S32K344 FlexCAN Change Highest-priority message buffer first to Lowest-number message buffer first
1,643件の閲覧回数
bruceyun
Hi all,
I am working on a project to route CAN messages. I found out that CAN write block by default has arbitration process, which choose highest-priority CAN message buffer to send first. I want to change it to lowest-number message buffer to send first.
After I read document, there are some lines:
73.3.3.1
"If CTRL1[LBUF] is 1, the first (lowest number) active transmission message buffer found is the arbitration winner. MCR[LPRIOEN] has no effect when CTRL1[LBUF] is 1."
So I am trying to write CTRL1[LBUF] to 1. I believe that I need to change to Freeze Mode.
"MCR[FRZ] must be 1 and the module must not be in a low-power mode"
"After requesting Freeze mode, you must wait for MCR[FRZACK] to become 1 before executing any other action, otherwise FlexCAN may operate unpredictably. In Freeze mode, all memory-mapped registers are accessible."
I tried to write MCR[FRZ] to 1 but I failed to change to Freeze mode. Can anyone here have the knowledge about this? I appreciate it.
##S32K34 #FlexCAN #CAN #Route #AUTOSAR #NXP
1,625件の閲覧回数
SorinIBancila
To put the FLEXCAN module into FreezeMode, we can use the S32K3 RTD functions:
  • FlexCAN_Ip_EnterFreezeMode_Privileged(uint8 instance)
  • FlexCAN_Ip_ExitFreezeMode_Privileged(uint8 instance)
To test this I've added the following blocks to an already existing model that sends messages over CAN. Basically, I have a variable CAN_0_enterfreeze which I modify from the FreeMASTER to have one of the following values:
  • 0: Do nothing
  • 1: read MCR register for CAN 0 instance and store the result in CAN_0_MCR
  • 2: Enter FreezeMode
  • 3: Exit FreezeMode
Inside case 2 and case 3, you have to add a MATLAB function block. The custom code to enter/exit freezemode can be found below:
To validate this I've done the following:
  • Reset the development board and read the content of MCR register for CAN 0 instance.
  • Set CAN_0_enterfreeze to 2 and read the content of the MCR register. Note! The FlexCAN is not working in FreezeMode.SorinIBancila_3-1754053812864.png
  •  Set CAN_0_enterfreeze to 3 and read the content of the MCR register. The CAN is working again. I just send a message (ID = 101) from CAN analyzer tool and the board replies with a message ID=0.
The S32K3 RTD sources can be found inside the toolbox, where you can check the implementation for a specific module in case you need it. To open the root of the S32K3 folder, you can type the following command in MATLAB command window : cd(mbd_find_s32k3_root).
Do not hesitate to reply in case you have any other questions.
Sorin Bancila
%3CLINGO-SUB%20id%3D%22lingo-sub-2144812%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3ES32K344%20FlexCAN%20%E6%9C%80%E9%AB%98%E5%84%AA%E5%85%88%E5%BA%A6%E3%81%AE%E3%83%A1%E3%83%83%E3%82%BB%E3%83%BC%E3%82%B8%E3%83%90%E3%83%83%E3%83%95%E3%82%A1%E3%82%92%E6%9C%80%E4%BD%8E%E7%95%AA%E5%8F%B7%E3%81%AE%E3%83%A1%E3%83%83%E3%82%BB%E3%83%BC%E3%82%B8%E3%83%90%E3%83%83%E3%83%95%E3%82%A1%E3%81%AB%E5%A4%89%E6%9B%B4%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-2144812%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%E3%81%93%E3%82%93%E3%81%AB%E3%81%A1%E3%81%AF%E3%80%81%E3%81%BF%E3%82%93%E3%81%AA%E3%80%81%3C%2FP%3E%3CP%3E%E7%A7%81%E3%81%AF%20CAN%20%E3%83%A1%E3%83%83%E3%82%BB%E3%83%BC%E3%82%B8%E3%82%92%E3%83%AB%E3%83%BC%E3%83%86%E3%82%A3%E3%83%B3%E3%82%B0%E3%81%99%E3%82%8B%E3%83%97%E3%83%AD%E3%82%B8%E3%82%A7%E3%82%AF%E3%83%88%E3%81%AB%E5%8F%96%E3%82%8A%E7%B5%84%E3%82%93%E3%81%A7%E3%81%84%E3%81%BE%E3%81%99%E3%80%82CAN%20%E6%9B%B8%E3%81%8D%E8%BE%BC%E3%81%BF%E3%83%96%E3%83%AD%E3%83%83%E3%82%AF%E3%81%AB%E3%81%AF%E3%83%87%E3%83%95%E3%82%A9%E3%83%AB%E3%83%88%E3%81%A7%E8%AA%BF%E5%81%9C%E3%83%97%E3%83%AD%E3%82%BB%E3%82%B9%E3%81%8C%E3%81%82%E3%82%8A%E3%80%81%E6%9C%80%E3%82%82%E5%84%AA%E5%85%88%E5%BA%A6%E3%81%AE%E9%AB%98%E3%81%84%20CAN%20%E3%83%A1%E3%83%83%E3%82%BB%E3%83%BC%E3%82%B8%20%E3%83%90%E3%83%83%E3%83%95%E3%82%A1%E3%82%92%E6%9C%80%E5%88%9D%E3%81%AB%E9%80%81%E4%BF%A1%E3%81%99%E3%82%8B%E3%82%88%E3%81%86%E3%81%AB%E9%81%B8%E6%8A%9E%E3%81%99%E3%82%8B%E3%81%93%E3%81%A8%E3%81%8C%E3%82%8F%E3%81%8B%E3%82%8A%E3%81%BE%E3%81%97%E3%81%9F%E3%80%82%E6%9C%80%E5%88%9D%E3%81%AB%E9%80%81%E4%BF%A1%E3%81%99%E3%82%8B%E3%83%A1%E3%83%83%E3%82%BB%E3%83%BC%E3%82%B8%20%E3%83%90%E3%83%83%E3%83%95%E3%82%A1%E3%83%BC%E7%95%AA%E5%8F%B7%E3%81%8C%E6%9C%80%E3%82%82%E5%B0%8F%E3%81%95%E3%81%84%E3%82%82%E3%81%AE%E3%81%AB%E5%A4%89%E6%9B%B4%E3%81%97%E3%81%BE%E3%81%99%E3%80%82%3C%2FP%3E%3CP%3E%E6%96%87%E6%9B%B8%E3%82%92%E8%AA%AD%E3%82%93%E3%81%A7%E3%81%BF%E3%82%8B%E3%81%A8%E3%80%81%E6%AC%A1%E3%81%AE%E3%82%88%E3%81%86%E3%81%AA%E8%A1%8C%E3%81%8C%E3%81%82%E3%82%8A%E3%81%BE%E3%81%99%3A%3C%2FP%3E%3CP%3E73.3.3.1%3CBR%20%2F%3E%E6%9C%80%E3%82%82%E5%B0%8F%E3%81%95%E3%81%84%E7%95%AA%E5%8F%B7%E3%81%AE%E3%83%A1%E3%83%83%E3%82%BB%E3%83%BC%E3%82%B8%E3%83%90%E3%83%83%E3%83%95%E3%82%A1%E3%82%92%E5%85%88%E9%A0%AD%E3%81%AB%E3%81%99%E3%82%8B%3CBR%20%2F%3ECTRL1%5BLBUF%5D%E3%81%8C1%E3%81%AE%E5%A0%B4%E5%90%88%E3%80%81%E6%9C%80%E5%88%9D%E3%81%AB%E8%A6%8B%E3%81%A4%E3%81%8B%E3%81%A3%E3%81%9F%EF%BC%88%E6%9C%80%E3%82%82%E5%B0%8F%E3%81%95%E3%81%84%E7%95%AA%E5%8F%B7%E3%81%AE%EF%BC%89%E3%82%A2%E3%82%AF%E3%83%86%E3%82%A3%E3%83%96%E3%81%AA%E9%80%81%E4%BF%A1%E3%83%A1%E3%83%83%E3%82%BB%E3%83%BC%E3%82%B8%20%E3%83%90%E3%83%83%E3%83%95%E3%82%A1%E3%81%8C%E8%AA%BF%E5%81%9C%E3%81%AE%E5%8B%9D%E8%80%85%E3%81%AB%E3%81%AA%E3%82%8A%E3%81%BE%E3%81%99%E3%80%82CTRL1%5BLBUF%5D%E3%81%8C1%E3%81%AE%E5%A0%B4%E5%90%88%E3%80%81MCR%5BLPRIOEN%5D%E3%81%AF%E5%8A%B9%E6%9E%9C%E3%81%8C%E3%81%82%E3%82%8A%E3%81%BE%E3%81%9B%E3%82%93%E3%80%82%3C%2FP%3E%3CP%3ESO%E3%80%81CTRL1%5BLBUF%5D%E3%81%AB1%E3%82%92%E6%9B%B8%E3%81%8D%E8%BE%BC%E3%82%82%E3%81%86%E3%81%A8%E3%81%97%E3%81%A6%E3%81%84%E3%81%BE%E3%81%99%E3%80%82%E3%83%95%E3%83%AA%E3%83%BC%E3%82%BA%E3%83%A2%E3%83%BC%E3%83%89%E3%81%AB%E5%A4%89%E6%9B%B4%E3%81%99%E3%82%8B%E5%BF%85%E8%A6%81%E3%81%8C%E3%81%82%E3%82%8B%E3%81%A8%E6%80%9D%E3%81%84%E3%81%BE%E3%81%99%E3%80%82%3C%2FP%3E%3CP%3E%E3%80%8CMCR%5BFRZ%5D%E3%81%AF1%E3%81%A7%E3%81%AA%E3%81%91%E3%82%8C%E3%81%B0%E3%81%AA%E3%82%89%E3%81%9A%E3%80%81%E3%83%A2%E3%82%B8%E3%83%A5%E3%83%BC%E3%83%AB%E3%81%AF%E4%BD%8E%E9%9B%BB%E5%8A%9B%E3%83%A2%E3%83%BC%E3%83%89%E3%81%A7%E3%81%82%E3%81%A3%E3%81%A6%E3%81%AF%E3%81%AA%E3%82%8A%E3%81%BE%E3%81%9B%E3%82%93%E3%80%8D%3C%2FP%3E%3CP%3E%E3%83%95%E3%83%AA%E3%83%BC%E3%82%BA%20%E3%83%A2%E3%83%BC%E3%83%89%E3%82%92%E8%A6%81%E6%B1%82%E3%81%97%E3%81%9F%E5%BE%8C%E3%80%81%E4%BB%96%E3%81%AE%E3%82%A2%E3%82%AF%E3%82%B7%E3%83%A7%E3%83%B3%E3%82%92%E5%AE%9F%E8%A1%8C%E3%81%99%E3%82%8B%E5%89%8D%E3%81%AB%20MCR%5BFRZACK%5D%20%E3%81%8C%201%20%E3%81%AB%E3%81%AA%E3%82%8B%E3%81%BE%E3%81%A7%E5%BE%85%E3%81%A4%E5%BF%85%E8%A6%81%E3%81%8C%E3%81%82%E3%82%8A%E3%81%BE%E3%81%99%E3%80%82%E3%81%9D%E3%81%86%E3%81%97%E3%81%AA%E3%81%84%E3%81%A8%E3%80%81FlexCAN%20%E3%81%8C%E4%BA%88%E6%9C%9F%E3%81%97%E3%81%AA%E3%81%84%E5%8B%95%E4%BD%9C%E3%82%92%E3%81%99%E3%82%8B%E5%8F%AF%E8%83%BD%E6%80%A7%E3%81%8C%E3%81%82%E3%82%8A%E3%81%BE%E3%81%99%E3%80%82%E3%83%95%E3%83%AA%E3%83%BC%E3%82%BA%E3%83%A2%E3%83%BC%E3%83%89%E3%81%A7%E3%81%AF%E3%80%81%E3%81%99%E3%81%B9%E3%81%A6%E3%81%AE%E3%83%A1%E3%83%A2%E3%83%AA%E3%83%9E%E3%83%83%E3%83%97%E3%83%AC%E3%82%B8%E3%82%B9%E3%82%BF%E3%81%AB%E3%82%A2%E3%82%AF%E3%82%BB%E3%82%B9%E3%81%A7%E3%81%8D%E3%81%BE%E3%81%99%E3%80%82%3C%2FP%3E%3CBR%20%2F%3E%3CP%3EMCR%5BFRZ%5D%E3%82%921%E3%81%AB%E6%9B%B8%E3%81%8D%E8%BE%BC%E3%82%82%E3%81%86%E3%81%A8%E3%81%97%E3%81%BE%E3%81%97%E3%81%9F%E3%81%8C%E3%80%81%E3%83%95%E3%83%AA%E3%83%BC%E3%82%BA%E3%83%A2%E3%83%BC%E3%83%89%E3%81%AB%E5%A4%89%E6%9B%B4%E3%81%A7%E3%81%8D%E3%81%BE%E3%81%9B%E3%82%93%E3%81%A7%E3%81%97%E3%81%9F%E3%80%82%E3%81%93%E3%81%AE%E3%81%93%E3%81%A8%E3%81%AB%E3%81%A4%E3%81%84%E3%81%A6%E7%9F%A5%E3%81%A3%E3%81%A6%E3%81%84%E3%82%8B%E4%BA%BA%E3%81%AF%E3%81%93%E3%81%93%E3%81%ABCAN%E3%81%8B%3F%E3%81%9D%E3%82%8C%E3%81%AF%E6%9C%89%E3%82%8A%E9%9B%A3%E3%81%84%E3%81%A7%E3%81%99%E3%80%82%3C%2FP%3E%3CBR%20%2F%3E%3CP%3E%23%23S32K34%20%23FlexCAN%20%23CAN%20%23%E3%83%AB%E3%83%BC%E3%83%88%20%23AUTOSAR%20%23NXP%3C%2FP%3E%3C%2FLINGO-BODY%3E%3CLINGO-SUB%20id%3D%22lingo-sub-2145208%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%20translate%3D%22no%22%3ERe%3A%20S32K344%20FlexCAN%20Change%20Highest-priority%20message%20buffer%20first%20to%20Lowest-number%20message%20buffer%20fir%3C%2FLINGO-SUB%3E%3CLINGO-BODY%20id%3D%22lingo-body-2145208%22%20slang%3D%22en-US%22%20mode%3D%22CREATE%22%3E%3CP%3E%E3%81%93%E3%82%93%E3%81%AB%E3%81%A1%E3%81%AF%E3%80%81%3C%2FP%3E%0A%3CBR%20%2F%3E%0A%3CP%3EFLEXCAN%20%E3%83%A2%E3%82%B8%E3%83%A5%E3%83%BC%E3%83%AB%E3%82%92%20FreezeMode%20%E3%81%AB%E3%81%99%E3%82%8B%E3%81%AB%E3%81%AF%E3%80%81S32K3%20RTD%20%E9%96%A2%E6%95%B0%E3%82%92%E4%BD%BF%E7%94%A8%E3%81%97%E3%81%BE%E3%81%99%E3%80%82%3C%2FP%3E%0A%3CDIV%20class%3D%22rtcContent%22%3E%0A%3CUL%3E%0A%3CLI%20class%3D%22lineNode%22%3E%3CSPAN%3EFlexCAN_Ip_EnterFreezeMode_Privileged(uint8%20%E3%82%A4%E3%83%B3%E3%82%B9%E3%82%BF%E3%83%B3%E3%82%B9)%3C%2FSPAN%3E%3C%2FLI%3E%0A%3C%2FUL%3E%0A%3CDIV%20class%3D%22rtcContent%22%3E%0A%3CUL%3E%0A%3CLI%20class%3D%22lineNode%22%3E%3CSPAN%3EFlexCAN_Ip_ExitFreezeMode_Privileged(uint8%20%E3%82%A4%E3%83%B3%E3%82%B9%E3%82%BF%E3%83%B3%E3%82%B9)%3C%2FSPAN%3E%3C%2FLI%3E%0A%3C%2FUL%3E%0A%3CDIV%20class%3D%22lineNode%22%3E%26nbsp%3B%3C%2FDIV%3E%0A%3CDIV%20class%3D%22lineNode%22%3E%E3%81%93%E3%82%8C%E3%82%92%E3%83%86%E3%82%B9%E3%83%88%E3%81%99%E3%82%8B%E3%81%9F%E3%82%81%E3%81%AB%E3%80%81CAN%20%E7%B5%8C%E7%94%B1%E3%81%A7%E3%83%A1%E3%83%83%E3%82%BB%E3%83%BC%E3%82%B8%E3%82%92%E9%80%81%E4%BF%A1%E3%81%99%E3%82%8B%E6%97%A2%E5%AD%98%E3%81%AE%E3%83%A2%E3%83%87%E3%83%AB%E3%81%AB%E6%AC%A1%E3%81%AE%E3%83%96%E3%83%AD%E3%83%83%E3%82%AF%E3%82%92%E8%BF%BD%E5%8A%A0%E3%81%97%E3%81%BE%E3%81%97%E3%81%9F%E3%80%82%E5%9F%BA%E6%9C%AC%E7%9A%84%E3%81%AB%E3%80%81%E5%A4%89%E6%95%B0%3CSTRONG%3ECAN_0_enterfreeze%3C%2FSTRONG%3E%E3%81%8C%E3%81%82%E3%82%8A%E3%80%81%E3%81%93%E3%82%8C%E3%82%92%20FreeMASTER%20%E3%81%8B%E3%82%89%E5%A4%89%E6%9B%B4%E3%81%97%E3%81%A6%E6%AC%A1%E3%81%AE%E3%81%84%E3%81%9A%E3%82%8C%E3%81%8B%E3%81%AE%E5%80%A4%E3%82%92%E8%A8%AD%E5%AE%9A%E3%81%97%E3%81%BE%E3%81%99%E3%80%82%3C%2FDIV%3E%0A%3CUL%3E%0A%3CLI%20class%3D%22lineNode%22%3E0%3A%20%E4%BD%95%E3%82%82%E3%81%97%E3%81%AA%E3%81%84%3C%2FLI%3E%0A%3CLI%20class%3D%22lineNode%22%3E1%3A%20CAN%200%E3%82%A4%E3%83%B3%E3%82%B9%E3%82%BF%E3%83%B3%E3%82%B9%E3%81%AEMCR%E3%83%AC%E3%82%B8%E3%82%B9%E3%82%BF%E3%82%92%E8%AA%AD%E3%81%BF%E5%8F%96%E3%82%8A%E3%80%81%E7%B5%90%E6%9E%9C%E3%82%92%3CSTRONG%3ECAN_0_MCR%3C%2FSTRONG%3E%E3%81%AB%E6%A0%BC%E7%B4%8D%E3%81%97%E3%81%BE%E3%81%99%E3%80%82%3C%2FLI%3E%0A%3CLI%20class%3D%22lineNode%22%3E2%3A%20%E3%83%95%E3%83%AA%E3%83%BC%E3%82%BA%E3%83%A2%E3%83%BC%E3%83%89%E3%81%AB%E5%85%A5%E3%82%8B%3C%2FLI%3E%0A%3CLI%20class%3D%22lineNode%22%3E3%3A%20%E3%83%95%E3%83%AA%E3%83%BC%E3%82%BA%E3%83%A2%E3%83%BC%E3%83%89%E3%82%92%E7%B5%82%E4%BA%86%E3%81%99%E3%82%8B%3C%2FLI%3E%0A%3C%2FUL%3E%0A%3CDIV%20class%3D%22lineNode%22%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-center%22%20image-alt%3D%22SorinIBancila_0-1754053072043.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22SorinIBancila_0-1754053072043.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F350631iB5E751A958AE2A07%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22SorinIBancila_0-1754053072043.png%22%20alt%3D%22SorinIBancila_0-1754053072043.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%0A%3CBR%20%2F%3E%0A%3CP%3ECASE%202%20%E3%81%A8%20CASE%203%20%E5%86%85%E3%81%A7%E3%80%81MATLAB%20%E9%96%A2%E6%95%B0%E3%83%96%E3%83%AD%E3%83%83%E3%82%AF%E3%82%92%E8%BF%BD%E5%8A%A0%E3%81%99%E3%82%8B%E5%BF%85%E8%A6%81%E3%81%8C%E3%81%82%E3%82%8A%E3%81%BE%E3%81%99%E3%80%82%E3%83%95%E3%83%AA%E3%83%BC%E3%82%BA%E3%83%A2%E3%83%BC%E3%83%89%E3%82%92%E9%96%8B%E5%A7%8B%2F%E7%B5%82%E4%BA%86%E3%81%99%E3%82%8B%E3%81%9F%E3%82%81%E3%81%AE%E3%82%AB%E3%82%B9%E3%82%BF%E3%83%A0%20%E3%82%B3%E3%83%BC%E3%83%89%E3%81%AF%E6%AC%A1%E3%81%AE%E3%81%A8%E3%81%8A%E3%82%8A%E3%81%A7%E3%81%99%E3%80%82%3C%2FP%3E%0A%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22SorinIBancila_1-1754053486901.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22SorinIBancila_1-1754053486901.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F350632iA67E3C78D6ED6D43%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22SorinIBancila_1-1754053486901.png%22%20alt%3D%22SorinIBancila_1-1754053486901.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%0A%3CBR%20%2F%3E%0A%3CP%3E%E3%81%93%E3%82%8C%E3%82%92%E6%A4%9C%E8%A8%BC%E3%81%99%E3%82%8B%E3%81%9F%E3%82%81%E3%81%AB%E3%80%81%E6%AC%A1%E3%81%AE%E6%93%8D%E4%BD%9C%E3%82%92%E5%AE%9F%E8%A1%8C%E3%81%97%E3%81%BE%E3%81%97%E3%81%9F%E3%80%82%3C%2FP%3E%0A%3CUL%3E%0A%3CLI%3E%E9%96%8B%E7%99%BA%E3%83%9C%E3%83%BC%E3%83%89%E3%82%92%E3%83%AA%E3%82%BB%E3%83%83%E3%83%88%E3%81%97%E3%80%81CAN%200%20%E3%82%A4%E3%83%B3%E3%82%B9%E3%82%BF%E3%83%B3%E3%82%B9%E3%81%AE%20MCR%20%E3%83%AC%E3%82%B8%E3%82%B9%E3%82%BF%E3%81%AE%E5%86%85%E5%AE%B9%E3%82%92%E8%AA%AD%E3%81%BF%E5%8F%96%E3%82%8A%E3%81%BE%E3%81%99%E3%80%82%3C%2FLI%3E%0A%3C%2FUL%3E%0A%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-center%22%20image-alt%3D%22SorinIBancila_2-1754053730649.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22SorinIBancila_2-1754053730649.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F350633iDBFBB2BF9415F59D%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22SorinIBancila_2-1754053730649.png%22%20alt%3D%22SorinIBancila_2-1754053730649.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%0A%3CBR%20%2F%3E%0A%3CUL%3E%0A%3CLI%3ECAN_0_enterfreeze%20%E3%82%92%3CSTRONG%3E2%3C%2FSTRONG%3E%E3%81%AB%E8%A8%AD%E5%AE%9A%E3%81%97%E3%80%81MCR%20%E3%83%AC%E3%82%B8%E3%82%B9%E3%82%BF%E3%81%AE%E5%86%85%E5%AE%B9%E3%82%92%E8%AA%AD%E3%81%BF%E5%8F%96%E3%82%8A%E3%81%BE%E3%81%99%E3%80%82%E6%B3%A8%E8%A8%98%EF%BC%81FlexCAN%20%E3%81%AF%20FreezeMode%20%E3%81%A7%E3%81%AF%E5%8B%95%E4%BD%9C%E3%81%97%E3%81%BE%E3%81%9B%E3%82%93%E3%80%82%20%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22SorinIBancila_3-1754053812864.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22SorinIBancila_3-1754053812864.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F350634iA7D2E25FFDA45DC4%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22SorinIBancila_3-1754053812864.png%22%20alt%3D%22SorinIBancila_3-1754053812864.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3C%2FLI%3E%0A%3C%2FUL%3E%0A%3C%2FDIV%3E%0A%3CDIV%20class%3D%22lineNode%22%3E%26nbsp%3B%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-center%22%20image-alt%3D%22SorinIBancila_5-1754053865424.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22SorinIBancila_5-1754053865424.png%22%20style%3D%22width%3A%20978px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F350636i12B004EE689ADA75%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22SorinIBancila_5-1754053865424.png%22%20alt%3D%22SorinIBancila_5-1754053865424.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%0A%3CBR%20%2F%3E%0A%3C%2FDIV%3E%0A%3CUL%3E%0A%3CLI%20class%3D%22lineNode%22%3ECAN_0_enterfreeze%20%E3%82%92%3CSTRONG%3E3%3C%2FSTRONG%3E%E3%81%AB%E8%A8%AD%E5%AE%9A%E3%81%97%E3%80%81MCR%20%E3%83%AC%E3%82%B8%E3%82%B9%E3%82%BF%E3%81%AE%E5%86%85%E5%AE%B9%E3%82%92%E8%AA%AD%E3%81%BF%E5%8F%96%E3%82%8A%E3%81%BE%E3%81%99%E3%80%82CAN%20%E3%81%8C%E5%86%8D%E3%81%B3%E5%8B%95%E4%BD%9C%E3%81%99%E3%82%8B%E3%82%88%E3%81%86%E3%81%AB%E3%81%AA%E3%82%8A%E3%81%BE%E3%81%97%E3%81%9F%E3%80%82CAN%20%E3%82%A2%E3%83%8A%E3%83%A9%E3%82%A4%E3%82%B6%E3%83%BC%20%E3%83%84%E3%83%BC%E3%83%AB%E3%81%8B%E3%82%89%E3%83%A1%E3%83%83%E3%82%BB%E3%83%BC%E3%82%B8%20(ID%20%3D%20101)%20%E3%82%92%E9%80%81%E4%BF%A1%E3%81%99%E3%82%8B%E3%81%A8%E3%80%81%E3%83%9C%E3%83%BC%E3%83%89%E3%81%AF%E3%83%A1%E3%83%83%E3%82%BB%E3%83%BC%E3%82%B8%20ID%20%3D%200%20%E3%81%A7%E5%BF%9C%E7%AD%94%E3%81%97%E3%81%BE%E3%81%99%E3%80%82%3C%2FLI%3E%0A%3C%2FUL%3E%0A%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22SorinIBancila_6-1754053942109.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22SorinIBancila_6-1754053942109.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F350637iFD2600671E5AC9E7%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22SorinIBancila_6-1754053942109.png%22%20alt%3D%22SorinIBancila_6-1754053942109.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-inline%22%20image-alt%3D%22SorinIBancila_7-1754053978440.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22SorinIBancila_7-1754053978440.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F350638iCCC8B227BA0FE9EA%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22SorinIBancila_7-1754053978440.png%22%20alt%3D%22SorinIBancila_7-1754053978440.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%0A%3CBR%20%2F%3E%0A%3CP%3ES32K3%20RTD%20%E3%82%BD%E3%83%BC%E3%82%B9%E3%81%AF%E3%83%84%E3%83%BC%E3%83%AB%E3%83%9C%E3%83%83%E3%82%AF%E3%82%B9%E5%86%85%E3%81%AB%E3%81%82%E3%82%8A%E3%80%81%E5%BF%85%E8%A6%81%E3%81%AB%E5%BF%9C%E3%81%98%E3%81%A6%E7%89%B9%E5%AE%9A%E3%81%AE%E3%83%A2%E3%82%B8%E3%83%A5%E3%83%BC%E3%83%AB%E3%81%AE%E5%AE%9F%E8%A3%85%E3%82%92%E7%A2%BA%E8%AA%8D%E3%81%A7%E3%81%8D%E3%81%BE%E3%81%99%E3%80%82S32K3%20%E3%83%95%E3%82%A9%E3%83%AB%E3%83%80%E3%83%BC%E3%81%AE%E3%83%AB%E3%83%BC%E3%83%88%E3%82%92%E9%96%8B%E3%81%8F%E3%81%AB%E3%81%AF%E3%80%81MATLAB%20%E3%82%B3%E3%83%9E%E3%83%B3%E3%83%89%20%E3%82%A6%E3%82%A3%E3%83%B3%E3%83%89%E3%82%A6%E3%81%AB%E6%AC%A1%E3%81%AE%E3%82%B3%E3%83%9E%E3%83%B3%E3%83%89%E3%82%92%E5%85%A5%E5%8A%9B%E3%81%97%E3%81%BE%E3%81%99%3A%20%3CSTRONG%3Ecd(mbd_find_s32k3_root)%3C%2FSTRONG%3E%20%E3%80%82%3C%2FP%3E%0A%3CSPAN%20class%3D%22lia-inline-image-display-wrapper%20lia-image-align-center%22%20image-alt%3D%22SorinIBancila_0-1754059684536.png%22%20style%3D%22width%3A%20999px%3B%22%3E%3Cspan%20class%3D%22lia-inline-image-display-wrapper%22%20image-alt%3D%22SorinIBancila_0-1754059684536.png%22%20style%3D%22width%3A%20550px%3B%22%3E%3Cimg%20src%3D%22https%3A%2F%2Fcommunity.nxp.com%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F350643i82257A597E9849F2%2Fimage-size%2Flarge%3Fv%3Dv2%26amp%3Bpx%3D999%22%20role%3D%22button%22%20title%3D%22SorinIBancila_0-1754059684536.png%22%20alt%3D%22SorinIBancila_0-1754059684536.png%22%20%2F%3E%3C%2Fspan%3E%3C%2FSPAN%3E%0A%3CBR%20%2F%3E%0A%3CBR%20%2F%3E%0A%3CBR%20%2F%3E%0A%3CP%3E%E4%BB%96%E3%81%AB%E3%81%94%E8%B3%AA%E5%95%8F%E3%81%8C%E3%81%94%E3%81%96%E3%81%84%E3%81%BE%E3%81%97%E3%81%9F%E3%82%89%E3%80%81%E9%81%A0%E6%85%AE%E3%81%AA%E3%81%8F%E3%81%94%E8%BF%94%E4%BF%A1%E3%81%8F%E3%81%A0%E3%81%95%E3%81%84%E3%80%82%3C%2FP%3E%0A%3CBR%20%2F%3E%0A%3CP%3E%E3%82%88%E3%82%8D%E3%81%97%E3%81%8F%E3%81%8A%E9%A1%98%E3%81%84%E3%81%84%E3%81%9F%E3%81%97%E3%81%BE%E3%81%99%E3%80%82%3C%2FP%3E%0A%3CP%3E%E3%82%BD%E3%83%AA%E3%83%B3%E3%83%BB%E3%83%90%E3%83%B3%E3%83%81%E3%83%A9%3C%2FP%3E%0A%3C%2FDIV%3E%0A%3C%2FDIV%3E%3C%2FLINGO-BODY%3E