sMCAL safety requirement - control flow monitor

取消
显示结果 
显示  仅  | 搜索替代 
您的意思是: 
已解决

sMCAL safety requirement - control flow monitor

跳至解决方案
534 次查看
zeyu_yan
Contributor III

Hello,

 I have a question about the integration requirement for ASIL C.

the number is SMCAL_CPR_EXT168:control flow monitor

   should Watchdog_Manager(in Autosar) monitor the checkpoint in MCAL or just monitor the checkpoints in SWC(or BSW,CDD) which uses the MCAL ?  (for example , the mcal for ADC is used for sampling of accelarator pedal which is allocated to ASIL C)

how should I 

zeyu_yan_0-1669175831442.png

zeyu_yan_1-1669175839626.png

reference:S32XX_MCAL4_4_SAFETY_PACK_RTM_1_0_0_Safety_Manual

 

 

标签 (1)
0 项奖励
1 解答
522 次查看
frantisekdobes
NXP Employee
NXP Employee

Hello,

SMCAL_CPR_EXT168 is specified for the user application so user application needs to implement the control flow monitoring and also decide where the checkpoints will be located (MCAL itself does not define any checkpoints).

Best Regards,

Frantisek

在原帖中查看解决方案

0 项奖励
2 回复数
523 次查看
frantisekdobes
NXP Employee
NXP Employee

Hello,

SMCAL_CPR_EXT168 is specified for the user application so user application needs to implement the control flow monitoring and also decide where the checkpoints will be located (MCAL itself does not define any checkpoints).

Best Regards,

Frantisek

0 项奖励
500 次查看
zeyu_yan
Contributor III

Thank you.We have used WatchdogManager  to add checkpoints in the SWC.

0 项奖励