Conection of PLC and LPC804 via Modbus RTU

キャンセル
次の結果を表示 
表示  限定  | 次の代わりに検索 
もしかして: 

Conection of PLC and LPC804 via Modbus RTU

ソリューションへジャンプ
1,171件の閲覧回数
Mayk_Blanco
Contributor I

Hello everyone!

I'm new to the world of microcontrollers. I'm trying to design a master-slave system with LPC804 (master) and Eaton PLC (slave). The system has to be connected via Modbus RTU, but I have no idea how to make the hardware connection between the microcontroller and the PLC. Do I need some kind of external component? Any suggestions are welcome.

Thanks for your time.

0 件の賞賛
返信
1 解決策
1,148件の閲覧回数
Pavel_Hernandez
NXP TechSupport
NXP TechSupport

Hello, my name is Pavel, and I will be supporting your case, the protocol Modbus can be mounted on UART, for long distances you will need a transceiver, that makes the communication of tx and rx to the differential. The way to know what transceiver you need is by reviewing how the PLC supports this protocol.

Best regards,
Pavel

元の投稿で解決策を見る

1 返信
1,149件の閲覧回数
Pavel_Hernandez
NXP TechSupport
NXP TechSupport

Hello, my name is Pavel, and I will be supporting your case, the protocol Modbus can be mounted on UART, for long distances you will need a transceiver, that makes the communication of tx and rx to the differential. The way to know what transceiver you need is by reviewing how the PLC supports this protocol.