3D%22aaa.png%22%20%2F%3E%3Cspan%20class%3D%22lia-inline-image-caption%22%20onclick%3D%22event.preventDefault()%3B%22%3Eaaa.png%3C%2Fspan%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FP%3E%3CP%3E%E6%88%91%E4%BB%AC%E5%8F%AF%E4%BB%A5%E7%9C%8B%E5%88%B0MCU%E6%B8%A9%E5%BA%A6%E5%9C%A8-10%E5%BA%A6%E5%92%8C50%E5%BA%A6%E4%B9%8B%E9%97%B4%E6%8C%AF%E8%8D%A1%E3%80%82%E8%BF%99%E6%98%BE%E7%84%B6%E6%98%AF%E4%B8%8D%E6%AD%A3%E7%A1%AE%E3%80%82%3C%2FP%3E%3CP%3E%E9%82%A3%E4%B9%88%EF%BC%8C%E4%BD%A0%E8%83%BD%E5%B8%AE%E6%88%91%E6%89%BE%E5%87%BA%E8%BF%99%E7%A7%8D%E7%8E%B0%E8%B1%A1%E7%9A%84%E5%8E%9F%E5%9B%A0%E5%90%97%EF%BC%9F%3C%2FP%3E%3CP%3E%E9%9D%9E%E5%B8%B8%E6%84%9F%E8%B0%A2%E3%80%82%3C%2FP%3E%3C%2FLINGO-BODY%3E
无评分
版本历史
最后更新:
‎04-17-2015 03:06 AM
更新人: