Hi,
I have a MPX5100DP sensor, and I can´t undestand him sensibility and acuracy. In the manual, the especification is ±2.5 %VFSS . With the VFSS = 4,5, the acuracy would be close to 0,11V or 110mV, right? This value applied to the sensibility, that is 45mV/kPA, I would have +/- 2.44KPA. This is what I can conclude with informations of the manual, but doing some tests, tying to measure a level of water, I discover that the true sensibility is much more less. I did increases in 1 cmca (0,098kpa), and the sensor detect this variation, and the acuracy that I observed was +/- 1,5cmca (0,147kPA). I would like to undestand, why this values are so different, because I'm interested to use other sensors like mpx10dp, but I have to understand this issues.