Thanks Adam,
Once you are in overmodulation though, you should stay in that state correct? I'm afraid maybe my DC Bus input or one of my settings is not allowing it to function correctly.My system is going in and out of that state when the voltage gets low.
My system is getting very close to the voltage limit - the system is designed to run all the way to the voltage limit at 3x rated load and then fault (on low voltage) or shut off before we lose sync.
This is a quick analysis of what the system should be able to provide at 200V:
I did a fast analysis of the voltage drop in the resistor path to the motor and the converter should be able to provide around 124Vac ph-ph rms at 200Vdc using max modulation index. Therefore, it should be able to operate 140Nm at 1155 rpm, which would require around 115Vac ph-ph rms.

Instead, if we don’t apply common mode voltage in the modulation to get maximum modulation index we cannot provide the required 115 Vac ph-ph rms and we would need to reduce speed until around 1050 rpm (according to the calculation).

On my opinion, what I would check is if we are providing and defining properly the modulation index by trendering all modulation parameters and converter output.