Hello All,
I have a project that controls an AC fan motor via a triac. It senses the zero crossing & then after a delay triggers the triac to supply power to the ac motor. The speed of the fan is determined by the delay (which changes depending on user input) in switching on the triac. It is similar to attached the circuit.
I had been using interrupts & an LPC1768 for this project but am now switching to an '812. After investing it looks like the SCTimer/PWM is a suitable, but complicated in setup & control. Could anyone with experience tell me should I stick with an interrupt driven setup or is the SCTimer/PWM suitable? Once it's setup correctly it seems like it offloads alot of potential overhead.
Many thanks,
Leo
Jeremy,
Thanks for the reply.
Yes, your correct, the reason I was getting the 5ms delay was the the counter reaching all ones. My post previous to this outlines the reason the counter was not cleared.
I've attached the last version of my project for reference. The quickest I could achieve the stop, clear & restart scheme of the counter was approx 1ms, if you can see any quicker way I be grateful if you could share!
Hi ,
Thanks for your clarification.
Maybe you can try to create another event to detect the voltage level of kSCTIMER_Out_0 became 0 when the event 2 arises, after detecting it, triggering the counter resume.
In my opinion, it should be quicker than the interrupt handler function.
TIC
It looks like I've found the issue.
I was attempting to stop the counter & trigger an interrupt routine based on the same event. It appears that the counter was still running when the ISR attempted to clear it, hence it failed. Moving the call to the ISR into the following state solved the issue.
However based on the new code the minimum delay I was able to achieve using the stop, clear & restart scheme of the counter was approx 1ms, unsuitable for my application. I cannot see a way to achieve this any quicker. Also occasionally the clearing of the counter was missed & a long delay occurred.
I can definitely see the usefulness of the SCT but unfortunately it seems inappropriate for my application.
Jeremy,
I've changed to a 824 & have got a working project running now.
However I've found that I need to stop & restart the counter to achieve consistent timings. Using this technique however it looks like the minimum time I can get from starting the timer, it reaching a limit & triggering the event (setting an output high in state 1) is approx 5ms. I don't see anything in the manual mentioning delays between starting the counter & it running so its difficult to understand the delay. Ideally I'd like to achieve a minimum delay of 500uSec. I attach the project & the main file below.
* Copyright (c) 2016, Freescale Semiconductor, Inc.
* Copyright 2016-2017 NXP
* All rights reserved.
* SPDX-License-Identifier: BSD-3-Clause
* Modified --
* Input P0_24
* Output P0_15
* State 0 -> rising edges detected on input -> counter L started -> advance to state 1
* State 1 -> Counter L reaches limit value -> output set high -> advance to state 2
* State 2- > Falling edge on input -> output set low & counter stopped -> set state to 0
#include "fsl_debug_console.h"
#include "board.h"
#include "fsl_sctimer.h"
#include "fsl_gpio.h"
#include "pin_mux.h"
#include "fsl_inputmux.h"
#include <stdbool.h>
* Definitions
#define SCTIMER_CLK_FREQ CLOCK_GetFreq(kCLOCK_Irc)
#define DEMO_FIRST_SCTIMER_OUT kSCTIMER_Out_2
#define DEMO_SECOND_SCTIMER_OUT kSCTIMER_Out_4
#define INPUTSYNC0 (0U)
#define INPUTSYNC1 (1U)
#define INPUTSYNC2 (2U)
#define INPUTSYNC3 (3U)
* Prototypes
* Code
* @brief Main function
int main(void)
sctimer_config_t sctimerInfo;
uint32_t riseEvent, eventCounterL, fallEvent, riseEvent2; // Modified
uint32_t stateNumber; // Modified
uint32_t sctimerClock;
uint32_t matchValueL;
/* Board pin, clock, debug console init */
/* Enable clock of uart0. */
CLOCK_EnableClock(kCLOCK_Uart0);
/* Ser DIV of uart0. */
CLOCK_SetClkDivider(kCLOCK_DivUsartClk, 1U);
/* configure the input mux for the sct timer input0 from external pin*/
INPUTMUX_Init(INPUTMUX);
INPUTMUX_AttachSignal(INPUTMUX, 0U, kINPUTMUX_SctPin0ToSct0);
BOARD_InitPins();
BOARD_BootClockIRC12M();
BOARD_InitDebugConsole();
/* Enable clock of sct. */
CLOCK_EnableClock(kCLOCK_Sct);
sctimerClock = SCTIMER_CLK_FREQ;
/* Print a note to terminal */
PRINTF("\r\nAC Fan Controller using an LPC824 & SCT\r\n");
SCTIMER_GetDefaultConfig(&sctimerInfo);
/* Add judgment for change clock source*/
#if defined(SCTIMER_NEED_CHANGE_CLOCK_SOURCE)
sctimerInfo.clockMode = DEMO_CLOCK_MODE;
sctimerInfo.clockSelect = DEMO_CLOCK_SEL;
#endif
/* Switch to 16-bit mode */
sctimerInfo.enableCounterUnify = false;
/* Calculate prescaler and match value for Counter L for 100ms interval */
//matchValueL = MSEC_TO_COUNT(7U, sctimerClock);
// Looking for 0.5ms or 500uSec resolution
// From 0 to approx 10ms
matchValueL = USEC_TO_COUNT(1000U, sctimerClock);
sctimerInfo.prescale_l = matchValueL / 65536;
matchValueL = matchValueL / (sctimerInfo.prescale_l + 1) - 1;
// Switch off synchronization for inputs to speed up TODO: Necessary??
//sctimerInfo.inputsync = (1 << INPUTSYNC0);
/* Initialize SCTimer module */
SCTIMER_Init(SCT0, &sctimerInfo);
stateNumber = SCTIMER_GetCurrentState(SCT0);
// Interrupt callback for SCT //////////////////////////////////////////////////////////////
/* The interrupt callback function is used to update the PWM dutycycle */
void SCTIMER_COUNTER_HANDLER()
// Clear Counter_L so it starts from known value each time for event
SCT0->CTRL |= (1 << SCT_CTRL_CLRCTR_L_SHIFT);
//GPIO_PortToggle(GPIO, 0U, 1U << 13U);
// STATE 0 /////////////////////////////////////////////////////////////////////////////////
// event 0
/* Schedule an event to look for a rising edge on input 0 in this state */
if (SCTIMER_CreateAndScheduleEvent(SCT0, kSCTIMER_InputRiseEvent, 0u, kSCTIMER_Input_0, kSCTIMER_Counter_L,
&riseEvent) == kStatus_Fail)
return -1;
// Set output in this state TODO DEBUG
//SCTIMER_SetupOutputToggleAction(SCT0, kSCTIMER_Out_1, riseEvent);
// Restart counter for (next) timer event
SCTIMER_SetupCounterStartAction(SCT0, kSCTIMER_Counter_L,riseEvent);
/* Transition to next state when a rising edge is detected on input 1 */
SCTIMER_SetupNextStateAction(SCT0, stateNumber + 1, riseEvent);
// Goto next state
SCTIMER_IncreaseState(SCT0);
// STATE 1 /////////////////////////////////////////////////////////////////////////////////
// event 1
// Schedule a single match event for Counter L
if (SCTIMER_CreateAndScheduleEvent(SCT0, kSCTIMER_MatchEventOnly, matchValueL, 0, kSCTIMER_Counter_L,
&eventCounterL) == kStatus_Fail)
return -1;
SCTIMER_SetupOutputSetAction(SCT0, kSCTIMER_Out_0, eventCounterL);
// Transition to next state when counter expires
SCTIMER_SetupNextStateAction(SCT0, stateNumber + 2, eventCounterL);
// Stop counter to enable it to be cleared in interrupt handler
SCTIMER_SetupCounterStopAction(SCT0,kSCTIMER_Counter_L,eventCounterL);
// Enable interrupt for this event
SCTIMER_EnableInterrupts(SCT0,(1 << eventCounterL));
/* Receive notification when event is triggered */
SCTIMER_SetCallback(SCT0, SCTIMER_COUNTER_HANDLER, eventCounterL);
// Goto next state
// STATE 2 /////////////////////////////////////////////////////////////////////////////////
// event 2
/* Schedule an event to look for a falling edge on input 0 in this state */
if (SCTIMER_CreateAndScheduleEvent(SCT0, kSCTIMER_InputFallEvent, 0u, kSCTIMER_Input_0, kSCTIMER_Counter_L,
&fallEvent) == kStatus_Fail)
return -1;
// Clear output in this state
SCTIMER_SetupOutputClearAction(SCT0, kSCTIMER_Out_0, fallEvent);
// Transition to next state when event occurs in this state, i.e. loop back to initial state
SCTIMER_SetupNextStateAction(SCT0, stateNumber, fallEvent);
// STATE 3 /////////////////////////////////////////////////////////////////////////////////
// Use this state when full power is required
// SCT will be stuck in this state until software intervention
// event 3
&riseEvent2) == kStatus_Fail)
SCTIMER_SetupOutputSetAction(SCT0, kSCTIMER_Out_0, riseEvent2);
// No automatic transition to next event..
/* Enable at the NVIC */
EnableIRQ(SCT0_IRQn);
/* Start the L counter */
SCTIMER_StartTimer(SCT0, kSCTIMER_Counter_L);
/* Force the counter to be placed into memory. */
volatile static int i = 0 ;
/* Enter an infinite loop, just incrementing a counter. */
while(1) {
i++ ;
// char strdat[19] = " ";
// sprintf(strdat,"\n\r\n\r\n\r%i",SCT0->SCTCAP[riseTimeReg]);
// char strdat2[15] = " ";
// sprintf(strdat2,"\n\r%i",SCT0->SCTCAP[fallTimeReg]);
// USART_WriteBlocking(USART0, strdat,19);
// USART_WriteBlocking(USART0, strdat2,15);
for(int i=0; i < 5000000; i++);
PRINTF(".");
__asm volatile ("nop");
Sorry for reply late.
Regarding the statement: 'it looks like the minimum time I can get from starting the timer, it reaching a limit & triggering the event (setting an output high in state 1) is approx 5ms.', I think you misunderstand the limit event. When without other event configurations, counting up to all ones or counting down to zero is always equivalent to a limit event occurring. So the 'delay' between the starting the timer and reaching a limit & triggering the event seems like a 'timeout' period actually.
I was wondering if you can share the new code and introduce the testing process, as I'm not very clear with your current question.
TIC
Hello all,
I've hit a wall & could use some assistance. Using the code below I can successfully get an output to go high after the rising edge (state 0) & timer (state 1) have occurred. However the output never gets set low (state 2). If I remove the timer element (state 1) & edit the code the output correctly transitions to follow the input.
Can anyone see what I'm doing wrong? Is it something to do with the timer triggering while the SCT is in other states? Do I need to stop or halt the timer in other states to stop it interfering?
Thanks for looking..
* Modified -- P0_13 now as input to counter to start it,
* State 2- > Falling edge on input -> output set low & counter reset -> set state to 0
#include "board.h"
* Definitions
#define DEMO_SECOND_SCTIMER_OUT kSCTIMER_Out_3
* Prototypes
* Code
int main(void)
uint32_t riseEvent, fallEvent; // Modified
uint32_t eventCounterL;
BOARD_InitPins();
// PRINTF("\r\nSCTimer example to use it in 16-bit mode\r\n");
// PRINTF("\r\nThe example shows both 16-bit counters running and toggling an output periodically ");
#endif
/* Calculate prescaler and match value for Counter L for 10ms */
matchValueL = MSEC_TO_COUNT(100U, sctimerClock);
// sctimerInfo.inputsync = 0x0U;
// event 0
/* Schedule an event to look for a rising edge on input 1 in this state */
if (SCTIMER_CreateAndScheduleEvent(SCT0, kSCTIMER_InputRiseEvent, 0u, kSCTIMER_Input_1, kSCTIMER_Counter_L,
return -1;
// Goto next state
// event 1
/* Schedule a single match event for Counter L */
return -1;
/* Reset Counter L when Counter L event occurs TODO: Should counter be reset?? */
//SCTIMER_SetupCounterLimitAction(SCT0, kSCTIMER_Counter_L, eventCounterL);
/* Transition to next state when a rising edge detected on input 1 */
// Goto next state
// event 2
/* Schedule an event to look for a falling edge on input 1 in this state */
if (SCTIMER_CreateAndScheduleEvent(SCT0, kSCTIMER_InputFallEvent, 0u, kSCTIMER_Input_1, kSCTIMER_Counter_L,
return -1;
// Clear output when event occurs in this state
SCTIMER_SetupNextStateAction(SCT0, 0u, fallEvent);
while (1)
__asm("NOP"); /* delay */
& pin_mux.c
* This file was generated by the MCUXpresso Config Tools. Any manual edits made to this file
* will be overwritten if the respective MCUXpresso Config Tools is used to update this file.
/* clang-format off */
* TEXT BELOW IS USED AS SETTING FOR TOOLS *************************************
!!GlobalInfo
product: Pins v6.0
processor: LPC812
package_id: LPC812M101JDH20
mcu_data: ksdk2_0
processor_version: 6.0.2
* BE CAREFUL MODIFYING THIS COMMENT - IT IS YAML SETTINGS FOR TOOLS ***********
/* clang-format on */
#include "fsl_common.h"
#include "fsl_swm.h"
/* FUNCTION ************************************************************************************************************
* Function Name : BOARD_InitBootPins
* Description : Calls initialization functions.
* END ****************************************************************************************************************/
void BOARD_InitBootPins(void)
BOARD_InitPins();
BOARD_InitPins:
- options: {callFromInitBoot: 'true', coreID: core0, enableClock: 'true'}
- pin_list:
- {pin_num: '18', peripheral: USART0, signal: TXD, pin_signal: PIO0_6/VDDCMP}
- {pin_num: '12', peripheral: USART0, signal: RXD, pin_signal: PIO0_1/ACMP_I2/CLKIN}
- {pin_num: '3', peripheral: SCT0, signal: 'IN, 1', pin_signal: PIO0_12, mode: pullDown}
- {pin_num: '2', peripheral: SCT0, signal: 'OUT, 0', pin_signal: PIO0_13, mode: pullDown}
- {pin_num: '20', peripheral: SCT0, signal: 'OUT, 1', pin_signal: PIO0_14, mode: pullDown}
- {pin_num: '11', peripheral: SCT0, signal: 'OUT, 2', pin_signal: PIO0_15, mode: pullDown}
* Function Name : BOARD_InitPins
* Description : Configures pin routing and optionally pin electrical features.
/* Function assigned for the Cortex-M0P */
void BOARD_InitPins(void)
/* Enables clock for switch matrix.: Enable. */
CLOCK_EnableClock(kCLOCK_Swm);
IOCON->PIO[2] = ((IOCON->PIO[2] &
/* Mask bits to zero which are setting */
(~(IOCON_PIO_MODE_MASK)))
/* Selects function mode (on-chip pull-up/pull-down resistor control).: Pull-down. Pull-down
* resistor enabled. */
| IOCON_PIO_MODE(PIO0_12_MODE_PULL_DOWN));
IOCON->PIO[1] = ((IOCON->PIO[1] &
| IOCON_PIO_MODE(PIO0_13_MODE_PULL_DOWN));
IOCON->PIO[18] = ((IOCON->PIO[18] &
| IOCON_PIO_MODE(PIO0_14_MODE_PULL_DOWN));
IOCON->PIO[10] = ((IOCON->PIO[10] &
| IOCON_PIO_MODE(PIO0_15_MODE_PULL_DOWN));
/* USART0_TXD connect to P0_6 */
SWM_SetMovablePinSelect(SWM0, kSWM_USART0_TXD, kSWM_PortPin_P0_6);
/* USART0_RXD connect to P0_1 */
SWM_SetMovablePinSelect(SWM0, kSWM_USART0_RXD, kSWM_PortPin_P0_1);
/* SCT_PIN1 connect to P0_12 */
SWM_SetMovablePinSelect(SWM0, kSWM_CTIN_1, kSWM_PortPin_P0_12);
/* SCT_OUT0 connect to P0_13 */
SWM_SetMovablePinSelect(SWM0, kSWM_CTOUT_0, kSWM_PortPin_P0_13);
/* SCT_OUT1 connect to P0_14 */
SWM_SetMovablePinSelect(SWM0, kSWM_CTOUT_1, kSWM_PortPin_P0_14);
/* SCT_OUT2 connect to P0_15 */
SWM_SetMovablePinSelect(SWM0, kSWM_CTOUT_2, kSWM_PortPin_P0_15);
/* Disable clock for switch matrix. */
CLOCK_DisableClock(kCLOCK_Swm);
* EOF
Hi ,
Thanks for your reply.
After having a reviewing of the code, I've not found any of the wrongs in the codes. So I'd like to suggest you take advantage of step in step debug feature to observe the values of the set of SCTimer's registers to locate the issue.
TIC
In state 1 I’m using the L counter to achieve a delay. The other two states using input edge transitions as events. After using the L counter in state 1 should I stop the counter?
Hi ,
According to the description of your scheme, I don't think it should stop the counter after using the L counter in state 1.
TIC
Jeremy,
Thanks for the reply. I've spent hours looking at the code & trying to debug but without any success. I've verified that it increments to state 2 & gets stuck there, the event (number 3) in state 2 is never triggered. I've tried numerous ways to trigger & verified the inputs show a level change but no action occurs in this event.
I had thought I'd discovered the reason as a possible bug in the file fsl_sctimer.c. At line 516 the following code appears:
/* Enable the event in the current state */
base->EVENT[s_currentEvent].STATE = (1U << s_currentState);
Once s_currentState increases beyond 2 this fails to set anything (only bit 0 & 1 can be set) but this has no impact on my code. Perhaps I'm missing something.
I can only suspect another possible bug or I've damaged my board (an Xpresso board) during debugging. I've attached the project, if you had a moment to see if it runs on a similar board I'd be much appreciated.
Well the penny finally dropped! The part I'm using (812) only has 2 states for it's SCT, others have more. Interestingly the manual mentions numerous times the max possible number of events but not states. The SDK software checks for exceedance in events but not states. I found the table below in the SCT cookbook, included for reference by others.
As an aside is it possible for the L & H counter to use the same input & output or must they be separate?
Thanks for your reply and I'm glad to hear that you found out the issue.
Regarding another question, is it possible for the L & H counter to use the same input & output or must they be separated?
-- Yes, the L & H counter share the same clock source.
TIC
Hi ,
1) Could anyone with experience tell me should I stick with an interrupt driven setup or is the SCTimer/PWM suitable?
-- According to your description, I consider the SCTimer is suited to the application, I've attached an application note which will guide to you how to utilize the SCTimer module.
TIC
Ive had a look at this but difficult to get my head around. What I'd like to do:
so far I have something like:
/* SCT_PIN2 connect to P0_13 */
SWM_SetMovablePinSelect(SWM0, kSWM_CTIN_2, kSWM_PortPin_P0_13);
/* SCT_OUT3 connect to P0_12 */
SWM_SetMovablePinSelect(SWM0, kSWM_CTOUT_3, kSWM_PortPin_P0_12);
/* Schedule a capture event to start timer on rising edge of input pin*/
if (SCTIMER_CreateAndScheduleEvent(SCT0, kSCTIMER_InputRiseEvent, matchValueL, output_pin_here, kSCTIMER_Counter_L,&eventCounterL) == kStatus_Fail)
return -1;
I've obviously a long way to go... any pointers??