Does anyone have example code for MPC5744P FCCU EOUT connected to SBC IO?

キャンセル
次の結果を表示 
表示  限定  | 次の代わりに検索 
もしかして: 

Does anyone have example code for MPC5744P FCCU EOUT connected to SBC IO?

901件の閲覧回数
juliusjai
Contributor II

Hi,

I'm interested to know how I can send the FCCU EOUT reaction to SBC IO.

Does anyone have example implementation?

Thanks.

タグ(3)
0 件の賞賛
3 返答(返信)

589件の閲覧回数
petervlna
NXP TechSupport
NXP TechSupport

Hi,

There is no code needed.

FCCU has 2 EOUT signals.

EOUT0 and EOUT1 which for this device are always connected to pins.

If you want to enable the fault notification for EOUT, then you simply configure Fault-Output (EOUT) Signaling Enable
(FCCU_EOUT_SIG_ENn) register to do it.

Each bit represents  NCF which will be signaled out if the fault is active in NCFS_x registers:

pastedImage_1.png

Peter

0 件の賞賛

589件の閲覧回数
juliusjai
Contributor II

Hi Peter,

Thank you very much.

Julius

0 件の賞賛

589件の閲覧回数
李丽丽
Contributor I

Have you successed?Any replay would be greatful

0 件の賞賛