Using BMS based on S32K144 and MC3377xB. Change duration of TPL blocking time threshold?

キャンセル
次の結果を表示 
表示  限定  | 次の代わりに検索 
もしかして: 

Using BMS based on S32K144 and MC3377xB. Change duration of TPL blocking time threshold?

915件の閲覧回数
ranulf
Contributor IV

TPL communication as monitored by the S32K144 appears to be blocking. So, if TPL communication fails for some reason code execution on the S32K144 is stopped until a time threshold is crossed. Is there a way to change the duration of that time threshold?

0 件の賞賛
返信
1 返信

891件の閲覧回数
SorinIBancila
NXP Employee
NXP Employee

Hello @ranulf,

In the MC33772B configuration block's tlc you can find the following define: #define BCC_COM_TIMEOUT_MS 10.

You can try to modify this value to increase/decrease the timeout.

 

Best regards,

Bancila Sorin 

SorinIBancila_0-1668087904370.png

 

0 件の賞賛
返信