Behaviour of PGA in MC56F845xx in case of error

跳至解决方案
2,402 次查看
guenter_loettrich
NXP Employee
NXP Employee


Hi all,

 

customer Diehl are asking a very specific question about the influence of the settings of ADCx_GC1 on the conversion result in case of an error.

This may need help from design to get an answer. Its a question of the customer's FMEA exercise.

 

Imagine the following setup:

95946_95946.PNGADC12.PNG

 

ANA0 is configured to be amplified by 4 (ADCx_GC1_GAIN0 = 01)

ANA1 is configured to be amplified by 1 (ADCx_GC1_GAIN1 = 00)

 

The question: What happens to the conversion results in RSLT0 and RSLT1 if the analog input multiplexer of ANA is set to channel ANA0 due to an

internal short to 0 of the lowest bit of the multiplexer adressing signal? Meaning that channel ANA0 is selected due to the error although software initiated a conversion of channel ANA1. 

Will the PGA amplify the input signal by 4 or not?

 

Thanks

 

Guenter

标签 (1)
0 项奖励
回复
1 解答
2,098 次查看
johnlwinters
NXP Employee
NXP Employee

The signal scaling function, which incorporates the programmable gain feature, is independent of the signal select function. So, at the ADC level, the signal provided by the signal select function will be scaled in accordance with the signal scaling setting irrespective of if the signal was correctly selected or not.

Or, in orther words:

If the error causes ANA0 to be selected instead of ANA1, then the result would be ANA0 scaled by the gain control programmed for ANA1.  This means that RSLT0 would be correct and RSLT1 would be ANA0 scaled by 1 (or RSLT0 divided by 4 in this case). There is only one PGA and it is after the analog muxing so it would be independent of the error in the muxing.

在原帖中查看解决方案

4 回复数
2,099 次查看
johnlwinters
NXP Employee
NXP Employee

The signal scaling function, which incorporates the programmable gain feature, is independent of the signal select function. So, at the ADC level, the signal provided by the signal select function will be scaled in accordance with the signal scaling setting irrespective of if the signal was correctly selected or not.

Or, in orther words:

If the error causes ANA0 to be selected instead of ANA1, then the result would be ANA0 scaled by the gain control programmed for ANA1.  This means that RSLT0 would be correct and RSLT1 would be ANA0 scaled by 1 (or RSLT0 divided by 4 in this case). There is only one PGA and it is after the analog muxing so it would be independent of the error in the muxing.

2,098 次查看
johnlwinters
NXP Employee
NXP Employee


Design has been consulted.  The answer will be posted soon.

0 项奖励
回复
2,098 次查看
guenter_loettrich
NXP Employee
NXP Employee

Hi John,

have you got any feedback from design on that? Customer is pushing for an answer.

0 项奖励
回复
2,098 次查看
johnlwinters
NXP Employee
NXP Employee

I posted the question on 11/5.

I reposted it today to engineering.  I'll let you know any response to this hypothetical situation.

0 项奖励
回复