Does anyone have example code for MPC5744P FCCU EOUT connected to SBC IO?

取消
显示结果 
显示  仅  | 搜索替代 
您的意思是: 

Does anyone have example code for MPC5744P FCCU EOUT connected to SBC IO?

898 次查看
juliusjai
Contributor II

Hi,

I'm interested to know how I can send the FCCU EOUT reaction to SBC IO.

Does anyone have example implementation?

Thanks.

标记 (3)
0 项奖励
3 回复数

586 次查看
petervlna
NXP TechSupport
NXP TechSupport

Hi,

There is no code needed.

FCCU has 2 EOUT signals.

EOUT0 and EOUT1 which for this device are always connected to pins.

If you want to enable the fault notification for EOUT, then you simply configure Fault-Output (EOUT) Signaling Enable
(FCCU_EOUT_SIG_ENn) register to do it.

Each bit represents  NCF which will be signaled out if the fault is active in NCFS_x registers:

pastedImage_1.png

Peter

0 项奖励

586 次查看
juliusjai
Contributor II

Hi Peter,

Thank you very much.

Julius

0 项奖励

586 次查看
李丽丽
Contributor I

Have you successed?Any replay would be greatful