Hello,
In the page 51 of the datasheet Figure 31 shows the graphic of the Power-up ramp. The wait time (twait) specifies the time the power supply must be at levels below 200mV. In the datasheet says that this time has to be at least 12us before the ramping. However, the errata says that the device won't start always if you only wait 12us, in order to avoid that is better wait 2ms before the ramping.

These power up conditions must be met when you do a power-on reset. You can check this by connecting a oscilloscope to VDD and make a power-on reset on the LPC, this way you should see the same response as in Figure 31 as shown in the attach image
This could only affect you if you are making continuous power on resets.
Hope it helps!
Victor.
-----------------------------------------------------------------------------------------------------------------------