Hi, rdelljh:
Imajeff has posted everything you need to know. To summarize, and basically update my previous post with current information:
You cannot use an RS232->RS485 adapter, because the Dragon doesn't give you the modem-control lines that are necessary to control it.
You can communicate directly with the motor controller with the Dragon's RS485 port, using the procedure that I outlined above, but asserting and de-asserting PJ0 in those places where I called out RTS.
Hi, Imajeff:
I can describe RS485 in a few sentences. It is not really a protocol, but simply an electrical interface spec, like RS232.
It is usually half-duplex, using two twisted-pair wires, but can also be full-duplex, using two sets of twisted-pair wires. It is multi-drop, and your software has to insure that only one node tries to transmit at any point in time. The two wires are driven differentially: when one is high, the other is low. The cable typically has a characteristic impedance of around 120 ohms, and is terminated with a 120 ohm resistor at each end. It can work over very long runs, up to 4000 feet, and can support baud rates into the mega-bauds. The transceivers requires only 5 volts. Like RS232, you need to define the software protocol, including baud-rate, number of data bits, stop bits, parity and the like.