Hi Pavel.
Thanks for the response.
The 'Sample Time' in 'Current Loop Parameters' does indeed update, which I
didn't notice before.
I followed the following sequence:
1. Changed M1_PWM_FREQ to 1000.
2. Rebuild project.
3. Load firmware onto KV31 micro controller.
4. Open Freemaster project.
5. Check 'Sample Time' parameter (updated).
6. Measure Parameters.
1. Calculates Rs = -2.2Ω (takes much longer than when M1_PWM_FREQ is
10k, also at 10kHz the resistance is 0.98Ω).
2. Then the motor rotates CCW before starting to spin CW. The motor
spins for quite long (approximately 2 minutes) and then abruptly stops.
3. After approximately 30s the blocked rotor test message appears.
The windings remain energised as the rotor is tough to rotate
and the 1kHz
switching can be heard clearly. Again this test takes very long
to complete.
4. The mechanical parameters test runs quite quickly.
5. 1kHz
10kHz
7. With the above parameters the motor runs well in both Speed and
Current FOC.
I am rather concerned with the negative stator resistance, surely this must
imply everything else is questionable?
1. Could you point me in a direction regarding the resistance and
accuracy of the parameters?
2. How can I get the inverter in the off state to safely block and
unblock the rotor (at 10kHz I'm sure it is off since the rotor rotates
freely)?
3. Is there a way I can reduce the test duration? I understand a number
of samples are required to attain a reasonable accuracy, but I'd like to
fool around and hopefully come to a more realistic tradeoff.
4. I get an information message that Un is outside the hardware range
however UDCBusMax is 415V. Could you please elaborate on the reasons and
implications of this. See images below.
Thanks again for your prompt response and help.
Regards
Vickus (JL) Boshoff
082 557 4885